richardl007 Posted February 28, 2013 Posted February 28, 2013 I recently upgraded my 99i to a 994i and I'm having a problem. 1 of my light switches turns off with a scen that it's not in. I restored the switch but it still seems to act like it's in the sean that it's not in. Any suggestions?
LeeG Posted February 28, 2013 Posted February 28, 2013 Is it reacting to a Scene initiated by an ISY Program/Admin Console or is it reacting to the paddle/button press of another Controller?
LeeG Posted March 1, 2013 Posted March 1, 2013 That means there are two distinct problems as the device responds to each in a different way. Suggest running Tools | Diagnostics | Show Device Links Table for the device that is responding to both a Program initiated Scene and a Controller initiated Scene (button/paddle press). Post the Show results along with the Insteon address of the Controller that turns the device On. Run a Show Device Links Table for the Controller device and post that Show result. Also run Tools | Diagnostics | Event Viewer with LEVEL 3. Run the Program that invokes the Scene that turns the device On and post the event trace along with the PLM Insteon address.