TriLife Posted August 15, 2020 Posted August 15, 2020 (edited) Greetings; I have a newbie question: Trying to control outputs 7-16 of the ELK M1. On ISY, it only shows 65 and up. I did figure out to tick the SHOW box in ELK RP, but I haven't figured out how to "sync" the newly available outputs. And, yes, I did disconnect ELK RP from the panel. Cheers. JR Edited August 15, 2020 by TriLife
garybixler Posted August 15, 2020 Posted August 15, 2020 Have you tried going to 'Configuration-Elk-Configuration' and do a Refresh Topology? 1
TriLife Posted August 17, 2020 Author Posted August 17, 2020 On 8/15/2020 at 5:47 PM, garybixler said: Have you tried going to 'Configuration-Elk-Configuration' and do a Refresh Topology? That worked, thanks Gary!
CMcCarron Posted March 16, 2021 Posted March 16, 2021 I wonder if there are any other troubleshooting steps for this condition that anyone can suggest? I just added the Elk module to my ISY and no matter what I do I can only get outputs 065 - 208. I've tried to refresh it and it doesn't really help. The module is communicating - I can see that when I trip a zone the status changes immediately at the ISY. But no matter what I seem to do, including reboots and refreshes, I can't get the outputs below 065 to show up. Any ideas appreciated!
CMcCarron Posted March 16, 2021 Posted March 16, 2021 Disregard that please - apparently still had ElkRP connected so the refresh silently fails.