mhunterdts Posted Monday at 10:59 PM Posted Monday at 10:59 PM Rigging up the Christmas lights and this year the tree is around 700W all incandescent. I have a 600W Switchlink in a metal box connected to a cord plugged into the box (so the dimmer is in free space not in a wall.) I see the triac is rated for 10A. Anyone know of a hard limitation to 600W. If I can keep it cool enough, 700W should work?? That's "only" 6 amps. Thoughts? Quote
Guy Lavoie Posted Tuesday at 01:46 AM Posted Tuesday at 01:46 AM 600W would be more of a heat limitation than just amperage through the triac. That's close, but would probably be ok if well ventilated. Just a personal hypothesis... Will you be dimming it? Otherwise a relay switch would be better. Maybe add a box fan to the enclosure? 2 Quote
Brian H Posted Tuesday at 11:26 AM Posted Tuesday at 11:26 AM Depending on if the metal frame of the switch is mounted on a surface that will help remove the generated heat. Incandescent loads also may have a current surge when starting with a cold filament. To consider. Relay type as pointed out would be better if you don't need dimming. Quote
Guy Lavoie Posted Tuesday at 02:41 PM Posted Tuesday at 02:41 PM Even better would be to split up the load between two switches. Depending on what you have available, a few lamplincs could be plugged into a power strip. They're only rated for 300 watts though so you'd need 3 or more. Quote