dsleegers Posted November 6, 2017 Posted November 6, 2017 Hi Guys, first time poster here. I have been using digital input 1 (DI1) on the EZIO8SA as part of my ISY994i system for about a year without any trouble. Now I am adding a second input. Adding DI2,3 and 4 has stumped me, however. I am using dry contacts from motion sensors connected to the digital inputs to turn on lights via Z Wave dimmers - so, the faster the better! For testing purposes, I have connected a binary thumbwheel switch to the 4 inputs and confirmed that I have voltage present at each optocoupler at the appropriate position. Input 1 works every time. Input 2 seems to work most times and Input 3 fails most times. Input 4 fails most times If I Query the network manually through the Administrative Console, the "Current State" changes to display all 4 inputs correctly. Any help would be appreciated. Thanks, David
Michel Kohanim Posted November 6, 2017 Posted November 6, 2017 Hi David, Just to be clear, are you using a wire to short inputs 2-4? What do you get in the Event Viewer, Level 3? With kind regards, Michel
dsleegers Posted November 7, 2017 Author Posted November 7, 2017 Hi Michel, I have attached an image of the connections that I made to the EZIO8SA via TB1. Inputs 2-4 are not shorted. I have not been exposed to the event viewer until now. I wired up test switches to inputs 1-4 and found out a few interesting things via the event viewer. 1. If I turn the switches on in the same sequence as my actual application - everything works as expected. 2. If I turn the switches on in any sequence leaving a time delay between switch changes, everything works as expected 3. If I turn multiple switches on simultaneously, one or more current states are not updated correctly. 4. The contact bounce created by my interposing relay (as measured across DI3 in my actual application and seen on one of the attachments) appears to cause problems 5. When the current state is not updated correctly, the communication information regarding a change of state of that input does not exist in the event viewer I'll let you know how this turns out Thanks David 1
dsleegers Posted November 7, 2017 Author Posted November 7, 2017 SOLVED: turns out that failure to update was being caused by contact bounce. I have eliminated the contact bounce by replacing the mechanical relay with a solid state relay (see attachment for scope results) Michel, Thanks for pointing me to the Event Viewer. David
Recommended Posts