Fanlinc Wiring Help


hum099

Recommended Posts

I have a Hampton Bay ceiling  fan which has its own RF control (UC7067RC). I would like to switch this out for an Insteon fanlinc. I’m not sure how it should be wired up. (or if it even can be hooked up). It is also hooked up a standard wall switch which I just leave on all the time and use the remotes. The Hampton unit has 5 wires whereas the Fanlinc  only has 4. The Hampton has a white and black wire (neutral and load) which I hook up to the main power (like it was on the Hampton unit). The Hampton also has a black wire labeled Motor L (assume Load), a white wire labeled Motor N (assume neutral) and a Blue wire labelled Light. It looks like there is an extra neutral going to the fan motor. I’m not sure where to attach the extra neutral wire. Any help would greatly be appreciated.

Link to comment

On the Hampton Bay controller, the two white wires are internally connected.

 

You can connect the white wire from the fan motor to the Neutral white wire that is also connected to the Fanlinc white wire. (i.e all white wires connect together)

Link to comment

On the Hampton Bay controller, the two white wires are internally connected.

 

You can connect the white wire from the fan motor to the Neutral white wire that is also connected to the Fanlinc white wire. (i.e all white wires connect together)

Thank you very much.

Link to comment