jsu1995 Posted July 2, 2012 Share Posted July 2, 2012 Question: Is it possible to change status of a Keypadlinc LED when turning an Outletlinc On/Off via its set button? Background Information: I just added my first outletlinc (relay) to my system (ISY-99i Pro) and have linked one keypadlinc button to operate it. I wrote a simple program to command the LED status to follow the status of the outletlinc. To my surprise, the LED status does not change when operating the local On/Off command integrated into the set button at the Outletlinc. Is this normal? Link to comment
LeeG Posted July 2, 2012 Share Posted July 2, 2012 "Is it possible to change status of a Keypadlinc LED when turning an Outletlinc On/Off via its set button?" Unfortunately no. The OutletLinc Relay is a Responder only device. As such it does not indicate local changes to any other Insteon device. ApplianceLinc is in the same category of Responder only. A Responder only device can be identified by looking at the Quick Start and User Guide. There is information on linking the OutletLinc Relay as a Responder but no information on linking the OutletLinc Relay as a Controller which would be necessary for another device to be notified of a local change in status. EDIT: the OutletLinc Dimmer will function as a Controller but the load must be dimmable. Link to comment