ISY 994i Fails to display correct current temperature and setting


dba62

Recommended Posts

The thermostat is the 2441TH.  This is a relatively new phenomenon, but it appears that the ISY is often not in sync with the thermostat.

 

For instance, currently the Temperature is 70 and the Heat set point is 70, but the ISY thinks the current temp is 66 and the set point is 64.

 

Any ideas?

 

Thanks.

 

Link to comment

Compare link tables?  May still be tied to old PLM.

 

How do I do this?   

 

I should also add that control of the thermostat works fine (I have a program running which sets the temperature to different values at different times of the day).

Link to comment

I had the same problem (Thermostat = 69, ISY=65, recently replaced PLM, motion control sensors to change thermostat temps based on room occupancy)... For the last several days, my ISY was showing 0 degrees but programs appeared to all work properly....

 

SOLUTION . . . I “restored” the Thermostat (right mouse click in ISY) and then sent updates to the device... it has been 12 hours and they remain sychronized...

Link to comment

How do I do this?   

 

I should also add that control of the thermostat works fine (I have a program running which sets the temperature to different values at different times of the day).

I can't see my console from here, so I can't give you the exact steps, but you can see link tables by right clicking the device in the admin console.  Probably under the diagnostics menu when the right click context menu pops up.  If you have done a restore they should be identical.  Checking to see if it is orphaned from the PLM is a little more tedious - you have to find the common single link that all the other devices have, which will be the PLM link, and make sure your troublesome device also has that link.  If not, that device has to be removed and re-added.

 

As for intermittent failures to update status, note that even the hard wired Insteon thermostat model is wireless-only because it is powered by a 5-30v transformer in the furnace, not the power line.  That means you could potentially just have a communications issue.  Move a dual band device or two near it for a while to check that.

Link to comment

I am having exactly the same problem. Just replaced my PLM a month ago and both my powered thermostats are not reporting correct temps or status to the isy unless I query them.

 

I'll try restoring them.

 

Sent from my XT1575 using Tapatalk

Link to comment

I am wondering now if perhaps thermostats are secure devices that require special treatment in some way, like the morninglinc lock controller.

Nothing in my experience leads me to think that they are.

 

 

Sent from my XT1575 using Tapatalk

Link to comment

Nothing in my experience leads me to think that they are.

 

 

Sent from my XT1575 using Tapatalk

 

In which case I still recommend checking to make sure the devices are indeed pointing to the new PLM.  Removing, resetting, and

adding them back would be the quickest thing, but you can manually inspect the links as mentioned above.

Link to comment

I had the same problem (Thermostat = 69, ISY=65, recently replaced PLM, motion control sensors to change thermostat temps based on room occupancy)... For the last several days, my ISY was showing 0 degrees but programs appeared to all work properly....

 

SOLUTION . . . I “restored” the Thermostat (right mouse click in ISY) and then sent updates to the device... it has been 12 hours and they remain sychronized...

 

Sorry it took me so long to get back to the forum, but this ^^^^ solution resolved my issue.

Link to comment