andrew77 Posted December 6, 2013 Share Posted December 6, 2013 Hi Guys; I have a simple scene that triggers correctly from a KPL button and from the ISY GUI It doesn't turn on correctly from the remotelinc. Specifically, The whole scene triggers from the RL except the load on the KPL. But the LED on the KPL does light. The Load does not. When triggered by the RL, the ISY GUI says the KPL load is 45% but the light is not on. I've written all the updates to the RL. I just switched PLM but I don't think thats an issue. I airgapped the KPL and I pulled a battery out of the RL and then put it back in hoping that would reset it. Drew Link to comment Share on other sites More sharing options...
LeeG Posted December 6, 2013 Share Posted December 6, 2013 Click the Red RemoteLinc button below the Scene name and check the KPL Ramp Rate. With KPL button turning On the KPL got the On command. It sounds like it is taking minutes to ramp on. This is the KPL Primary button that is turning On and not one of the Secondary buttons? Link to comment Share on other sites More sharing options...
andrew77 Posted December 6, 2013 Author Share Posted December 6, 2013 The ramp rate is what it should be. To be sure I re clicked "copy scene settings" The KPL button that triggers the scene is the E button. The A button is the load that isn't lighting .( light or Led) Link to comment Share on other sites More sharing options...
LeeG Posted December 6, 2013 Share Posted December 6, 2013 KPL button E and button A are both responders (or controllers) of the Scene? Link to comment Share on other sites More sharing options...
andrew77 Posted December 6, 2013 Author Share Posted December 6, 2013 KPL button E is a controller and a responder KPL button A is a responder. Aside from the rl there are no other controllers Drew Link to comment Share on other sites More sharing options...
LeeG Posted December 7, 2013 Share Posted December 7, 2013 The PLM is a Controller which you indicated works (works from the ISY GUI). The RemoteLinc sends several more Insteon messages compared to the PLM. I can see where the PLM and RemoteLinc would not work as the relationship between button E and button A are done with internal Exclusive Or relationship rather than link records but with the PLM working and the RemoteLinc not, that is unusual. Have to think about this. Link to comment Share on other sites More sharing options...
oberkc Posted December 7, 2013 Share Posted December 7, 2013 I am wondering if a link record in the KPL is somehow messed up. Would restoring the KPL do any good? I can't see that it would hurt. Link to comment Share on other sites More sharing options...
andrew77 Posted December 7, 2013 Author Share Posted December 7, 2013 That was the issue. Seems to work fine now. Thank you again oberkc. When you replace a PLM does it (for lack of a better word) 'scramble' these link records usually? Drew Link to comment Share on other sites More sharing options...
oberkc Posted December 7, 2013 Share Posted December 7, 2013 Not to my knowledge does it scramble link records in the insteon devices. Things happen, unfortunately. Link to comment Share on other sites More sharing options...
andrew77 Posted December 7, 2013 Author Share Posted December 7, 2013 A simple fix. Thanks again, Drew Link to comment Share on other sites More sharing options...