Jump to content
View in the app

A better way to browse. Learn more.

Universal Devices Forum

A full-screen app on your home screen with push notifications, badges and more.

To install this app on iOS and iPadOS
  1. Tap the Share icon in Safari
  2. Scroll the menu and tap Add to Home Screen.
  3. Tap Add in the top-right corner.
To install this app on Android
  1. Tap the 3-dot menu (⋮) in the top-right corner of the browser.
  2. Tap Add to Home screen or Install app.
  3. Confirm by tapping Install.

2nd failed wall outlet. Anyone else having problems?

Featured Replies

Posted

I have had 2 2663-2 wall outlets fail.  I had my wall air conditioner plugged into it and it worked for a couple months then smelt a burning smell and it doesn't work anymore.  The air conditioner is 11.5amps and the outlet says 15 amp

I've had two 2663 outlets fail that were controlling a window A/C with even a lower amp rating. An ApplianceLinc works.

 

BTW, I bypassed the electronics so that only one outlet is controllable, which is all I needed in another location.

I've had two 2663 outlets fail that were controlling a window A/C with even a lower amp rating. An ApplianceLinc works.

 

BTW, I bypassed the electronics so that only one outlet is controllable, which is all I needed in another location.

 

Stu, the outletlincs are very sensitive to line noise. While It probably defeats the aesthetics purpose, a filterlinc between the AC and OL should solve the problem.

I have had 2 2663-2 wall outlets fail.  I had my wall air conditioner plugged into it and it worked for a couple months then smelt a burning smell and it doesn't work anymore.  The air conditioner is 11.5amps and the outlet says 15 amp

 

I probably wouldn't tempt fate and use that AC unit on that replacement dual outlet linc you receive. For what ever reason the specs for the unit are pretty sparse and indicates only 600 watts incandescent and 15 amp *all other* loads.

 

Normally this would not bother me for most hardware devices but Smartlabs hasn't been known to get a product right the first go round.

 

The On-Off Module does however clearly indicate the rating for various loads:

 

- General Appliances: 15 amps

- Resistive: 15 amps

- Incandescent: 1800 watts

- Motors: 1 HP

 

I realize its a wall wart and negates the whole purpose of a clean install. But, if your going to use them and they are going to blow why go through the headache?

  • Author

I should also add that both failed while turning it on using mobilinc. Not sure if that matters.

I suspect the large inrush starting current may have damaged the relays used to control the outlets.

Especially if the compressor got short cycled.

I will see if I can read the relay model number and its markings in the FCC Database.

I have had 2 2663-2 wall outlets fail.  I had my wall air conditioner plugged into it and it worked for a couple months then smelt a burning smell and it doesn't work anymore.  The air conditioner is 11.5amps and the outlet says 15 amp

Gah!  I'm suprised it lasted that long!

 

An air conditioner - that's about the worst possible load you can put on a relay; I can't think of any worse household appliance.  The startup current is simply off-the-scale with those compressor motors.  That 11.5 A rating -- that's "running".  The starting current for that sucker is probably 20+ amps, but even worse, if the A/C unit is "on" when the tiny itty-bitty little relay in the outletlinc turns "off", there's going to be a massive arc inside that little relay.

 

They make special relays for A/C units -- google "definite purpose contactor" to get an idea of what they look like (there's NO way that'll fit inside an outlet); the little relays in your outletlinc aren't in that league by any means.

 

So, nothing wrong with the outletlinc, just the wrong application for it.

Guest
This topic is now closed to further replies.

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.