Posted

I have installed a new 2474D 2-wire dimmer switch but when I try to add it to the ISY994i I receive the error message "Cannot determine Insteon Engine".  I know this device is RF only, but there are several dual mode Insteon devices nearby.  In the list of Insteon devices the 2474D is described as a "Companion Dimmer'; not sure what that means.  Any hints to decrypt the error message and get this linked would be appreciated.

2474D_Error.JPG

Posted
17 minutes ago, Breezyken said:

I have installed a new 2474D 2-wire dimmer switch but when I try to add it to the ISY994i I receive the error message "Cannot determine Insteon Engine".  I know this device is RF only, but there are several dual mode Insteon devices nearby.  In the list of Insteon devices the 2474D is described as a "Companion Dimmer'; not sure what that means.  Any hints to decrypt the error message and get this linked would be appreciated.

2474D_Error.JPG

What type of load is the switch connected to? It's not compatible with LED bulbs

Posted (edited)

The 2474D steals power through the Load and designed for incandescent type loads.

That maybe part of why it is not being detected correctly. If you are not using a compatible Load.

There are two 2474D modules in my drop down list in the add a new device screen. Depending on what the module reported it was. Category 01 Subcategory 18 was the Companion Dimmer description and the 01 24 was the the later 2474DWH.

Edited by Brian H
Add information
Posted

I am using a compatible load (2 60 watt incandescent bulbs).  I have tried both 2474D modules as well as the auto detect function.   The error  "Cannot determine Insteon Engine" says to me the device has been detected but the software is not correct (and I'm probably wrong.  It would be nice if the device type was ordered by part number, but Category and subcat must mean something to someone.  Any more thoughts and is there a definition/description of Cat & Subcat?  Thanks

Posted (edited)
50 minutes ago, Breezyken said:

I am using a compatible load (2 60 watt incandescent bulbs).  I have tried both 2474D modules as well as the auto detect function.   The error  "Cannot determine Insteon Engine" says to me the device has been detected but the software is not correct (and I'm probably wrong.  It would be nice if the device type was ordered by part number, but Category and subcat must mean something to someone.  Any more thoughts and is there a definition/description of Cat & Subcat?  Thanks

 "Cannot determine Insteon Engine" usually means one of two things.  The PLM is unable to communicate with the device due to noise on the power line or a poor communication link between the device and the PLM.

The other possibility is that if you tried to link using "new Insteon Device" from the admin console you may have typed in an incorrect 6 digit address.

Take a look at this link:

 

Edited by Techman
  • Like 1
Posted (edited)

The Category and Subcategory are assigned to the modules by Smartlabs and reported when you add a module. They are in the module. They use to be listed on the modules sales page but I am not too sure they do that anymore.

Like Category 0X03 is Network Bridges. Which the PLM is part of. The Subcategory is different for the USB and Serial port models and sometimes even revisions. Like a different firmware in it.

https://github.com/pyinsteon/pyinsteon/blob/2533494a8b13b30b2d0938c9a18afe782b740410/docs/dev_guides/INSTEON_DevCats_and_Product_Keys_20081008.pdf

Edited by Brian H
Posted

You may try opening the Event Viewer in Level 3.

Try to add it and save the Event Viewers contents. So you can look at the messages back and forth from the problem module and the ISY994i.

Posted

Attached is the diagnostic results of trying to add the 2474d dimmer.  It looks like there is no communication to the device.  I am using a valid load (2 60 watt incandescent bulbs).  

Thanks for the links to the Insteon command list and device tables.  The Youtube video is helpful and I will check all the details and try the method in the video to establish communication.

2474D_Error.JPG

Posted (edited)

It does look like the module is not sending back any responses. When you try and add it. As there are no messages received back from the module. Just the messages being sent.

The 2474D is Insteon RF communications. No power line communications. Make sure you have a Dual Band module close enough to pass the RF commands to and from the ISY994i. Some have used a spare Dual Band module for the needed communications. An Access Point or Range Extender would also do.

Double check the modules six digit Insteon ID. We have seen B,8,0 and D sometimes misread. As a incorrect ID would also not respond.

Edited by Brian H
Posted

Attached is the diagnostic results of trying to add the 2474d dimmer.  It looks like there is no communication to the device.  I am using a valid load (2 60 watt incandescent bulbs).  

Thanks for the links to the Insteon command list and device tables.  The Youtube video is helpful and I will check all the details and try the method in the video to establish communication.

Posted

Thanks to everyone that jumped in to solve this mystery.  The technique in the YouTube video to start linking revealed that what my old eyes thought was a 40 was actually a 4D.  Everything went smoothly once that was corrected.  

Fri 09/10/2021 12:50:09 PM : Start Insteon Device Linking Mode
Fri 09/10/2021 12:50:09 PM : [LNK-BGN     ] 02 64 01 00 06 
Fri 09/10/2021 12:51:03 PM : [LNK-STAT    ] 02 53 M(01) gid=00 4D.4E.13 0124 42 
Fri 09/10/2021 12:51:03 PM : [4D.4E.13 00] Linked device type=01.24 fw=42
Fri 09/10/2021 12:51:03 PM : [4D 4E 13 0  ] Added to list of devices to link to ISY
Fri 09/10/2021 12:51:03 PM : [LNK-BGN     ] 02 64 01 00 06 

Thank You