Haven't done much all summer with my ISY and I can't believe I'm this rusty...

 

I've created a scene with an On/Off module (closing and opening my N/O main water shutoff valve) and a leak sensor-wet.  Added the leak sensor as a controller and the On/Off module as a responder.

 

When I hit the set button once on the leak sensor, it sets the leak sensor as wet-on and the On/Off module goes on.

When I hit the set button again on the leak sensor, it sets the leak sensor as wet-off but the On/Off module stays on.  I would like for the On/Off module to follow the leak sensor wet conditions.

 

I know I can do this using a program, but was hoping I could do it with a scene...

 

What did I do wrong?

 

Thanks once again in advance

 

PhanTomiZ

Posted (edited)

Although the ISY marks the Wet node Off the Leak Sensor did not send that command.  The Leak Sensor sent a Dry On so the ISY marked the Wet node Off.  Marking the Wet node Off in the ISY does not generate a Scene Off command.

 

You can run a LEVEL 3 event viewer to see that the Leak Sensor did not send an Off message for the Wet node. 

Edited by LeeG
Posted

Just receiving two new Leak sensors and having two  previous I have found they operate quite differently.

 

On the two newer units (v.41) the pushbutton sends out Dry On, every time.

On the two older units (v.43) the pushbutton sends out Wet On for a quick tap each time and Dry On for a longer push each time.

Posted

Just receiving two new Leak sensors and having two  previous I have found they operate quite differently.

 

On the two newer units (v.41) the pushbutton sends out Dry On, every time.

On the two older units (v.43) the pushbutton sends out Wet On for a quick tap each time and Dry On for a longer push each time.

All three of my leak sensors are (v.41).  

Noticed that if: 

 

I tap once, I get a DON 1

I tap again, I get a DON 2

 

But if I tap once, I get a DON 1

If I leave it for about 5 seconds, I get a DON 4

Posted

Although the ISY marks the Wet node Off the Leak Sensor did not send that command.  The Leak Sensor sent a Dry On so the ISY marked the Wet node Off.  Marking the Wet node Off in the ISY does not generate a Scene Off command.

 

You can run a LEVEL 3 event viewer to see that the Leak Sensor did not send an Off message for the Wet node. 

LeeG,

 

Where do I find the Wiki that describes all the codes of the event viewer?  I thought I saw it somewhere, but I can't find it when I need it.  Terrible thing this getting old.....

 

Anyway, here is the event viewer...Can you tell me what it means?

 

 

 
Wed 09/23/2015 09:38:17 AM : [iNST-SRX    ] 02 50 2E.09.48 00.00.02 CF 11 02    LTONRR (02)
Wed 09/23/2015 09:38:17 AM : [std-Group   ] 2E.09.48-->Group=2, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:17 AM : [D2D EVENT   ] Event [2E 9 48 2] [DON] [2] uom=0 prec=-1
Wed 09/23/2015 09:38:17 AM : [   2E 9 48 2]      DON   2
Wed 09/23/2015 09:38:17 AM : [D2D EVENT   ] Event [2D 1 8E 1] [sT] [255] uom=0 prec=-1
Wed 09/23/2015 09:38:17 AM : [   2D 1 8E 1]       ST 255
Wed 09/23/2015 09:38:17 AM : [D2D EVENT   ] Event [2E 9 48 2] [sT] [255] uom=0 prec=-1
Wed 09/23/2015 09:38:17 AM : [   2E 9 48 2]       ST 255
Wed 09/23/2015 09:38:17 AM : [D2D-CMP 0064] STS [2E 9 48 2] ST op=1 Event(val=255 uom=0 prec=-1) is Condition(val=255 uom=0 prec=-1) --> true
Wed 09/23/2015 09:38:17 AM : [D2D EVENT   ] Event [2E 9 48 1] [sT] [0] uom=0 prec=-1
Wed 09/23/2015 09:38:17 AM : [   2E 9 48 1]       ST   0
Wed 09/23/2015 09:38:17 AM : [D2D-CMP 0064] STS [2E 9 48 1] ST op=1 Event(val=0 uom=0 prec=-1) is Condition(val=0 uom=0 prec=-1) --> true
Wed 09/23/2015 09:38:17 AM : [iNST-SRX    ] 02 50 2E.09.48 00.00.02 CF 11 02    LTONRR (02)
Wed 09/23/2015 09:38:17 AM : [std-Group   ] 2E.09.48-->Group=2, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:17 AM : [iNST-DUP    ] Previous message ignored.
Wed 09/23/2015 09:38:18 AM : [iNST-SRX    ] 02 50 2E.09.48 33.5E.55 45 11 02    LTONRR (02)
Wed 09/23/2015 09:38:18 AM : [std-Cleanup ] 2E.09.48-->ISY/PLM Group=2, Max Hops=1, Hops Left=1
Wed 09/23/2015 09:38:18 AM : [iNST-DUP    ] Previous message ignored.
Wed 09/23/2015 09:38:18 AM : [iNST-SRX    ] 02 50 2E.09.48 11.02.02 CF 06 00           (00)
Wed 09/23/2015 09:38:18 AM : [std-Group   ] 2E.09.48-->11.02.02, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:18 AM : [iNST-INFO   ] Previous message ignored.
Wed 09/23/2015 09:38:18 AM : [iNST-SRX    ] 02 50 2E.09.48 11.02.02 CF 06 00           (00)
Wed 09/23/2015 09:38:18 AM : [std-Group   ] 2E.09.48-->11.02.02, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:18 AM : [iNST-INFO   ] Previous message ignored.
Wed 09/23/2015 09:38:21 AM : [iNST-SRX    ] 02 50 2E.09.48 00.00.01 CB 11 01    LTONRR (01)
Wed 09/23/2015 09:38:21 AM : [std-Group   ] 2E.09.48-->Group=1, Max Hops=3, Hops Left=2
Wed 09/23/2015 09:38:21 AM : [D2D EVENT   ] Event [2E 9 48 1] [DON] [1] uom=0 prec=-1
Wed 09/23/2015 09:38:21 AM : [   2E 9 48 1]      DON   1
Wed 09/23/2015 09:38:21 AM : [D2D EVENT   ] Event [2E 9 48 1] [sT] [255] uom=0 prec=-1
Wed 09/23/2015 09:38:21 AM : [   2E 9 48 1]       ST 255
Wed 09/23/2015 09:38:21 AM : [D2D-CMP 0064] STS [2E 9 48 1] ST op=1 Event(val=255 uom=0 prec=-1) is Condition(val=0 uom=0 prec=-1) --> false
Wed 09/23/2015 09:38:21 AM : [D2D EVENT   ] Event [2E 9 48 2] [sT] [0] uom=0 prec=-1
Wed 09/23/2015 09:38:21 AM : [   2E 9 48 2]       ST   0
Wed 09/23/2015 09:38:21 AM : [D2D-CMP 0064] STS [2E 9 48 2] ST op=1 Event(val=0 uom=0 prec=-1) is Condition(val=255 uom=0 prec=-1) --> false
Wed 09/23/2015 09:38:21 AM : [iNST-SRX    ] 02 50 2E.09.48 00.00.01 CF 11 01    LTONRR (01)
Wed 09/23/2015 09:38:21 AM : [std-Group   ] 2E.09.48-->Group=1, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:21 AM : [iNST-DUP    ] Previous message ignored.
Wed 09/23/2015 09:38:21 AM : [iNST-SRX    ] 02 50 2E.09.48 33.5E.55 45 11 01    LTONRR (01)
Wed 09/23/2015 09:38:21 AM : [std-Cleanup ] 2E.09.48-->ISY/PLM Group=1, Max Hops=1, Hops Left=1
Wed 09/23/2015 09:38:21 AM : [iNST-DUP    ] Previous message ignored.
Wed 09/23/2015 09:38:21 AM : [iNST-SRX    ] 02 50 2E.09.48 11.01.01 CF 06 00           (00)
Wed 09/23/2015 09:38:21 AM : [std-Group   ] 2E.09.48-->11.01.01, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:21 AM : [iNST-INFO   ] Previous message ignored.
Wed 09/23/2015 09:38:22 AM : [iNST-SRX    ] 02 50 2E.09.48 11.01.01 CF 06 00           (00)
Wed 09/23/2015 09:38:22 AM : [std-Group   ] 2E.09.48-->11.01.01, Max Hops=3, Hops Left=3
Wed 09/23/2015 09:38:22 AM : [iNST-INFO   ] Previous message ignored.
 
Posted

Although the ISY marks the Wet node Off the Leak Sensor did not send that command.  The Leak Sensor sent a Dry On so the ISY marked the Wet node Off.  Marking the Wet node Off in the ISY does not generate a Scene Off command.

 

You can run a LEVEL 3 event viewer to see that the Leak Sensor did not send an Off message for the Wet node. 

So does this mean I won't be able to use a scene, but rather a program to shut the water off in the event of a flood/leak detected?

Posted

The DON 4 is the Heartbeat test message. If there is a pause between taps whether the DON 1 or DON 2 test is sent, the DON 4 will follow. This is the expected response.

 

Latest Leak Sensor firmware does not send the Heartbeat test message with the Set button.

Posted (edited)

All three of my leak sensors are (v.41).  

Noticed that if: 

 

I tap once, I get a DON 1

I tap again, I get a DON 2

 

But if I tap once, I get a DON 1

If I leave it for about 5 seconds, I get a DON 4

Thanks

I assume a DON 1/2 would be a wet/dry signal.

What would a DON 4 be? Perhaps a heartbeat?

 

Maybe I got fooled. Did you try the short and long press. I found anything longer than about 1/2 second a long press.

 

Edit: I saw your LeeG response above.

Edited by larryllix
Posted (edited)

 

Wed 09/23/2015 09:38:17 AM : [iNST-SRX ] 02 50 2E.09.48 00.00.02 CF 11 02 LTONRR (02) - Group 2 (Wet) - On 11

Wed 09/23/2015 09:38:17 AM : [std-Group ] 2E.09.48-->Group=2, Max Hops=3, Hops Left=3

Wed 09/23/2015 09:38:17 AM : [D2D EVENT ] Event [2E 9 48 2] [DON] [2] uom=0 prec=-1

Wed 09/23/2015 09:38:17 AM : [ 2E 9 48 2] DON 2

Wed 09/23/2015 09:38:17 AM : [D2D EVENT ] Event [2D 1 8E 1] [sT] [255] uom=0 prec=-1

Wed 09/23/2015 09:38:17 AM : [ 2D 1 8E 1] ST 255

Wed 09/23/2015 09:38:17 AM : [D2D EVENT ] Event [2E 9 48 2] [sT] [255] uom=0 prec=-1

Wed 09/23/2015 09:38:17 AM : [ 2E 9 48 2] ST 255

Wed 09/23/2015 09:38:17 AM : [D2D-CMP 0064] STS [2E 9 48 2] ST op=1 Event(val=255 uom=0 prec=-1) is Condition(val=255 uom=0 prec=-1) --> true

Wed 09/23/2015 09:38:17 AM : [D2D EVENT ] Event [2E 9 48 1] [sT] [0] uom=0 prec=-1

Wed 09/23/2015 09:38:17 AM : [ 2E 9 48 1] ST 0

Wed 09/23/2015 09:38:17 AM : [D2D-CMP 0064] STS [2E 9 48 1] ST op=1 Event(val=0 uom=0 prec=-1) is Condition(val=0 uom=0 prec=-1) --> true

Wed 09/23/2015 09:38:17 AM : [iNST-SRX ] 02 50 2E.09.48 00.00.02 CF 11 02 LTONRR (02)

Wed 09/23/2015 09:38:17 AM : [std-Group ] 2E.09.48-->Group=2, Max Hops=3, Hops Left=3

Wed 09/23/2015 09:38:17 AM : [iNST-DUP ] Previous message ignored.

Wed 09/23/2015 09:38:18 AM : [iNST-SRX ] 02 50 2E.09.48 33.5E.55 45 11 02 LTONRR (02)

Wed 09/23/2015 09:38:18 AM : [std-Cleanup ] 2E.09.48-->ISY/PLM Group=2, Max Hops=1, Hops Left=1

Wed 09/23/2015 09:38:18 AM : [iNST-DUP ] Previous message ignored.

Wed 09/23/2015 09:38:18 AM : [iNST-SRX ] 02 50 2E.09.48 11.02.02 CF 06 00 (00)

Wed 09/23/2015 09:38:18 AM : [std-Group ] 2E.09.48-->11.02.02, Max Hops=3, Hops Left=3

Wed 09/23/2015 09:38:18 AM : [iNST-INFO ] Previous message ignored.

Wed 09/23/2015 09:38:18 AM : [iNST-SRX ] 02 50 2E.09.48 11.02.02 CF 06 00 (00)

Wed 09/23/2015 09:38:18 AM : [std-Group ] 2E.09.48-->11.02.02, Max Hops=3, Hops Left=3

Wed 09/23/2015 09:38:18 AM : [iNST-INFO ] Previous message ignored.

Wed 09/23/2015 09:38:21 AM : [iNST-SRX ] 02 50 2E.09.48 00.00.01 CB 11 01 LTONRR (01) - Group 1 (Dry) - On 11

Wed 09/23/2015 09:38:21 AM : [std-Group ] 2E.09.48-->Group=1, Max Hops=3, Hops Left=2

Wed 09/23/2015 09:38:21 AM : [D2D EVENT ] Event [2E 9 48 1] [DON] [1] uom=0 prec=-1

Wed 09/23/2015 09:38:21 AM : [ 2E 9 48 1] DON 1

Wed 09/23/2015 09:38:21 AM : [D2D EVENT ] Event [2E 9 48 1] [sT] [255] uom=0 prec=-1

Wed 09/23/2015 09:38:21 AM : [ 2E 9 48 1] ST 255

Wed 09/23/2015 09:38:21 AM : [D2D-CMP 0064] STS [2E 9 48 1] ST op=1 Event(val=255 uom=0 prec=-1) is Condition(val=0 uom=0 prec=-1) --> false

Wed 09/23/2015 09:38:21 AM : [D2D EVENT ] Event [2E 9 48 2] [sT] [0] uom=0 prec=-1

Wed 09/23/2015 09:38:21 AM : [ 2E 9 48 2] ST 0

Wed 09/23/2015 09:38:21 AM : [D2D-CMP 0064] STS [2E 9 48 2] ST op=1 Event(val=0 uom=0 prec=-1) is Condition(val=255 uom=0 prec=-1) --> false

Wed 09/23/2015 09:38:21 AM : [iNST-SRX ] 02 50 2E.09.48 00.00.01 CF 11 01 LTONRR (01)

Wed 09/23/2015 09:38:21 AM : [std-Group ] 2E.09.48-->Group=1, Max Hops=3, Hops Left=3

Wed 09/23/2015 09:38:21 AM : [iNST-DUP ] Previous message ignored.

Wed 09/23/2015 09:38:21 AM : [iNST-SRX ] 02 50 2E.09.48 33.5E.55 45 11 01 LTONRR (01)

Wed 09/23/2015 09:38:21 AM : [std-Cleanup ] 2E.09.48-->ISY/PLM Group=1, Max Hops=1, Hops Left=1

Wed 09/23/2015 09:38:21 AM : [iNST-DUP ] Previous message ignored.

Edited by LeeG
Posted

"So does this mean I won't be able to use a scene, but rather a program to shut the water off in the event of a flood/leak detected?"

 

Correct.  The Leak Sensor does not send a Dry Off nor a Wet Off.  It sends Dry On or Wet On only at your firmware.  Later firmware sends a Wet On only.  The latest Leak Sensor firmware does not cycle back to Dry On if the condition goes back to Dry.

Posted

"So does this mean I won't be able to use a scene, but rather a program to shut the water off in the event of a flood/leak detected?"

 

Correct.  The Leak Sensor does not send a Dry Off nor a Wet Off.  It sends Dry On or Wet On only at your firmware.  Later firmware sends a Wet On only.  The latest Leak Sensor firmware does not cycle back to Dry On if the condition goes back to Dry.

 

How about a full description Wiki for the event viewer in order to decipher the code?  Is there one?

 

Thanks

PhanTomiZ

Posted (edited)

Not that I have seen.

 

One of the issues is that to understand the event viewer requires a knowledge of Insteon.  I doubt UDI ever plans on that level of information.   Need to look at SmartLabs documents to learn/understand Insteon.  