Insteon thermostat programs
barrygordon
Operating firmware 4.0.5 ISY 994i
I have two Insteon thermostats (2441TH). I have one program that runs at 1AM setting the cooling setpoints to 80 degrees. It runs fine every night with no issue. Both thermostats go to a cooling setpoint of 80 degrees F. The then section is:
set 'HVAC Systems / 24.05.B5.1 - Master System' 80 (Cool Setpoint)
set 'HVAC Systems / 20.44.74.1 - Guest System' 80 (Cool Setpoint)
The second program runs at 6AM and has a then section as follows:
set 'HVAC Systems / 24.05.B5.1 - Master System' 77 (Cool Setpoint)
set 'HVAC Systems / 20.44.74.1 - Guest System' 77 (Cool Setpoint)
The problem is with the second program that runs at 6AM.
Which ever thermostat is the last in the 'Then' section does not get its setpoint changed, but remains at the setpoint established at 1AM. If I switch the order it is always the last (second) thermostat that does not get the correct result.
Here is the pertinent section from the log file:
HVAC Systems / 20.44.74.1 - Guest System Heat/Cool State Off Sat 2013/11/02 10:32:04 PM
HVAC Systems / 20.44.74.1 - Guest System Status 76.5? Sat 2013/11/02 10:32:06 PM
HVAC Systems / 20.44.74.1 - Guest System Cool Setpoint 80? Sun 2013/11/03 01:00:00 AM
HVAC Systems / 20.44.74.1 - Guest System Cool Setpoint 80? Sun 2013/11/03 01:00:01 AM
HVAC Systems / 24.05.B5.1 - Master System Cool Setpoint 80? Sun 2013/11/03 01:00:01 AM
HVAC Systems / 24.05.B5.1 - Master System Cool Setpoint 80? Sun 2013/11/03 01:00:03 AM
HVAC Systems / 20.44.74.1 - Guest System Cool Setpoint 80? Sun 2013/11/03 01:00:08 AM
HVAC Systems / 24.05.B5.1 - Master System Cool Setpoint 80? Sun 2013/11/03 01:00:09 AM
HVAC Systems / 24.05.B5.1 - Master System Status 77? Sun 2013/11/03 04:40:58 AM
HVAC Systems / 20.44.74.1 - Guest System Cool Setpoint 77? Sun 2013/11/03 06:00:00 AM
HVAC Systems / 20.44.74.1 - Guest System Cool Setpoint 77? Sun 2013/11/03 06:00:01 AM
HVAC Systems / 24.05.B5.1 - Master System Cool Setpoint 77? Sun 2013/11/03 06:00:01 AM
HVAC Systems / 24.05.B5.1 - Master System Cool Setpoint 77? Sun 2013/11/03 06:00:03 AM
HVAC Systems / 20.44.74.2 - Guest Cool Ctl Status On Sun 2013/11/03 10:32:08 AM
HVAC Systems / 20.44.74.1 - Guest System Heat/Cool State Cool On Sun 2013/11/03 10:32:08 AM
I am not sure why all the entries appear. My iPads which subscribe to the ISY get the correct values sent to them for both thermostats at 1AM and at 6AM. It is just the one thermostat that does not change its setpoint value.
I would say it is the thermostat, but I can reliably move the problem between them depending on which entry is second in the 'Them' action at 6AM.
Any advice? I have just moved to 4.1.0 so I will see what happens tonight. If it does not clear up, I will try two separate programs, one for each thermostat, at ~6AM spaced 5 minutes apart (0600 AM, 0605 AM). I do not see how it could be a Tstat problem or a comms problem as I can reliably shift the problem between the Tstats.
Try adding a 4 second wait between the two set commands and see what happens.
It will help in situations where there is a lot of insteon traffic to prevent missed comms. With wireless devices sometimes having multiple message paths back to the PLM, I have seen odd behavior at times. Not sure this will fix it but I see no other reason that what you are doing would fail.
This morning both thermostats were at the correct setpoints. Thanks for the advice. I am using a 10 second delay to allow everything to settle down.
Excellent. Thanks for posting back. You should likely add a delay to the nighttime setback as well. Not sure why that worked when the other didn't but would be safer to add the delay to both in my opinion.
I did add the delay to both systems. I suspect on the change in setpoints from 80 to 77 the ambient temperature was above 77 causing the Tstat to start sending additional status info such as the fact that cooling has started. I suspect this additional traffic caused the problem. On the change from 77 to 80 there would have been no additional traffic as the current HVAC would not have changed
      377k