Jump to content

Set Ramp Rates and Levels in ISY 99


AnthemAVM

Recommended Posts

Posted

Hello,

 

I just can not figure this one out. I can set the ramp rates in ISY-99, but when you localy hit the switch it goes on 100% when it is set at 60% in the ISY, what am I doing wrong?

 

Thanks

Posted

Hi Michael,

 

This is actually a frequently asked question :) . After setting the local level/ramp (for any device other than a KeypadLinc), you must reboot the device for the new settings to take effect. You can do this by pulling out the Set button (known as air-gapping) for a few seconds and then pushing gently back in, unplugging the module and replugging, or turning off the breaker for a few seconds.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


×
×
  • Create New...