Recommended Posts

All,

 

Just got my thermostat in the yesterday, my current thermostat only has two wire from the garage heater.  I am not sure of the exact connections however basically open/closed connection from the existing thermostat (the heater came with an old mechanical one).  In any case I see that I require 24 VAC to power the 2441TH, I assume I can get a power supply from an electrical place to provide power, however were do the other two wires go on the 2441TH ?.

 

Thanks

Link to comment

Any 24VAC transformer/power supply will work. Connect one terminal of the power supply to 24COM. Connect the other side of the power supply and one of the two existing thermostat wires to 24R. Connect the other thermostat wire to W1.

Link to comment

All,

 

Just got my thermostat in the yesterday, my current thermostat only has two wire from the garage heater.  I am not sure of the exact connections however basically open/closed connection from the existing thermostat (the heater came with an old mechanical one).  In any case I see that I require 24 VAC to power the 2441TH, I assume I can get a power supply from an electrical place to provide power, however were do the other two wires go on the 2441TH ?.

 

Thanks

What is the voltage across the two wires? If it isn't 24vac you may have taken out a line voltage thermostat and you may get some fire.

Link to comment

If you put 24 volts on a system that is a millivolt system you'll most likely burn out the coil in the gas valve. (a millivolt system uses a thermocouple which is heated by the pilot light and produces a low voltage that opens the gas valve). If the heater has only two wires running to the thermostat then it's most likely a millivolt system.

Link to comment

So I did a little investigation in the garage and found the following...

 

The heater has the following connection points

R

G

W1

W2

 

My current thermostat (2 wire) is connected to R and W1, I then measured the voltage across R and G and got approx 27 VAC, based on this do you have any further wiring suggestions ?

Link to comment

Usually and typically the wires wlll be as follows:

R = Red      (I think 'red Hot') =24vac

G = Green  (I think 'Grill') =fan only control

W1= White (I think 'Warm 1') = first stage of heating

W2= Brown? (I think 'Warm 2') =second stage of heating

 

 

Some thermostats will run off just the two wires R-W1 in a parasitic mode with a battery to carry them over when the contacts are closed and the voltage is (almost) shorted. I am not sure how Insteon controllable units do it

 

These should be compatible with almost any thermostat. I would be looking inside the heater to convert that W2 to a 24vac ground/common to run to your 'stat so you have both 24vac and common. Many times the common is connected to the frame.

Link to comment

Usually and typically the wires wlll be as follows:

R = Red      (I think 'red Hot') =24vac

G = Green  (I think 'Grill') =fan only control

W1= White (I think 'Warm 1') = first stage of heating

W2= Brown? (I think 'Warm 2') =second stage of heating

 

 

Some thermostats will run off just the two wires R-W1 in a parasitic mode with a battery to carry them over when the contacts are closed and the voltage is (almost) shorted. I am not sure how Insteon controllable units do it

 

These should be compatible with almost any thermostat. I would be looking inside the heater to convert that W2 to a 24vac ground/common to run to your 'stat so you have both 24vac and common. Many times the common is connected to the frame.

 

I assume I can use any ground point inside the heater (earth ground and/or the ground for the 120 VAC power that is used for the fan) ?

Link to comment

I assume I can use any ground point inside the heater (earth ground and/or the ground for the 120 VAC power that is used for the fan) ?

You really should find the ground point and connect as close as possible to the transformer for the best reliability but you need to prove the 24vac return is grounded first.  Meter from R to case for the same voltage but you should still see the connection for best proof.

Link to comment

The diagram shows a "C" terminal. That will be your "Common" to the "R". The connections are all there. You just need to run a 5-conductor cable to the thermostat and duplicate the terminal numbers. R-R, W-W1, W2-W2, G-G, C-C.

Link to comment
  • 3 weeks later...

All,

 

Finally got around to doing this, found the following on the control board

 

C -

R - Had external connection

G - Had external connection

W1 - Had external connection

W2 -

 

The C and W2 were not wired, so I added a pin to the plug to allow for a C wire and everything worked out.  The unit does not have secondary heat (W2) so I am only using 4 wires and everything is working fine, thanks all for the help.

Link to comment

If larryyllix's suggestion doesn't work then you may have a defective unit.  Does the humidity update?

Techman, I will check but I doubt it.  Correct me if I am wrong but when I look in the event viewer I should see the updates/comms from the thermostat when it updates ?.  I will try larryllix's suggestion tonight and report back.

 

Thanks

Link to comment

On the 2444ZTH unit (I have two but no wired units) the humidity reading updates on a clock basis. On batteries it updates every 5 minutes and on PS it updates every 1 minute. Silly to pick a secondary humidity value to do that but it acts like a heartbeat to indicate life.

 

The temperature only updates by exception (on changes outside of the set bandwidth allowance from the last value sent). Temprature is NOT queriable unless the 244ZTH is in linking mode.

 

My older firmware unit can be set from the ISY but the newer firmware unit cannot be set from ISY. Yes Insteon has been having problems or they wouldn't keep getting more 10 year olds to change  their firmware.

 

Again my experience only applies to the wireless 2441ZTH units.

YMMV

Link to comment

All,

 

Here are the steps and results

 

1. Deleted device in ISY

2. Reset Thermostat

3. Re-linked thermostat

4. Synced clock on thermostat with ISY

5. Queried Thermostat to have values show up on ISY

6. Started Log/event viewer (started approx 9:14 pm)

 

The display/status on the ISY did change from the start of the log to end

 

I only had two communications on the event viewer

 

9:48 pm, DOF 0, ST 0 (This may have been me turning down the thermostat locally)

3:00 am, CLISPH 110, CLIHUM 38, ST 122

 

Note: I have a clock sync program set to run at midnight and this did not show up, not sure if it would to begin with though.

Link to comment

The only comm I see from the stat is at 3am - likely due to the 3am query running.  At that time, the temp was 61F, the stat was set to heat and 55F and the humidity was 38%.

 

-Xathros

Link to comment

The only comm I see from the stat is at 3am - likely due to the 3am query running.  At that time, the temp was 61F, the stat was set to heat and 55F and the humidity was 38%.

 

-Xathros

I did not run a query (program or manually) so I assume this is a legit communication. I got back from work and looked at the event viewer and it did communicate twice since 7:00 am

 

12:47:06 am  CLIMD 0

12:47:44 am, CLIMD 1

 

On a side note, do you know where I can get the meaning of these items (example CLIMD) ?, so from this I can assume it is not updating, is there are any detrimental effects from making a program to query, say every 10-15 min ?