Mouton sensor 3 sec delay
khisanthax
That's pretty much it. I was wondering if a 3 second delay from motion sensor to lights on its natural? I watch the motion sensor and when the red light blinks I count to three. ..If I syst counting when I walk in the room it can be closer to 5 seconds. I'd this normal communication time?
How far away from the ISY is the MS? If you view the event log in level 3 you can see how many hops the signal has to do. More indicates more devices have to  retransmit the signal to get there.
My MS to lamps takes from about 1/2 second to 2 seconds (rarely) at times for an X10 MS and an Insteon responder device. Faster for Insteon to Insteon. If I link the two devices together the delay is not noticeable at all but then I cannot interfere with the light response with an ISY program condition. eg. time of day.
If you have lot of electrical interference on your system it can take some retries to get there. Does the signal not work at all sometimes?
If you post the Event Log on level 3 somebody can analyse it and probably tell you what is taking the delay so you may be able to alleviate that.
Are you using a scene or a program to control the light?
Thanks guys. I'm using insteon to insteon and it's a program written with conditions to change a scene that only has the light in it. In total I have 5 ms the furthest is maybe 35ft and closest maybe 15ft.
How can I count the hops in the log? I'll try to paste it here. If that's the issue how can I reduce the hops or make it more efficient?
Any program with conditions will introduce a delay. What are you using to time the delay?
I don't have a delay written into the program if that's what you mean ... but if you mean how am I counting how long it takes to activate ... I'm using the Mississippi method?
"How can I count the hops in the log? "
Max Hops is the maximum allowed.   Hops Left shows how many hops taken.   It always takes 1 so Hops Left=2 is best.  The event viewer should be run at LEVEL 3.
Tue 09/30/2014 04:24:29 PM : [std-Group   ] 28.40.E7-->Group=1, Max Hops=3, Hops Left=1
Edited by LeeG
The info posted above by LeeG is taken from the event viewer running at level 3 (device communications)
To get the event viewer select tools / diagnistics / Event Viewer -or- click the empty white toolbar button.
Once opened, change the dropdown at the bottom of the event viewer window to: 3 (device communications)
With the event viewer open and set to level 3, move in front of your motion sensor.  The insteon traffic will be captured by the event viewer.  Save and post the event log here for analysis.
When using a program instead of a scene, a one or two second delay is usually expected.
Thanks guys, here's what my log says:
Sat 10/11/2014 17:54:43 : [INST-TX-I1  ] 02 62 00 00 12 CF 13 00
Sat 10/11/2014 17:54:43 : [INST-ACK    ] 02 62 00.00.12 CF 13 00 06          LTOFFRR(00)
Sat 10/11/2014 18:01:44 : [        Time] 18:01:44 0(0)
Sat 10/11/2014 18:04:22 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 18:04:22 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:04:22 : [  27 91 81 1]      DON   1
Sat 10/11/2014 18:04:22 : [24 A BB 1   ] Link    2 : 0FE8 [A21228CB3FA51F01] Saving  [..........A5....]
Sat 10/11/2014 18:04:22 : [All         ] Writing 1 bytes to devices
Sat 10/11/2014 18:04:22 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:04:22 : [24 A BB 1   ] Link    2 : 0FE8 [A21228CB3FA51F01] Writing [..........A5....]
Sat 10/11/2014 18:04:22 : [INST-TX-I2CS] 02 62 24 0A BB 1F 2F 00 00 02 0F EF 08 A2 12 28 CB 3F A5 1F 01 1E
Sat 10/11/2014 18:04:22 : [INST-ACK    ] 02 62 24.0A.BB 1F 2F 00 00 02 0F EF 08 A2 12 28 CB 3F A5 1F 01 1E 06        (00)
Sat 10/11/2014 18:04:22 : [INST-TX-I1  ] 02 62 00 00 12 CF 11 00
Sat 10/11/2014 18:04:22 : [  27 91 81 1]       ST 255
Sat 10/11/2014 18:04:22 : [INST-ACK    ] 02 62 00.00.12 CF 11 00 06          LTONRR (00)
Sat 10/11/2014 18:04:22 : [Ext MH      ] Unexpected Ack imCmd=62 cmd1=LTONRR 0x11
Sat 10/11/2014 18:04:24 : [INST-SRX    ] 02 50 24.0A.BB 28.CB.3F 2B 2F 00           (00)
Sat 10/11/2014 18:04:24 : [Std-Direct Ack] 24.0A.BB-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:04:27 : [INST-TX-I2CS] 02 62 24 0A BB 1F 2F 00 00 02 0F EF 08 A2 12 28 CB 3F A5 1F 01 1E
Sat 10/11/2014 18:04:27 : [INST-ACK    ] 02 62 24.0A.BB 1F 2F 00 00 02 0F EF 08 A2 12 28 CB 3F A5 1F 01 1E 06        (00)
Sat 10/11/2014 18:04:28 : [INST-SRX    ] 02 50 24.0A.BB 28.CB.3F 2B 2F 00           (00)
Sat 10/11/2014 18:04:28 : [Std-Direct Ack] 24.0A.BB-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:05:56 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:05:56 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:05:56 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 18:05:56 : [  27 91 81 1]       ST   0
Sat 10/11/2014 18:05:57 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:05:57 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:05:57 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:05:57 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 18:05:57 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:05:57 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:08:56 : [INST-TX-I1  ] 02 62 00 00 12 CF 13 00
Sat 10/11/2014 18:08:56 : [INST-ACK    ] 02 62 00.00.12 CF 13 00 06          LTOFFRR(00)
Sat 10/11/2014 18:15:56 : [        Time] 18:15:57 0(0)
Sat 10/11/2014 18:23:16 : [        Time] 18:23:17 0(0)
Sat 10/11/2014 18:23:16 : [        Time] 18:23:18 0(0)
Sat 10/11/2014 18:33:15 : [        Time] 18:33:17 0(0)
Sat 10/11/2014 18:43:15 : [        Time] 18:43:17 0(0)
Sat 10/11/2014 18:45:00 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 18:45:00 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:45:00 : [  27 91 81 1]      DON   1
Sat 10/11/2014 18:45:00 : [  27 91 81 1]       ST 255
Sat 10/11/2014 18:45:00 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:45:00 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:45:00 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:45:00 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:45:01 : [INST-SRX    ] 02 50 24.0A.BB 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:45:01 : [Std-Group   ] 24.0A.BB-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:45:01 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:47:10 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:47:10 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:47:10 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 18:47:10 : [  27 91 81 1]       ST   0
Sat 10/11/2014 18:47:10 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:47:10 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 18:47:10 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:47:10 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:48:27 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 18:48:27 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:48:27 : [  27 91 81 1]      DON   1
Sat 10/11/2014 18:48:27 : [  27 91 81 1]       ST 255
Sat 10/11/2014 18:48:27 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:48:27 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:48:27 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:48:27 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:49:27 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:49:27 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:49:27 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 18:49:27 : [  27 91 81 1]       ST   0
Sat 10/11/2014 18:49:27 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:49:27 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 18:49:27 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:49:27 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:50:04 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 18:50:04 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:50:04 : [  27 91 81 1]      DON   1
Sat 10/11/2014 18:50:04 : [  27 91 81 1]       ST 255
Sat 10/11/2014 18:50:04 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:50:04 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:50:04 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:50:04 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:50:05 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:50:05 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:50:05 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:52:26 : [INST-TX-I1  ] 02 62 00 00 12 CF 13 00
Sat 10/11/2014 18:52:26 : [INST-ACK    ] 02 62 00.00.12 CF 13 00 06          LTOFFRR(00)
Sat 10/11/2014 18:52:35 : [INST-SRX    ] 02 50 24.0A.BB 00.00.01 CB 11 00    LTONRR (00)
Sat 10/11/2014 18:52:35 : [Std-Group   ] 24.0A.BB-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:52:35 : [   24 A BB 1]      DON   0
Sat 10/11/2014 18:52:35 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:52:36 : [INST-SRX    ] 02 50 24.0A.BB 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:52:36 : [Std-Group   ] 24.0A.BB-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:52:36 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:52:36 : [INST-TX-I1  ] 02 62 00 00 12 CF 11 00
Sat 10/11/2014 18:52:36 : [   24 A BB 1]       ST 255
Sat 10/11/2014 18:52:36 : [INST-ACK    ] 02 62 00.00.12 CF 11 00 06          LTONRR (00)
Sat 10/11/2014 18:52:36 : [   24 A BB 1]       ST 165
Sat 10/11/2014 18:57:14 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:57:14 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:57:14 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 18:57:14 : [  27 91 81 1]       ST   0
Sat 10/11/2014 18:57:15 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 18:57:15 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:57:15 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:57:15 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 18:57:15 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:57:15 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 18:59:31 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 18:59:31 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:59:31 : [  27 91 81 1]      DON   1
Sat 10/11/2014 18:59:31 : [  27 91 81 1]       ST 255
Sat 10/11/2014 18:59:31 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 18:59:32 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 18:59:32 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 18:59:32 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:00:14 : [INST-TX-I1  ] 02 62 00 00 12 CF 13 00
Sat 10/11/2014 19:00:14 : [INST-ACK    ] 02 62 00.00.12 CF 13 00 06          LTOFFRR(00)
Sat 10/11/2014 19:00:14 : [   24 A BB 1]       ST   0
Sat 10/11/2014 19:00:19 : [INST-SRX    ] 02 50 24.0A.BB 00.00.01 CB 11 00    LTONRR (00)
Sat 10/11/2014 19:00:19 : [Std-Group   ] 24.0A.BB-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:00:19 : [   24 A BB 1]      DON   0
Sat 10/11/2014 19:00:19 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 19:00:19 : [INST-SRX    ] 02 50 24.0A.BB 11.00.01 CB 06 00           (00)
Sat 10/11/2014 19:00:19 : [Std-Group   ] 24.0A.BB-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:00:19 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:00:19 : [INST-SRX    ] 02 50 24.0A.BB 11.00.01 C7 06 00           (00)
Sat 10/11/2014 19:00:19 : [Std-Group   ] 24.0A.BB-->11.00.01, Max Hops=3, Hops Left=1
Sat 10/11/2014 19:00:20 : [INST-TX-I1  ] 02 62 00 00 12 CF 11 00
Sat 10/11/2014 19:00:20 : [INST-ACK    ] 02 62 00.00.12 CF 11 00 06          LTONRR (00)
Sat 10/11/2014 19:00:20 : [   24 A BB 1]       ST 255
Sat 10/11/2014 19:00:20 : [   24 A BB 1]       ST 165
Sat 10/11/2014 19:02:45 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 19:02:45 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:02:45 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 19:02:45 : [  27 91 81 1]       ST   0
Sat 10/11/2014 19:02:45 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 19:02:45 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 19:02:45 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:02:45 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:03:04 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 19:03:04 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:03:04 : [  27 91 81 1]      DON   1
Sat 10/11/2014 19:03:04 : [  27 91 81 1]       ST 255
Sat 10/11/2014 19:03:04 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 19:03:04 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 19:03:04 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:03:04 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:03:05 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 19:03:05 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:03:05 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:04:19 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 13 01    LTOFFRR(01)
Sat 10/11/2014 19:04:19 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:04:19 : [  27 91 81 1]      DOF   1
Sat 10/11/2014 19:04:19 : [  27 91 81 1]       ST   0
Sat 10/11/2014 19:04:19 : [INST-SRX    ] 02 50 27.91.81 00.00.01 C7 13 01    LTOFFRR(01)
Sat 10/11/2014 19:04:19 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=1
Sat 10/11/2014 19:04:19 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 19:04:19 : [INST-SRX    ] 02 50 27.91.81 13.00.01 CB 06 00           (00)
Sat 10/11/2014 19:04:19 : [Std-Group   ] 27.91.81-->13.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:04:19 : [INST-INFO   ] Previous message ignored.
Sat 10/11/2014 19:04:53 : [INST-SRX    ] 02 50 27.91.81 00.00.01 CB 11 01    LTONRR (01)
Sat 10/11/2014 19:04:53 : [Std-Group   ] 27.91.81-->Group=1, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:04:53 : [  27 91 81 1]      DON   1
Sat 10/11/2014 19:04:53 : [  27 91 81 1]       ST 255
Sat 10/11/2014 19:04:53 : [INST-DUP    ] Previous message ignored.
Sat 10/11/2014 19:04:53 : [INST-SRX    ] 02 50 27.91.81 11.00.01 CB 06 00           (00)
Sat 10/11/2014 19:04:53 : [Std-Group   ] 27.91.81-->11.00.01, Max Hops=3, Hops Left=2
Sat 10/11/2014 19:04:53 : [INST-INFO   ] Previous message ignored.
My perceptions from this log is that you have pretty darn good communication.  Hops left=2 suggests, I understand, there was little need for retries and retransmissions.  Given this, it is hard to imagine how you can improve your delay by improvements in this area.
As for my experience, I would guess that time between detection and lights are aroudn a second..
Agree with other posts about good comm with Hops Left=2.
The trace indicates some Adjust Scene activity is being issued.  Device 27.91.81 turns On immediately followed by an Adjust Scene to 24 0A BB.  That Scene is then turned On, followed by a repeat of Adjust Scene to 24 0A BB because the update interrupted by the Scene On.  This started at 18:04:22.
Device 27.91.81 turned On at 18:45:00 with 24.0A.BB turning On with what looks like the result of being linked to 27.91.81.  Not sure about the activity to 24.0A.BB.
Device 27.91.81 turns On and Off without additional Scene activity.
There is additional activity from 27.91.81 turning On with a Scene Off some 10 seconds later.
It appears that information as to 27.91.81 and 24.0A.BB is needed along with what Scene activity is being done.
Suggest posting the Program(s) involved and the device addresses of the devices involved as there is more going on then a simple motion On.
      379.9k