mzn50 Posted April 30, 2014 Posted April 30, 2014 Hello All.. I recently installed multiple Foscam FI9828W outdoors...and just ordered IOlinc modules to install.. Question...On the Camera there is an I/O alarm terminal block that has 2 inputs and 2 outputs.. On the IOLINC there is • Ground – Used with Sense terminal for detecting sensor status • Sense – Used with Ground terminal for detecting sensor status • Normally Close • Normally Open – • Common – Using 22guage wire.. Has anyone wired this up successfully and configured this on the ISY? I'm thinking the 2 Output of the Camera Terminal to the N/O and Command ? Any help would be appreciated! thanks
Xathros Posted April 30, 2014 Posted April 30, 2014 Normally Open Output of the cam to Sense and Ground on the IOLinc. -Xathros