Yesterday at 02:54 AM1 day My garage door is controlled with an IO Linc. Most of the time it works, sometimes the garage door starts to move, then reverses, then reverses again. And again. And again x 20.The event viewer shows the command (0.5 second Momentary C ) being sent every second, many times.In Admin Console, right clicking on the relay, advanced PLM Communication the sensor communication to the PLM is set to 0 retries. Should I raise this number? Or is there another path?Thanks!
22 hours ago22 hr While retries aren't a bad thing for powerline only devices like iolincs, I would only add it in a mostly working steady state where a few occasional commands are not making itThe diagnostic path would be best:Open ioxTools/Diagnostics/Event ViewerAt the bottom of the event viewer, click level 3 device communicationsLeave it running and wait for it to happen again.When it does, get a copy of the iox log for that time and the contents of the event viewer and post back hereThere's members here better than me at walking those and identifying root cause(s) but this is the place to start
21 hours ago21 hr For what its worth, here are my settings for the IO Linc on my garage door. Additionally, I have the PLM set to 1 retry.
20 hours ago20 hr 12 hours ago, kurelgyer said:The event viewer shows the command (0.5 second Momentary C ) being sent every second, many times.The command is being sent by a program, right? Do you also have a sensor detecting if the door is closed? Sounds like a possible program race condition (timing).