IOLInc and nightly query
I have an IOLinc on my garage door.  The trigger reverse option is not checked.  When the ISY queries the network at 3am, the IOLinc status changes . .  . I have read that this issue can be caused by having the trigger reverse option checked, but in my case it is not . . . . anyone have a solution to waking up with the system thinking the garage door is open?
TIA
David
Need an Event Viewer trace at LEVEL 3 to be sure.  Does not have to be the 3AM Query.  Can be from a Query (done twice quickly) executed during the day.
I have seen multiple query responses received by the PLM from an I/O Linc Query.   A Query of either I/O Linc node results in both nodes (Sensor and Relay) being queried.  The 3AM Query is issued twice (once for each node) for an I/O Linc so 4 physical Query commands are issued.  If the I/O Linc sends (or the Insteon network produces) a duplicate query response the duplicate message can be applied against the wrong Query command making it appear that the Sensor has changed state when it has not.
Also need to know if the Sensor is normally On or Off when door is closed.   The Green LED next to the I/O Linc connections indicates the Sensor status (Green LED On when Sensor On).  The duplicate message is normally intermittent.
Edited by LeeG
Normally Off - 2B F8 BB
Fri 10/24/2014 12:29:55 PM : [iNST-TX-I1  ] 02 62 24 D9 7C 0F 19 00
Fri 10/24/2014 12:29:55 PM : [iNST-ACK    ] 02 62 24.D9.7C 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:55 PM : [iNST-SRX    ] 02 50 24.D9.7C 2C.07.70 2B 17 00    LTMCON (DOWN)
Fri 10/24/2014 12:29:55 PM : [std-Direct Ack] 24.D9.7C-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:55 PM : [iNST-TX-I1  ] 02 62 24 DA 13 0F 19 00
Fri 10/24/2014 12:29:55 PM : [iNST-ACK    ] 02 62 24.DA.13 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:56 PM : [iNST-SRX    ] 02 50 24.DA.13 2C.07.70 2B 55 FF           (FF)
Fri 10/24/2014 12:29:56 PM : [std-Direct Ack] 24.DA.13-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:56 PM : [iNST-TX-I1  ] 02 62 24 DC 6D 0F 19 00
Fri 10/24/2014 12:29:56 PM : [iNST-SRX    ] 02 50 24.DA.13 2C.07.70 23 55 FF           (FF)
Fri 10/24/2014 12:29:56 PM : [std-Direct Ack] 24.DA.13-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:29:56 PM : [iNST-ACK    ] 02 62 24.DC.6D 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:56 PM : [iNST-SRX    ] 02 50 24.DC.6D 2C.07.70 2B 1B 00           (00)
Fri 10/24/2014 12:29:56 PM : [std-Direct Ack] 24.DC.6D-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:56 PM : [iNST-TX-I1  ] 02 62 24 DD CA 0F 19 00
Fri 10/24/2014 12:29:56 PM : [iNST-ACK    ] 02 62 24.DD.CA 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:57 PM : [iNST-SRX    ] 02 50 24.DD.CA 2C.07.70 2B 48 00           (00)
Fri 10/24/2014 12:29:57 PM : [std-Direct Ack] 24.DD.CA-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:57 PM : [iNST-TX-I1  ] 02 62 24 DE 24 0F 19 00
Fri 10/24/2014 12:29:57 PM : [iNST-ACK    ] 02 62 24.DE.24 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:57 PM : [iNST-SRX    ] 02 50 24.DE.24 2C.07.70 2B 45 FE    IOON   (FE)
Fri 10/24/2014 12:29:57 PM : [std-Direct Ack] 24.DE.24-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:57 PM : [iNST-TX-I1  ] 02 62 24 DF 8C 0F 19 00
Fri 10/24/2014 12:29:57 PM : [iNST-ACK    ] 02 62 24.DF.8C 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:58 PM : [iNST-SRX    ] 02 50 24.DF.8C 2C.07.70 2B 53 00           (00)
Fri 10/24/2014 12:29:58 PM : [std-Direct Ack] 24.DF.8C-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:58 PM : [iNST-TX-I1  ] 02 62 24 E1 EE 0F 19 00
Fri 10/24/2014 12:29:58 PM : [iNST-ACK    ] 02 62 24.E1.EE 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:58 PM : [iNST-SRX    ] 02 50 24.E1.EE 2C.07.70 2B 59 00           (00)
Fri 10/24/2014 12:29:58 PM : [std-Direct Ack] 24.E1.EE-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:29:58 PM : [iNST-TX-I1  ] 02 62 24 EF 05 0F 19 00
Fri 10/24/2014 12:29:58 PM : [iNST-ACK    ] 02 62 24.EF.05 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:29:59 PM : [iNST-SRX    ] 02 50 24.EF.05 2C.07.70 27 E0 00           (00)
Fri 10/24/2014 12:29:59 PM : [std-Direct Ack] 24.EF.05-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:29:59 PM : [iNST-TX-I2CS] 02 62 24 EF 05 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1
Fri 10/24/2014 12:29:59 PM : [iNST-ACK    ] 02 62 24.EF.05 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06        (00)
Fri 10/24/2014 12:29:59 PM : [iNST-SRX    ] 02 50 24.EF.05 2C.07.70 2B 2E 00           (00)
Fri 10/24/2014 12:29:59 PM : [std-Direct Ack] 24.EF.05-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:00 PM : [iNST-ERX    ] 02 51 24 EF 05 2C 07 70 11 2E 00 01 01 00 00 20 20 1C FF 3F 34 FC 00 34 00
Fri 10/24/2014 12:30:00 PM : [Ext-Direct  ] 24.EF.05-->ISY/PLM Group=0, Max Hops=1, Hops Left=0
Fri 10/24/2014 12:30:00 PM : [iNST-TX-I1  ] 02 62 25 35 FF 0F 19 00
Fri 10/24/2014 12:30:00 PM : [iNST-ACK    ] 02 62 25.35.FF 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:01 PM : [iNST-SRX    ] 02 50 25.35.FF 2C.07.70 23 24 00           (00)
Fri 10/24/2014 12:30:01 PM : [std-Direct Ack] 25.35.FF-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:01 PM : [iNST-TX-I1  ] 02 62 25 39 34 0F 19 00
Fri 10/24/2014 12:30:01 PM : [iNST-ACK    ] 02 62 25.39.34 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:01 PM : [iNST-SRX    ] 02 50 25.39.34 2C.07.70 27 33 FF           (FF)
Fri 10/24/2014 12:30:01 PM : [std-Direct Ack] 25.39.34-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:01 PM : [iNST-TX-I1  ] 02 62 25 3D 28 0F 19 00
Fri 10/24/2014 12:30:01 PM : [iNST-ACK    ] 02 62 25.3D.28 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:01 PM : [iNST-SRX    ] 02 50 25.3D.28 2C.07.70 2B 4C 00           (00)
Fri 10/24/2014 12:30:01 PM : [std-Direct Ack] 25.3D.28-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:01 PM : [iNST-TX-I1  ] 02 62 25 43 7C 0F 19 00
Fri 10/24/2014 12:30:02 PM : [iNST-ACK    ] 02 62 25.43.7C 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:02 PM : [iNST-SRX    ] 02 50 25.43.7C 2C.07.70 2B 39 FF           (FF)
Fri 10/24/2014 12:30:02 PM : [std-Direct Ack] 25.43.7C-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:02 PM : [iNST-TX-I1  ] 02 62 25 44 F1 0F 19 00
Fri 10/24/2014 12:30:02 PM : [iNST-ACK    ] 02 62 25.44.F1 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:02 PM : [iNST-SRX    ] 02 50 25.44.F1 2C.07.70 2B 31 00           (00)
Fri 10/24/2014 12:30:02 PM : [std-Direct Ack] 25.44.F1-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:02 PM : [iNST-TX-I1  ] 02 62 25 45 0D 0F 19 00
Fri 10/24/2014 12:30:03 PM : [iNST-ACK    ] 02 62 25.45.0D 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:03 PM : [iNST-SRX    ] 02 50 25.45.0D 2C.07.70 23 32 FF           (FF)
Fri 10/24/2014 12:30:03 PM : [std-Direct Ack] 25.45.0D-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:03 PM : [iNST-TX-I1  ] 02 62 25 5C 57 0F 19 00
Fri 10/24/2014 12:30:03 PM : [iNST-ACK    ] 02 62 25.5C.57 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:03 PM : [iNST-SRX    ] 02 50 25.5C.57 2C.07.70 2B 21 00           (00)
Fri 10/24/2014 12:30:03 PM : [std-Direct Ack] 25.5C.57-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:03 PM : [iNST-TX-I1  ] 02 62 25 5D 94 0F 19 00
Fri 10/24/2014 12:30:04 PM : [iNST-ACK    ] 02 62 25.5D.94 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:04 PM : [iNST-SRX    ] 02 50 25.5D.94 2C.07.70 2B 05 00           (00)
Fri 10/24/2014 12:30:04 PM : [std-Direct Ack] 25.5D.94-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:04 PM : [iNST-TX-I1  ] 02 62 25 5D B7 0F 19 00
Fri 10/24/2014 12:30:04 PM : [iNST-ACK    ] 02 62 25.5D.B7 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:05 PM : [iNST-SRX    ] 02 50 25.5D.B7 2C.07.70 2B 42 FE           (FE)
Fri 10/24/2014 12:30:05 PM : [std-Direct Ack] 25.5D.B7-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:05 PM : [iNST-TX-I1  ] 02 62 25 62 7D 0F 19 00
Fri 10/24/2014 12:30:05 PM : [iNST-ACK    ] 02 62 25.62.7D 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:05 PM : [iNST-SRX    ] 02 50 25.62.7D 2C.07.70 2B 02 00           (00)
Fri 10/24/2014 12:30:05 PM : [std-Direct Ack] 25.62.7D-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:05 PM : [iNST-TX-I1  ] 02 62 25 64 6C 0F 19 00
Fri 10/24/2014 12:30:05 PM : [iNST-ACK    ] 02 62 25.64.6C 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:05 PM : [iNST-SRX    ] 02 50 25.64.6C 2C.07.70 2B 1B 00           (00)
Fri 10/24/2014 12:30:05 PM : [std-Direct Ack] 25.64.6C-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:05 PM : [iNST-TX-I1  ] 02 62 25 67 3F 0F 19 00
Fri 10/24/2014 12:30:06 PM : [iNST-ACK    ] 02 62 25.67.3F 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:06 PM : [iNST-SRX    ] 02 50 25.67.3F 2C.07.70 2B 02 FF           (FF)
Fri 10/24/2014 12:30:06 PM : [std-Direct Ack] 25.67.3F-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:06 PM : [iNST-TX-I1  ] 02 62 25 67 9A 0F 19 00
Fri 10/24/2014 12:30:06 PM : [iNST-ACK    ] 02 62 25.67.9A 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:06 PM : [iNST-SRX    ] 02 50 25.67.9A 2C.07.70 2B 01 00           (00)
Fri 10/24/2014 12:30:06 PM : [std-Direct Ack] 25.67.9A-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:06 PM : [iNST-TX-I1  ] 02 62 25 68 1E 0F 19 00
Fri 10/24/2014 12:30:07 PM : [iNST-ACK    ] 02 62 25.68.1E 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:07 PM : [iNST-SRX    ] 02 50 25.68.1E 2C.07.70 2B 46 FF    IOOFF  (FF)
Fri 10/24/2014 12:30:07 PM : [std-Direct Ack] 25.68.1E-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:07 PM : [iNST-TX-I1  ] 02 62 25 6A E4 0F 19 00
Fri 10/24/2014 12:30:07 PM : [iNST-ACK    ] 02 62 25.6A.E4 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:07 PM : [iNST-SRX    ] 02 50 25.6A.E4 2C.07.70 27 C5 00           (00)
Fri 10/24/2014 12:30:07 PM : [std-Direct Ack] 25.6A.E4-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:08 PM : [iNST-TX-I2CS] 02 62 25 6A E4 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1
Fri 10/24/2014 12:30:08 PM : [iNST-ACK    ] 02 62 25.6A.E4 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06        (00)
Fri 10/24/2014 12:30:08 PM : [iNST-SRX    ] 02 50 25.6A.E4 2C.07.70 2B 2E 00           (00)
Fri 10/24/2014 12:30:08 PM : [std-Direct Ack] 25.6A.E4-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:09 PM : [iNST-ERX    ] 02 51 25 6A E4 2C 07 70 16 2E 00 01 01 00 00 20 20 18 FF 7F 04 C8 00 04 00
Fri 10/24/2014 12:30:09 PM : [Ext-Direct  ] 25.6A.E4-->ISY/PLM Group=0, Max Hops=2, Hops Left=1
Fri 10/24/2014 12:30:09 PM : [iNST-TX-I1  ] 02 62 25 6B 6A 0F 19 00
Fri 10/24/2014 12:30:09 PM : [iNST-ACK    ] 02 62 25.6B.6A 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:10 PM : [iNST-SRX    ] 02 50 25.6B.6A 2C.07.70 27 4A FF           (FF)
Fri 10/24/2014 12:30:10 PM : [std-Direct Ack] 25.6B.6A-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:10 PM : [iNST-TX-I2CS] 02 62 25 6B 6A 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1
Fri 10/24/2014 12:30:10 PM : [iNST-ACK    ] 02 62 25.6B.6A 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06        (00)
Fri 10/24/2014 12:30:10 PM : [iNST-SRX    ] 02 50 25.6B.6A 2C.07.70 27 2E 00           (00)
Fri 10/24/2014 12:30:11 PM : [iNST-ERX    ] 02 51 25 6B 6A 2C 07 70 11 2E 00 01 01 00 00 20 20 1C FF 0A 24 3F 00 24 00
Fri 10/24/2014 12:30:11 PM : [Ext-Direct  ] 25.6B.6A-->ISY/PLM Group=0, Max Hops=1, Hops Left=0
Fri 10/24/2014 12:30:11 PM : [iNST-TX-I1  ] 02 62 25 6D 90 0F 19 00
Fri 10/24/2014 12:30:11 PM : [iNST-ACK    ] 02 62 25.6D.90 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:11 PM : [iNST-SRX    ] 02 50 25.6D.90 2C.07.70 27 AD 00           (00)
Fri 10/24/2014 12:30:11 PM : [std-Direct Ack] 25.6D.90-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:11 PM : [iNST-TX-I2CS] 02 62 25 6D 90 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1
Fri 10/24/2014 12:30:11 PM : [iNST-ACK    ] 02 62 25.6D.90 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06        (00)
Fri 10/24/2014 12:30:12 PM : [iNST-SRX    ] 02 50 25.6D.90 2C.07.70 2B 2E 00           (00)
Fri 10/24/2014 12:30:12 PM : [std-Direct Ack] 25.6D.90-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:12 PM : [iNST-ERX    ] 02 51 25 6D 90 2C 07 70 11 2E 00 01 01 00 00 20 20 1F FF 7F 30 F0 00 30 00
Fri 10/24/2014 12:30:12 PM : [Ext-Direct  ] 25.6D.90-->ISY/PLM Group=0, Max Hops=1, Hops Left=0
Fri 10/24/2014 12:30:12 PM : [iNST-TX-I1  ] 02 62 26 93 FE 0F 19 00
Fri 10/24/2014 12:30:12 PM : [iNST-ACK    ] 02 62 26.93.FE 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:12 PM : [iNST-SRX    ] 02 50 26.93.FE 2C.07.70 2B 00 00           (00)
Fri 10/24/2014 12:30:12 PM : [std-Direct Ack] 26.93.FE-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:12 PM : [iNST-TX-I1  ] 02 62 28 71 03 0F 19 00
Fri 10/24/2014 12:30:12 PM : [iNST-ACK    ] 02 62 28.71.03 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:13 PM : [iNST-SRX    ] 02 50 28.71.03 2C.07.70 2B 04 00           (00)
Fri 10/24/2014 12:30:13 PM : [std-Direct Ack] 28.71.03-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:13 PM : [iNST-TX-I1  ] 02 62 28 72 A4 0F 19 00
Fri 10/24/2014 12:30:13 PM : [iNST-ACK    ] 02 62 28.72.A4 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:13 PM : [iNST-SRX    ] 02 50 28.72.A4 2C.07.70 2B 23 00           (00)
Fri 10/24/2014 12:30:13 PM : [std-Direct Ack] 28.72.A4-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:13 PM : [iNST-TX-I1  ] 02 62 28 7B 44 0F 19 00
Fri 10/24/2014 12:30:13 PM : [iNST-ACK    ] 02 62 28.7B.44 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:14 PM : [iNST-SRX    ] 02 50 28.7B.44 2C.07.70 2B 13 00    LTOFFRR(00)
Fri 10/24/2014 12:30:14 PM : [std-Direct Ack] 28.7B.44-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:14 PM : [D2D EVENT   ] Event [28 7B 44 1] [sT] [0] uom=0 prec=-1
Fri 10/24/2014 12:30:14 PM : [  28 7B 44 1]       ST   0
Fri 10/24/2014 12:30:14 PM : [iNST-TX-I1  ] 02 62 28 7E 50 0F 19 00
Fri 10/24/2014 12:30:14 PM : [iNST-ACK    ] 02 62 28.7E.50 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:14 PM : [iNST-SRX    ] 02 50 28.7E.50 2C.07.70 27 1C 00           (00)
Fri 10/24/2014 12:30:14 PM : [std-Direct Ack] 28.7E.50-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:14 PM : [iNST-TX-I1  ] 02 62 28 7F 62 0F 19 00
Fri 10/24/2014 12:30:14 PM : [iNST-ACK    ] 02 62 28.7F.62 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:15 PM : [iNST-SRX    ] 02 50 28.7F.62 2C.07.70 23 0C 00           (00)
Fri 10/24/2014 12:30:15 PM : [std-Direct Ack] 28.7F.62-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:15 PM : [iNST-TX-I1  ] 02 62 28 80 52 0F 19 00
Fri 10/24/2014 12:30:15 PM : [iNST-ACK    ] 02 62 28.80.52 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:15 PM : [iNST-SRX    ] 02 50 28.80.52 2C.07.70 27 0C 00           (00)
Fri 10/24/2014 12:30:15 PM : [std-Direct Ack] 28.80.52-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:15 PM : [iNST-TX-I1  ] 02 62 28 83 4F 0F 19 00
Fri 10/24/2014 12:30:15 PM : [iNST-ACK    ] 02 62 28.83.4F 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:16 PM : [iNST-SRX    ] 02 50 28.83.4F 2C.07.70 23 0D 00           (00)
Fri 10/24/2014 12:30:16 PM : [std-Direct Ack] 28.83.4F-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:16 PM : [iNST-TX-I1  ] 02 62 28 87 73 0F 19 00
Fri 10/24/2014 12:30:16 PM : [iNST-ACK    ] 02 62 28.87.73 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:16 PM : [iNST-SRX    ] 02 50 28.87.73 2C.07.70 2B 13 00    LTOFFRR(00)
Fri 10/24/2014 12:30:16 PM : [std-Direct Ack] 28.87.73-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:16 PM : [iNST-TX-I1  ] 02 62 28 87 B8 0F 19 00
Fri 10/24/2014 12:30:16 PM : [iNST-ACK    ] 02 62 28.87.B8 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:17 PM : [iNST-SRX    ] 02 50 28.87.B8 2C.07.70 2B 21 00           (00)
Fri 10/24/2014 12:30:17 PM : [std-Direct Ack] 28.87.B8-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:17 PM : [iNST-TX-I1  ] 02 62 28 8B 70 0F 19 00
Fri 10/24/2014 12:30:17 PM : [iNST-ACK    ] 02 62 28.8B.70 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:17 PM : [iNST-SRX    ] 02 50 28.8B.70 2C.07.70 2B 0F 00    PING   (00)
Fri 10/24/2014 12:30:17 PM : [std-Direct Ack] 28.8B.70-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:17 PM : [iNST-TX-I1  ] 02 62 28 8C 3D 0F 19 00
Fri 10/24/2014 12:30:17 PM : [iNST-ACK    ] 02 62 28.8C.3D 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:18 PM : [iNST-SRX    ] 02 50 28.8C.3D 2C.07.70 2B 1E 00           (00)
Fri 10/24/2014 12:30:18 PM : [std-Direct Ack] 28.8C.3D-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:18 PM : [iNST-TX-I1  ] 02 62 28 8E A8 0F 19 00
Fri 10/24/2014 12:30:18 PM : [iNST-ACK    ] 02 62 28.8E.A8 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:18 PM : [iNST-SRX    ] 02 50 28.8E.A8 2C.07.70 2B 14 00    LTOFF-F(00)
Fri 10/24/2014 12:30:18 PM : [std-Direct Ack] 28.8E.A8-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:18 PM : [iNST-TX-I1  ] 02 62 28 8E DB 0F 19 00
Fri 10/24/2014 12:30:18 PM : [iNST-ACK    ] 02 62 28.8E.DB 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:19 PM : [iNST-SRX    ] 02 50 28.8E.DB 2C.07.70 2B 02 00           (00)
Fri 10/24/2014 12:30:19 PM : [std-Direct Ack] 28.8E.DB-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Fri 10/24/2014 12:30:19 PM : [iNST-TX-I1  ] 02 62 29 45 FA 0F 19 00
Fri 10/24/2014 12:30:19 PM : [iNST-ACK    ] 02 62 29.45.FA 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:20 PM : [iNST-SRX    ] 02 50 29.45.FA 2C.07.70 27 AE FF           (FF)
Fri 10/24/2014 12:30:20 PM : [std-Direct Ack] 29.45.FA-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:20 PM : [iNST-TX-I2CS] 02 62 29 45 FA 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1
Fri 10/24/2014 12:30:20 PM : [iNST-ACK    ] 02 62 29.45.FA 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06        (00)
Fri 10/24/2014 12:30:21 PM : [iNST-SRX    ] 02 50 29.45.FA 2C.07.70 27 2E 00           (00)
Fri 10/24/2014 12:30:21 PM : [std-Direct Ack] 29.45.FA-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:21 PM : [iNST-ERX    ] 02 51 29 45 FA 2C 07 70 11 2E 00 01 01 00 00 20 20 18 FF 05 34 D3 00 34 00
Fri 10/24/2014 12:30:21 PM : [Ext-Direct  ] 29.45.FA-->ISY/PLM Group=0, Max Hops=1, Hops Left=0
Fri 10/24/2014 12:30:21 PM : [iNST-TX-I1  ] 02 62 2B F8 BB 0F 19 01
Fri 10/24/2014 12:30:21 PM : [iNST-ACK    ] 02 62 2B.F8.BB 0F 19 01 06          LTSREQ (01)
Fri 10/24/2014 12:30:22 PM : [iNST-SRX    ] 02 50 2B.F8.BB 2C.07.70 23 00 01           (01)
Fri 10/24/2014 12:30:22 PM : [std-Direct Ack] 2B.F8.BB-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:22 PM : [iNST-TX-I1  ] 02 62 2B F8 BB 0F 19 00
Fri 10/24/2014 12:30:22 PM : [iNST-ACK    ] 02 62 2B.F8.BB 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:22 PM : [iNST-SRX    ] 02 50 2B.F8.BB 2C.07.70 27 00 00           (00)
Fri 10/24/2014 12:30:22 PM : [std-Direct Ack] 2B.F8.BB-->ISY/PLM Group=0, Max Hops=3, Hops Left=1
Fri 10/24/2014 12:30:22 PM : [iNST-TX-I1  ] 02 62 2B F8 BB 0F 19 01
Fri 10/24/2014 12:30:22 PM : [iNST-ACK    ] 02 62 2B.F8.BB 0F 19 01 06          LTSREQ (01)
Fri 10/24/2014 12:30:23 PM : [iNST-SRX    ] 02 50 2B.F8.BB 2C.07.70 23 00 01           (01)
Fri 10/24/2014 12:30:23 PM : [std-Direct Ack] 2B.F8.BB-->ISY/PLM Group=0, Max Hops=3, Hops Left=0
Fri 10/24/2014 12:30:23 PM : [iNST-TX-I1  ] 02 62 2B F8 BB 0F 19 00
Fri 10/24/2014 12:30:23 PM : [iNST-ACK    ] 02 62 2B.F8.BB 0F 19 00 06          LTSREQ (LIGHT)
Fri 10/24/2014 12:30:23 PM : [iNST-SRX    ] 02 50 2B.F8.BB 2C.07.70 23 00 00           (00)
Edited by davbow
Based on the Query response the garage door should be Open as the Sensor node is On for both queries.
Comm with the I/O Linc is at the very edge of working.  The Hops Left=0 means any interference or slight drop in comm quality could lose a state change.