Jump to content

Unit Testing Insteon Devices


matapan

Recommended Posts

Posted

Is there an official documented way to unit test Insteon components, like the:

 

PLM

SwitchLinc

ApplianceLinc

Motion Sensors

 

When a component fails for any reason, is there a way to determine from the Event Log if the component has indeed suffered a failure? Versus a communication issue?

 

Thanks!

Posted

Hello matapan,

 

The only thing we can currently test is the PLM by doing Tools->Diagnostics->PLM Status/Info. Beyond that, there's basically no way of knowing if the problem is obstruction of communications or a defective device for both exhibit the same symptoms: they do not respond to ISY.

 

With kind regards,

Michel

Is there an official documented way to unit test Insteon components, like the:

 

PLM

SwitchLinc

ApplianceLinc

Motion Sensors

 

When a component fails for any reason, is there a way to determine from the Event Log if the component has indeed suffered a failure? Versus a communication issue?

 

Thanks!

Guest
This topic is now closed to further replies.

  • Recently Browsing

    • No registered users viewing this page.
  • Who's Online (See full list)

    • There are no registered users currently online
  • Forum Statistics

    • Total Topics
      37.2k
    • Total Posts
      372.6k
×
×
  • Create New...