currieg Posted November 3, 2013 Posted November 3, 2013 When I do first boot up the ISY a get an message stating: "Your system is in Safe Mode"... But I can access the configuration page, etc. => Then when I go to the Program page I get the Error message: "Could not open File" [/CONF/INSTENG.OPT]. It looks like I may be missing a configuration file? Where would I find it? Also if I try to save a program (such as Query All) to my new ISY-994i I get this Error message: Invalid/incorrect program Key [HTTP]] I seem to be able to connect to the ISY-994i fine and adjust the Configuration, but when I try to save the Query All program I get the error message... I have not been able to figure out what is wrong / missing? Please help... Thanks!
LeeG Posted November 3, 2013 Posted November 3, 2013 Safe Mode usually indicates the PLM cannot be accessed. What ISY front panel LEDs are On? The ISY is not functional without a working PLM.
currieg Posted November 3, 2013 Author Posted November 3, 2013 The two Left Blue LEDs are on (Pwr & Rx)... I have re-booted (power off => on) a number of times. Also I have checked PLM connection cable? Thanks!
LeeG Posted November 3, 2013 Posted November 3, 2013 Where was the ISY and PLM obtained? Try another cable between the PLM and the ISY. The ISY will have to be rebooted after the installing the new PLM cable. The RX LED On steady indicates the ISY cannot communicate with the PLM. The ISY enters Safe Mode when this occurs. The various symptoms noted before are the result of not being able to communicate with the PLM. Once PLM communication is established those symptoms should no longer exist.
Brian H Posted November 3, 2013 Posted November 3, 2013 Is the LED on the PLM look normal? Mine is Green. Another possibility is the PLM has died. We have recently seen reports of them dying with little run time on them.
currieg Posted November 3, 2013 Author Posted November 3, 2013 Yes the green LED on the PLM is on... Thanks