gkisyuser Posted December 31, 2013 Posted December 31, 2013 EZIO8SA communicating with ISY Have also in the system I/O Linc #2450 Named Heat_Off#1-Relay I/O Linc #2450 Named Heat_On#2-Relay Motion Sensor Programs Motion sensor turns Output 6 on then off Heat off relay and heat on relay get turned off with the programs After reboot everything seems to work The heat on and heat off I/O Linc can be turned on and off as many times you can cycle them Once you toggle the EZIO8SA outputs a couple of times I get system busy and the log shows this: 22 7F B8 D Status 0% Wed 2013/12/25 02:44:12 PM System Log 22 7F B8 D Status 100% Wed 2013/12/25 02:44:12 PM System Log 22 7F B8 E Status 0% Wed 2013/12/25 02:45:48 PM System Log 22 7F B8 E Status 100% Wed 2013/12/25 02:45:48 PM System Log 22 7F B8 E Status 0% Wed 2013/12/25 02:45:49 PM System Log 22 7F B8 E Status 100% Wed 2013/12/25 02:45:49 PM System Log 22 7F B8 E Status 0% Wed 2013/12/25 02:45:50 PM System Log 22 7F B8 E Status 100% Wed 2013/12/25 02:45:50 PM System Log 22 7F B8 E Status 0% Wed 2013/12/25 02:45:51 PM System Log 22 7F B8 E Status 100% Wed 2013/12/25 02:45:52 PM System Log 22 7F B8 D Status 0% Wed 2013/12/25 02:45:57 PM System Log 22 7F B8 D Status 100% Wed 2013/12/25 02:46:31 PM System Log 22 7F B8 D Status 0% Wed 2013/12/25 02:46:37 PM System Log 22 7F B8 E Status 0% Wed 2013/12/25 02:46:37 PM System Log 22 7F B8 D Status 100% Wed 2013/12/25 02:46:37 PM System Log 22 7F B8 E Status 100% Wed 2013/12/25 02:46:38 PM System Log this goes on for ever and at some point nothing else works. I now realize that D and E are analog input 5 & 6. Could those not being grounded cause this? In the event log 12-24 at 10:45 the EZIO8SA was removed and the ISY rebooted Thanks gkisyuser 2-ISY Log.v4.0.5__Fri 2013.12.27 04.30.34 AM2.txt
LeeG Posted December 31, 2013 Posted December 31, 2013 Connect Inputs 5 & 6 to the EZIO8SA Gnd. Otherwise these Inputs will cycle On/Off enough to cause problems.
gkisyuser Posted May 29, 2014 Author Posted May 29, 2014 Had a new problem that gave same result as an old problem with the floating inputs of the EZIO8SA. the old problem was the two analog inputs of the EZIO8SA not being grounded that created constant polling by the ISY and at some point locking it up and not working. The new problem started with the emails showing no change in temp.and several days later the ISY quit working. I found the battery on the thermostat had gone dead and after replacing them, the ISY was still dead. Once doing a manual reset on the ISY, everthing was back working. When there is a repeating error such as the communication loss from the ISY to the EZIO8SA or in this case of communication loss to the thermostat, The ISY controller locks up. Is there any programming that will help this problem. By the way the remote thermostat's internal temp sensor is switched from the internal one to either an outside or underhouse sensor. Works great by switching a couple of outputs in the EZIO8SA with Mobillink and the one thermostat can see 4 different sensors with two outputs. Only down side is about a 1 minute delay for the updated temperature. Has there been any changes to allow variables to be used to turn logic on or off and not just sent as messages in email? Thanks gkisyuser
Recommended Posts