JSchumann Posted October 20, 2014 Share Posted October 20, 2014 I have a sump high level alarm (hooked up to ELK M1) that plugs in an outlet....recently the breaker tripped and I didn't get a high level alarm. Is there a module that I can rig to tell me if the alarm circuit lost power? Thanks, John Link to comment
stusviews Posted October 20, 2014 Share Posted October 20, 2014 An I/O Linc with the NC contacts connected to the external contacts of an INSTEON wireless Open/Close sensor (2843-222). Use latching mode and turn the I/O Linc relay On. Link to comment
JSchumann Posted October 20, 2014 Author Share Posted October 20, 2014 Thanks....I can probably use the I/O link and connect directly to ELK M1, when relay drops out NO contacts will close..... Link to comment