Garage Door / Switch not responding.
My mistake, sorry. That is the newest OutletLinc that controls both outlets and is Dual Band. The older OutletLinc 2472D (dimmer) is also Dual band. The 2473S relay is powerline only.
-
Event Viewer "Magic Decoder Ring" ?
"I have always wondered what the Hops Left and Max Hops numbers meant." Max Hops indicates the number of devices that are allow to repeat message at full strength. The larger Max Hops the longer it takes a message to arrive at its destination. Hops Left indicates how many devices (Hops) had to repeat the message. An Insteon Controller device normally starts out with Max Hops=1 for best Insteon network speed. If the Responder does not ACK, the Controller bumps the Max Hops count and tries again. There is an insteondetails.pdf doc on insteon.com that covers this in detail. Shows Insteon network speed possible at each Max Hops count.
-
Event Viewer "Magic Decoder Ring" ?
Normally Hops Left=0 is bad but in this case it is on a message that has Max Hops=1 so no comm problem indicated. At insteon.com there is an insteondetails.pdf doc that covers some of the Insteon messages. Also SmartLabs has released what was confidential information (no longer confidential) covering Insteon internals. insteon.com/developer/#devdocs
-
Garage Door / Switch not responding.
That 2663-222 OutletLinc is also powerline only. The Hops Left=x number changing frequently indicates poor comm to the I/O Linc. A Dual Band device may help as was already suggested. It would have to be in RF range of another Dual Band device.
-
How to assign "scene" to a button on KeypadLinc Dimmer in ISY
That is correct. Define an ISY Scene and add a KeypadLinc button as a Controller. Drag the KeypadLinc button to the ISY Scene. It will display in Red below the ISY Scene name.
-
How to assign "scene" to a button on KeypadLinc Dimmer in ISY
Click on the + sign to left of KeypadLinc. If using the device defined on the 99i it should be deleted and added back as 3.3.10 was not aware of the latest KeypadLinc device type.
-
View/Set Elk Alarm State with KeypadLinc
I do not have ELK so cannot help with Query result.
-
View/Set Elk Alarm State with KeypadLinc
The "If Control" as written has a True only evaluation so the Else clause is never executed. If Control 'Keypad - Alarm' is switched On And Control 'Keypad - Alarm' is not switched Off Then Set Elk Area 'Home' Arm Night Instant Else Set Elk Area 'Home' Query
-
Remotes & Keypadlinc
On 4.2.23 the KeypadLinc Relay shows On in Program Test1 - [iD 0025][Parent 0001][Not Enabled] If Status 'ICON Dimmer 1' is not 30% Then Repeat 3 times Set Scene 'Scene B' On Set 'SwitchLinc Dimmer DB' 100 (Beep Duration) Wait 2 seconds Set Scene 'Scene B' Off Wait 2 seconds Set 'KeypadLinc Relay' On Else Send X10 'A1/Off (11)'
-
Can you make a dimmer, beep by a program?
My 2477D SwitchLinc Dimmer at hardware 7.6, firmware v.44 Beeps. Can you post the Program as well as an Event Viewer trace at LEVEL 3 showing the Beep command.
-
Curious Folder Items
Look at page 15 in ISY User Guide for what it looked like originally. "Network" is/was the first Icon with "My Lighting" the second. My Lighting indicates the configuration came from a 99i that was migrated to a 994i. A configuration totally from a 994i has "ISY" rather than "My Lighting"
-
Can you make a dimmer, beep by a program?
What is the dimmer name/number and firmware? I have many KeypadLincs that do not have Beep feature. Also the Beep is not very loud.
-
Difference between Insteon keypad dimmer and keypadlinc?
The Keypad Dimmer is a later device which may have some feature differences such as Beep, etc. Not saying Beep is different, would need to compare the advertised features of both. The underlying function of a KeypadLinc and Keypad Dimmer are the same. SmartLabs changes the name of devices rather frequently lately. There is a 6 and 8 button Keypad Dimmer, just as there is a 6 and 8 button KeypadLinc
-
PLM Restore with Disabled Devices
blueman2 Thanks for the update. That is how I thought it worked which the Show ISY Links Table confirmed.
-
Can't link ISY994 to 2477D
The antenna's are generally on the back of the device. It can be seen when looking through the clear plastic back. This means an RF signal has to pass through two sets of electronics if the nearest Dual Band is across the room. If mounted in metal electrical boxes it further reduces the range. I do not have an RF range in mind. That is why I prefer to use a pair of Access Points (now call Range Extenders) which plug in and serve to couple the 120v legs. I locate them near the power panel so they have clear line of site. Others think that with the volume of Dual Band devices installed now days the Access Points are over kill. The reality is whether the installed devices work together.
-
PLM Restore with Disabled Devices
stusviews "Why not wait until you use/need them?" What makes you think we are not waiting?
-
Can't link ISY994 to 2477D
Moving the PLM plug point verified the SwitchLinc was not the source of the Extended message problem. Extended messages are carried by RF. The actual cause of the Extended message problem has not been identified, only verified it is not the SwitchLinc itself. Put the PLM into Set button 4 tap beacon test and see if the SwitchLinc indicates it is on the same or opposite 120v leg.
-
PLM Restore with Disabled Devices
Do a Show ISY Links Table for one of the Disabled devices. Do the links with PLM addresses have the old or new PLM address. I'm assuming the ISY Links Table will have the new PLM address.
-
Can't link ISY994 to 2477D
That should not be correct. Range Extenders (Access Points) couple the two 120v legs using RF. It would not be possible to program I2CS and some I2 devices if Extended messages were not carried over RF.
-
Can't link ISY994 to 2477D
In the Scene definition there is a Scene Name followed by all the Controllers of the Scene. These nodes will be in Red. Click the first Red Controller node below Scene name and set the Responder On Level as desired. Each Red Controller has a unique set of Responder On Levels. Click on each Red Controller and set the Responder On Level as desired.
-
Can't link ISY994 to 2477D
Good set of questions. I asked them in post 15. Perhaps if enough folks ask them they will eventually be answered.
-
Can't link ISY994 to 2477D
It is in the SwitchLinc Owner's manual.
-
8 button KPL shows up as 5 button
rich.curl The KeypadLinc is manufactured as a 6 button device, with a "Cat"egory, "Sub-cat"egory (device type) for a 6 button KPL. This is true regardless of how the device is configured to operate (as 6 button or 8 button). If there are 8 nodes it is configured for 8 button operation even though it is still considered a 6 button KPL and shows as a 6 button device type. If the device is Factory Reset it returns to 6 button mode and would have to be reconfigured for 8 button mode. Here is an 8 button KPL showing an 8 button device type on line 2, right side of display, even though configured for 6 button operation with 5 nodes.
-
PLM Failure Modes, and whether to wait for UDI's PLM
ZWave is not causing Insteon comm issues. ZWave does not use the PLM nor the powerline. If an Insteon network problem all the normal possibilities exist. Something absorbing the Insteon signal, something adding noise to powerline. All the issues that are covered in the forum. Look for patterns on the same electrical circuit.
-
Scene works intermitently
Try a Wait 2 seconds to allow all the commands from the IO Linc Sensors to complete Program: "Garage Door Open" - if "Garage Door Sensor 1" OR 2 is ON - then Wait 2 seconds set scene "Garage Door Open" ON - else <nil>