CompKing Posted January 3, 2009 Posted January 3, 2009 I have a program which regularly (every 5 mins) queries the thermostat for its reported temperature. I have a program which monitors the value and if below a threshold it adjusts the set temperature. I have had this program running for approx 4 months in all the prior betas. A symptom I have is occasionally the program is executed when the temperature reported is erroneously reported as "zero", which may be a default on bad comm's. As a "wireless device", perfect communication is likely not possible. So far, I only have a capture of my log with the Temperature entries. I have turned on event viewer to see if I can capture level 2 comms when this happens. The funny part is this only happened weekly previously. Now, it seems to happen multiple times in a single day. Here is a log of the applicable portion. THERMOSTAT Status Query░ Sat 01/03/2009 11:51:51 AM Program Log THERMOSTAT Status Query░ Sat 01/03/2009 11:51:51 AM Program Log THERMOSTAT Humidity 0.24 Sat 01/03/2009 11:52:04 AM System Log THERMOSTAT Fan State On Sat 01/03/2009 11:55:59 AM Program Log THERMOSTAT Status 26░ Sat 01/03/2009 11:56:10 AM System Log THERMOSTAT Humidity 0.23 Sat 01/03/2009 11:56:22 AM System Log THERMOSTAT Fan State Auto Sat 01/03/2009 11:56:25 AM Program Log THERMOSTAT Humidity 0.24 Sat 01/03/2009 11:57:01 AM System Log THERMOSTAT Status Query░ Sat 01/03/2009 11:57:09 AM Program Log THERMOSTAT Status Query░ Sat 01/03/2009 11:57:09 AM Program Log THERMOSTAT Status Query░ Sat 01/03/2009 12:03:31 PM Program Log THERMOSTAT Status Query░ Sat 01/03/2009 12:03:31 PM Program Log THERMOSTAT Status 27░ Sat 01/03/2009 12:03:33 PM System Log THERMOSTAT Fan State On Sat 01/03/2009 12:04:10 PM Program Log THERMOSTAT Status 0░ Sat 01/03/2009 12:04:44 PM System Log THERMOSTAT Heat Setpoint 18░ Sat 01/03/2009 12:05:16 PM Program Log THERMOSTAT Status 27░ Sat 01/03/2009 12:05:20 PM System Log THERMOSTAT Setpoint 18░ Sat 01/03/2009 12:05:53 PM System Log THERMOSTAT Thermostat Mode Heat Sat 01/03/2009 12:06:37 PM Program Log THERMOSTAT Humidity 0.23 Sat 01/03/2009 12:07:20 PM System Log Note the "Status 0". Also note the number of entries in each "5 minute" time period varies. Some have 2 lines with values, some have 3 lines. Some show 'Query' and no results, and some are quite comprehensive. Regardless of how good/poor my wireless traffic, I would argue that a zero value should not be assumed unless on poor data packets. Regards Geoff
CompKing Posted January 3, 2009 Author Posted January 3, 2009 I have captured the event using Event Viewer. I hope this helps. The time of "status" being reported as "0" in the event log shows as 03:06:01 PM The relevant areas of the log are: 2009/01/03 15:04:11 : [iNST-SRX ] 02 50 0A.3C.92 0C.A5.CB 41 13 01 LTOFFRR(01) 2009/01/03 15:04:12 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:04:20 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:04:21 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 32 (32) 2009/01/03 15:04:21 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:04:30 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:04:39 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:04:40 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 32 (32) 2009/01/03 15:04:41 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:04:49 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:04:50 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 23 6A 18 (18) 2009/01/03 15:04:50 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:04:59 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:04:59 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 01 (01) 2009/01/03 15:04:59 : [ Time] 15:05:29 1(0) 2009/01/03 15:05:16 : [ Time] 15:05:46 1(0) 2009/01/03 15:05:18 : [iNST-ACK ] 02 62 00.00.21 CF 11 FF 06 LTONRR (FF) 2009/01/03 15:05:19 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 07 06 (07) 2009/01/03 15:05:28 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 07 06 (07) 2009/01/03 15:05:30 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 07 (07) 2009/01/03 15:05:30 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:05:30 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 00 (00) 2009/01/03 15:05:31 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:05:39 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:05:40 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 32 (32) 2009/01/03 15:05:40 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:05:49 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:05:50 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 18 (18) 2009/01/03 15:05:50 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:05:59 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:06:08 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:06:09 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 01 (01) 2009/01/03 15:06:09 : [ A AD 16 4] ST 255 2009/01/03 15:06:09 : [ 9 91 5D 5] ST 255 2009/01/03 15:06:09 : [ B E3 76 1] ST 255 2009/01/03 15:06:09 : [ E 63 53 1] ST 0 2009/01/03 15:06:09 : [iNST-ACK ] 02 62 00.00.24 CF 11 FF 06 LTONRR (FF) 2009/01/03 15:06:10 : [iNST-ACK ] 02 62 0E.63.53 0F 6D 24 06 (24) 2009/01/03 15:06:12 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6D 24 (24) 2009/01/03 15:06:12 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:06:12 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 00 (00) 2009/01/03 15:06:12 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:06:13 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 24 (24) 2009/01/03 15:06:13 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:06:22 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:06:23 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 19 (19) 2009/01/03 15:06:24 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:06:25 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 01 (01) 2009/01/03 15:06:26 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 04 06 (04) 2009/01/03 15:06:35 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 04 06 (04) 2009/01/03 15:06:35 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 04 (04) 2009/01/03 15:06:35 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:06:44 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 00 06 (00) 2009/01/03 15:06:46 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 23 6A 32 (32) 2009/01/03 15:06:46 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:06:55 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 20 06 (20) 2009/01/03 15:06:56 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 24 (24) 2009/01/03 15:06:56 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:07:05 : [iNST-ACK ] 02 62 0E.63.53 0F 6A 60 06 (60) 2009/01/03 15:07:05 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6A 19 (19) 2009/01/03 15:07:05 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:07:14 : [iNST-ACK ] 02 62 0E.63.53 0F 6B 02 06 (02) 2009/01/03 15:07:15 : [iNST-SRX ] 02 50 0E.63.53 0C.A5.CB 27 6B 01 (01) 2009/01/03 15:07:15 : [ A AA F5 8] ST 255 2009/01/03 15:07:15 : [ A AE 44 5] ST 255 2009/01/03 15:07:15 : [ 9 91 5D 4] ST 255 2009/01/03 15:07:15 : [ E 63 53 1] CLISP 36 2009/01/03 15:07:16 : [ E 63 53 1] CLIHUM 25 2009/01/03 15:07:16 : [iNST-ACK ] 02 62 00.00.24 CF 11 FF 06 LTONRR (FF) 2009/01/03 15:07:16 : [ E 63 53 1] ST 50
Michel Kohanim Posted January 4, 2009 Posted January 4, 2009 Hello CompKing, This has been fixed in 2.6.14 ... just for reassurance, this is a LOG bug where instead of saying Query, the log is just showing 0. In short, those entries are the query REQUEST and not the response. With kind regards, Michel
CompKing Posted January 4, 2009 Author Posted January 4, 2009 Thank you for the prompt response. So it sounds to me even though there is a bug in the log, the "fix" will also impact the erroneous impact on my programs which rely on the returned value of the thermostat? Thanks
Michel Kohanim Posted January 4, 2009 Posted January 4, 2009 Hello again, The bug should not impact your programs right now. If you see 0 for the status of your thermostats, then please go to Help->About and let me know the version number. With kind regards, Michel Thank you for the prompt response. So it sounds to me even though there is a bug in the log, the "fix" will also impact the erroneous impact on my programs which rely on the returned value of the thermostat? Thanks
CompKing Posted January 9, 2009 Author Posted January 9, 2009 Hello again, The bug should not impact your programs right now. If you see 0 for the status of your thermostats, then please go to Help->About and let me know the version number. With kind regards, Michel Thank you for the prompt response. So it sounds to me even though there is a bug in the log, the "fix" will also impact the erroneous impact on my programs which rely on the returned value of the thermostat? Thanks I confirm this DOES impact my programs in 2.6.13 (as confirmed with Help -> About) My Product is ISY99/IR Pro (1050) The zero value both triggers a program, shows up in Admin Console device status, and under regular device status on the web interface. Keep in mind I am running in Celcius, not Farenheit. It is intermittent, and a subsequent query of the thermostat will typically clear up the zero value to the proper room temperature.
Michel Kohanim Posted January 11, 2009 Posted January 11, 2009 Hello CompKing, Thanks so very much for the update. I shall have it checked out again though I have not been able to reproduce it under 2.6.13. If another query resolves this, then perhaps we can also move the AccessPoint close to the thermostat to see if it helps the issue. With kind regards, Michel Hello again, The bug should not impact your programs right now. If you see 0 for the status of your thermostats, then please go to Help->About and let me know the version number. With kind regards, Michel Thank you for the prompt response. So it sounds to me even though there is a bug in the log, the "fix" will also impact the erroneous impact on my programs which rely on the returned value of the thermostat? Thanks I confirm this DOES impact my programs in 2.6.13 (as confirmed with Help -> About) My Product is ISY99/IR Pro (1050) The zero value both triggers a program, shows up in Admin Console device status, and under regular device status on the web interface. Keep in mind I am running in Celcius, not Farenheit. It is intermittent, and a subsequent query of the thermostat will typically clear up the zero value to the proper room temperature.
CompKing Posted January 13, 2009 Author Posted January 13, 2009 Hello CompKing, Thanks so very much for the update. I shall have it checked out again though I have not been able to reproduce it under 2.6.13. If another query resolves this, then perhaps we can also move the AccessPoint close to the thermostat to see if it helps the issue. With kind regards, Michel By moving the AP from 40ft to 4ft away from the thermostat module, I have not detected a zero value for the returned value since. It is unfortunate that noise would be interpreted as a zero instead of an invalid result (and thus ignored). I am assuming that noise caused the issue since it did resolve itself, but even 40 ft away shouldn't be a problem (same floor, neighboring room, mostly open space between)
Michel Kohanim Posted January 14, 2009 Posted January 14, 2009 Hello CompKing, I totally agree with you. The main issue is that we have nothing to do with the error detection/correction (the PLM is doing all that) and, as such, we can only report back what the PLM sends back to us. Would you be kind enough to do one more test? Would you move your Access Point back to where it was originally, reboot your thermostat, and retry? With kind regards, Michel Hello CompKing, Thanks so very much for the update. I shall have it checked out again though I have not been able to reproduce it under 2.6.13. If another query resolves this, then perhaps we can also move the AccessPoint close to the thermostat to see if it helps the issue. With kind regards, Michel By moving the AP from 40ft to 4ft away from the thermostat module, I have not detected a zero value for the returned value since. It is unfortunate that noise would be interpreted as a zero instead of an invalid result (and thus ignored). I am assuming that noise caused the issue since it did resolve itself, but even 40 ft away shouldn't be a problem (same floor, neighboring room, mostly open space between)
CompKing Posted January 26, 2009 Author Posted January 26, 2009 Hello CompKing, I totally agree with you. The main issue is that we have nothing to do with the error detection/correction (the PLM is doing all that) and, as such, we can only report back what the PLM sends back to us. Would you be kind enough to do one more test? Would you move your Access Point back to where it was originally, reboot your thermostat, and retry? With kind regards, Michel Hello CompKing, Thanks so very much for the update. I shall have it checked out again though I have not been able to reproduce it under 2.6.13. If another query resolves this, then perhaps we can also move the AccessPoint close to the thermostat to see if it helps the issue. With kind regards, Michel By moving the AP from 40ft to 4ft away from the thermostat module, I have not detected a zero value for the returned value since. It is unfortunate that noise would be interpreted as a zero instead of an invalid result (and thus ignored). I am assuming that noise caused the issue since it did resolve itself, but even 40 ft away shouldn't be a problem (same floor, neighboring room, mostly open space between) I haven't been ignoring your response, I have been on vacation. I do note that in the 4ft location that I still do occasionally get 0 thermostat values in my programs, though not as often (once ever 40 hours or so). I can try moving it back to the original location (when I have a sec), and see if the problem worsens. Regardless, even at 4 ft I still get the invalid/zero values. Regards
Michel Kohanim Posted January 26, 2009 Posted January 26, 2009 HI CompKing, We are going to have 2.6.14 released in a few minutes. So, perhaps, it would be best if you tried your experiments with the latest release? With kind regards, Michel Hello CompKing, I totally agree with you. The main issue is that we have nothing to do with the error detection/correction (the PLM is doing all that) and, as such, we can only report back what the PLM sends back to us. Would you be kind enough to do one more test? Would you move your Access Point back to where it was originally, reboot your thermostat, and retry? With kind regards, Michel Hello CompKing, Thanks so very much for the update. I shall have it checked out again though I have not been able to reproduce it under 2.6.13. If another query resolves this, then perhaps we can also move the AccessPoint close to the thermostat to see if it helps the issue. With kind regards, Michel By moving the AP from 40ft to 4ft away from the thermostat module, I have not detected a zero value for the returned value since. It is unfortunate that noise would be interpreted as a zero instead of an invalid result (and thus ignored). I am assuming that noise caused the issue since it did resolve itself, but even 40 ft away shouldn't be a problem (same floor, neighboring room, mostly open space between) I haven't been ignoring your response, I have been on vacation. I do note that in the 4ft location that I still do occasionally get 0 thermostat values in my programs, though not as often (once ever 40 hours or so). I can try moving it back to the original location (when I have a sec), and see if the problem worsens. Regardless, even at 4 ft I still get the invalid/zero values. Regards
CompKing Posted January 27, 2009 Author Posted January 27, 2009 HI CompKing, We are going to have 2.6.14 released in a few minutes. So, perhaps, it would be best if you tried your experiments with the latest release? With kind regards, Michel So far, so good. Been almost 24 hours, and no zero's noted. Fingers crossed
Michel Kohanim Posted January 27, 2009 Posted January 27, 2009 Hello CompKing, Thanks so very much for the update. With kind regards, Michel HI CompKing, We are going to have 2.6.14 released in a few minutes. So, perhaps, it would be best if you tried your experiments with the latest release? With kind regards, Michel So far, so good. Been almost 24 hours, and no zero's noted. Fingers crossed