kzboray Posted May 25, 2022 Posted May 25, 2022 (edited) I instilled an Elk-6052 wireless smoke / fire detector added it to my Elk M1 today. I set it up as Zone Definition = 10 Fire Alarm Type = ELO Hardware / Wireless Wireless setup is: Supervised = 3-fire supervision No Options selected Loop = 2 every 59 minutes it sounds the fire alarm. My family loves it! ROFL. Any idea what I did wrong. It feels like I missed a global somewhere, but I'm not sure where to look. Edited May 25, 2022 by kzboray
kzboray Posted May 27, 2022 Author Posted May 27, 2022 @keepersg Thanks for getting back to me! The actual config was correct. Here it is for reference. Nothing out of the ordinary, but the clue came from checking the status. Status showed the 6052 as N/A and not EOLR(=). I had to run a re-enrollment of the M1XRFTW and then reset the 6052 (removed the batteries). I confirmed the configuration with Elk support, and they suggested the reset.
keepersg Posted May 28, 2022 Posted May 28, 2022 Now that's interesting. I was looking at the instructions for the M1XRFTWM
keepersg Posted May 28, 2022 Posted May 28, 2022 (edited) And checking in my Elk-RP software 3 is fire supervision, just as you show. Very specific set up procedure. Thanks for posting the solution. Edited May 28, 2022 by keepersg