Captain Posted April 6, 2013 Share Posted April 6, 2013 I have installed the I/O Linc garage door control and have linked it to my ISY but the ISY cannot communicate with the sensor on the door. I have a green light on the sensor status at the I/O. I tried a FilterLinc out of curiosity but no luck. Next step? Link to comment Share on other sites More sharing options...
LeeG Posted April 6, 2013 Share Posted April 6, 2013 Move the I/O Linc to the PLM plug point to confirm it is working. Simply connect a short piece of wire to short GND and Sensor to see if I/O Linc is reporting state change. If it does not work at the PLM plug point it could be a link record problem in either the PLM or the I/O Linc, or a defective I/O Linc. If it works at the PLM plug point then work on the Insteon network. Link to comment Share on other sites More sharing options...