Hello,

 

I just can not figure this one out. I can set the ramp rates in ISY-99, but when you localy hit the switch it goes on 100% when it is set at 60% in the ISY, what am I doing wrong?

 

Thanks

Posted

Hi Michael,

 

This is actually a frequently asked question :) . After setting the local level/ramp (for any device other than a KeypadLinc), you must reboot the device for the new settings to take effect. You can do this by pulling out the Set button (known as air-gapping) for a few seconds and then pushing gently back in, unplugging the module and replugging, or turning off the breaker for a few seconds.