Insteon Leak Sensor 2852-222


flsenior

Recommended Posts

Posted

I am having trouble installing the new Insteon Leak Sensor 2852-222. I just upgraded to V3.2.6 on a ISY 99.

 

After depressing the set button and activating the blinking LED on the leak sensor, I have tried to install a new device on the ISY. I keep getting the following error message.

 

Node not added - failed restoring device

21 4F BF 1

[-200000/-10]

 

Any suggestions?

Posted

Beta 3.3.4 supports that module.

You may have to update to the Beta 3.3.4 to have it work.

It is device 10.08 in the drop down list in 3.3.4.

Posted

3.3.4 solved the installation issue.

 

Another question -

The installed device has two settings - dry & wet. When test the leak sensor via the test button on the unit, the wet is activated to "on" but will not reset to "off". Is this normal?

Posted

The leak sensor spec indicates this is correct. When the leak sensor goes Wet it turns the Wet node (Group 2) On. When it goes Dry it turns the Dry node (Group 1) On. There is no Off indicated for either node (Group).

 

EDIT: the TriggerLinc functions the same way when operating in two Scene mode. It sends an On command to one node when the TriggerLinc turns On and sends an On command to the other node when the TriggerLinc turns Off. It does not send an Off command to either node.