I have 4 thermostats... on one of them the fan control constantly reads "ON" whether the fan is ON or OFF. I have delinked and relinked the device which solves the issue for about a week and then it happens again. Has anyone else experienced this issue?

  • 4 months later...
Posted

Hello jcip,

 

Yes, they are. I assume you have four nodes for each.

 

The next question is whether or not you are on 2.7.15 firmware. If not, please do so. If yes, then I recommend doing a factory reset on the thermostat, remove it from ISY, and then add it back in. If that still doesn't work, then I would have to think a problem with the thermostat.

 

With kind regards,

Michel

Posted

i do have four nodes and i am on firmware 2.7.15. i will follow the procedure next time i experience the problem. at the moment, the fan and heat nodes are not reading a state at all (neither on or off)... does that sound correct? but the thermostats all seem to be functioning properly... they are all set to cool and the cool control is "on" or "off" as appropriate.

Posted

I don't quite understand. I do have the fan set to Auto but I do not get an update for whether it is on or off. Is that correct?

Posted

That is correct. In Auto the fan runs as required by the HVAC. The thermostat does not send separate fan states because the thermostat does not control the fan.

 

If On the fan would always run and the status should reflect On.

Guest
This topic is now closed to further replies.

×
×