ahwman Posted January 5, 2012 Posted January 5, 2012 After installing and syncing a TriggerLinc device to my ISY, I noticed that there is a "Closed" and "Opened" entry for it. The strange part is that the status for both shows as "On". The "Opened" side seems to change with the opening/closing of the circuit however the "Closed" entry doesn't seems to change. Should I simply use the "Opened" entry and disregard the "Closed" one?
LeeG Posted January 5, 2012 Posted January 5, 2012 The TriggerLinc has an optional operating mode where two nodes are used. The Open node gets On indications, the Closed node gets Off indications. There is a single jumper on the TriggerLinc printed circuit board that controls the option. The TriggerLinc User Guide covers this alternate method. Yes, using the Open node only is the normal approach. Don't know of anyone who uses a TriggerLinc in the alternate operating mode. May be useful where there is no intelligent controller but the second node is of no use when using an ISY.