simonsez Posted May 16, 2015 Share Posted May 16, 2015 Hi, I currently have a UPS which has a relay output that I've been using with a 2350 connect to the S and GND inputs so it can trigger some Insteon things. I'd like to use this somewhere else, so I got a ezio2x4. For the life of me I can't figure out how to connect the two. Can anyone tell me what connections I should use on the ezio2x4 to mimic what I was doing with the 2350? Simon Link to comment
Brian H Posted May 16, 2015 Share Posted May 16, 2015 You are using a 2450 I/OLinc? The EZIO2x4 has opto isolated and digital inputs. Connect I1+ or I2+ {Depending on which one you want to use} to the 5 volt connection on the EZIO2x4. Your relay output from the UPS to I1- or I2- and the GND terminal on the EZIO2x4. Link to comment
simonsez Posted May 16, 2015 Author Share Posted May 16, 2015 You are using a 2450 I/OLinc? The EZIO2x4 has opto isolated and digital inputs. Connect I1+ or I2+ {Depending on which one you want to use} to the 5 volt connection on the EZIO2x4. Your relay output from the UPS to I1- or I2- and the GND terminal on the EZIO2x4. hi brian, thats right using a 2450. thanks for the this, i am going to give it a go. simon Link to comment
simonsez Posted May 16, 2015 Author Share Posted May 16, 2015 hi brian, i just tried what you suggested and it worked like a charm. thanks! simon Link to comment