DevonSprings Posted February 27, 2011 Share Posted February 27, 2011 I have installed two Venstar thermostats and while I can read the values it doesn't seem to respond to me setting them. It just stays the way it was, I wonder if I missed a step. 1. Hook up Thermo's (professionally done) 2. Hook up AC points 3. Put ISY in linking mode 4. Press Set button 5 seconds. 5. Rename to something logical. 6. Monitor. I note the heat / cool state has to cycle before it shows up. Setting it says it is setting the Insteon device, but I don't see it on the screen of the Venstar. Issues? ? Devon Link to comment
Michel Kohanim Posted February 27, 2011 Share Posted February 27, 2011 Hi Devon, One very important step is that the thermostats should be in OFF mode before you link them to ISY. Do you have this problem on both of your thermostats? With kind regards, Michel Link to comment
DevonSprings Posted February 27, 2011 Author Share Posted February 27, 2011 Michel, I do have a problem with both Thermostats. What do I do now. 1. Drop them from the ISY. 2. Turn off ??? 3. Relink. Devon. Link to comment
Sub-Routine Posted February 27, 2011 Share Posted February 27, 2011 Michel, I do have a problem with both Thermostats. What do I do now. 1. Drop them from the ISY. 2. Turn off ??? 3. Relink. Devon. Hi Devon, 1. Turn them Off 2. Note their addresses 3. New Insteon Device 4. Enter an address, leave on Auto Discover 5. Press Finish 6. Set the Heating/Cooling on Rand Link to comment