Insteon leak detector faulty notifications.


boji

Recommended Posts

I have two leak detector programmed with the ISY and five days out of the week an email is sent that a leak was detected. One does this at 04:00 and the other at 07:11. The system does not indicate that an email was even sent however on those five days they are there. I have since removed them from the program and still get the email. Should I just do a factory reset and restore form an earlier backup?

Link to comment

Sounds like the email is being triggered by the leak sensor heartbeat signals. Post any programs that reference the leak detectors and I'm sure we can get to the bottom of this.

 

-Xathros

Link to comment