tlightne Posted February 19, 2023 Posted February 19, 2023 (edited) I have three fans that I turn on at 9:30am as long as outside and indoor temperatures are met and my AC supply temperatures are below 65°. I have a second AC supply sensor I want to add so that either AC supply Temperature is <65° or AC Supply 2 Temperature is <65°. When I add AC sensor 2 with an OR after AC sensor 1 the IF sees the or and starts the program regardless of the ands.. Thank you Here is my program: All Fans On 77 AC On Ambient PG3 - [ID 000E][Parent 0063] If From 9:30:00AM To 10:59:00PM (same day) And 'AmbientWeather PG3 / main' Temperature >= 77.0°F And 'AmbientWeather PG3 / indoor' Temperature > 76.0°F And 'AC Temps / AC Supply Tempature' Temperature < 65.5°F Then Set 'Dinning Room / Dinning Room Fan Switch' 18% Set 'Living Room / Living Room Fan Low' On Set 'Den / Den Fan Low' On Else - No Actions - (To add one, press 'Action') Edited February 20, 2023 by tlightne
kclenden Posted February 20, 2023 Posted February 20, 2023 1 hour ago, tlightne said: I want to add so that either AC supply Temperature is <65° or AC Supply 2 Temperature is <65°. Are you using parentheses? After you add AC sensor 2 with OR, click the "Add And (..)" button. Then click "Move Line Up" until the parentheses enclose your two AC supply Temperatures.
tlightne Posted February 20, 2023 Author Posted February 20, 2023 (edited) @kclenden I will give that a shot. Thank you Edited February 20, 2023 by tlightne