gweempose Posted February 26, 2016 Posted February 26, 2016 I have a scene that I'm using as a virtual 3-way circuit. The scene contains two dimmers. One is a 2477, and the other is an older 2476. The 2477 is directly connected to the load. Both dimmers are designated as controllers for the scene. Everything works as it should, however, the status lights on the 2476 do not change when I control the scene from the 2477. I have tried removing and then re-adding both dimmers to the scene, but it did not solve the problem. Any thoughts?
paulbates Posted February 26, 2016 Posted February 26, 2016 Hi, Did you try factory resetting the 2476, then do a restore device to it? I have older togglincs that act flaky after years of running correctly, that usually fixes it. Paul
gweempose Posted February 27, 2016 Author Posted February 27, 2016 Hi, Did you try factory resetting the 2476, then do a restore device to it? I have older togglincs that act flaky after years of running correctly, that usually fixes it. Paul That worked perfectly. Thanks, dude!