Jump to content
View in the app

A better way to browse. Learn more.

Universal Devices Forum

A full-screen app on your home screen with push notifications, badges and more.

To install this app on iOS and iPadOS
  1. Tap the Share icon in Safari
  2. Scroll the menu and tap Add to Home Screen.
  3. Tap Add in the top-right corner.
To install this app on Android
  1. Tap the 3-dot menu (⋮) in the top-right corner of the browser.
  2. Tap Add to Home screen or Install app.
  3. Confirm by tapping Install.

Xathros

Members
  • Joined

  • Last visited

Everything posted by Xathros

  1. Lets try a "File / Restore PLM" and see if we can get your statuses working. -Xathros
  2. I have done this, just this week. And yes, it does work. I have 3 Toggleinc Relays around my kitchen and dinning room. If I fade down any of the 3, a program is invoked to turn off 2 scenes. All of the 3 switches exist one or the other of those 2 scenes. When fading down the light will just turn off while I'm still holding the paddle down. I suspect if the device was a dimmer, the light would start do dim then turn off a second later when the program executes. -Xathros
  3. I believe the blinking ERR led indicates a problem with the file system. Yet another indication of an SD card issue. If you believe the backup after the upgrade was successful, then that is the one to use. If not, then I would attempt to make another now. If you are unable to due to lockups, then you can use the older one but I think you would want to flash the new/formatted card with the version of the firmware that was in use at the time of that backup, restore that backup, then upgrade to 3.2.6 after that. Of course your TriggerLinc will not be there and your notification program for the Triggerlinc won't be there since they were added since the upgrade. I would follow the Wiki procedure as there was something specific to the card being formatted by the ISY. I suspect it wants to be FAT16 not NTFS or HFS+ etc. and there may even be more to it than that. I have read that older ISY hardware has a 512Mb card size limit. I'm not sure at what point they started supporting the larger cards or how we can tell if yours does or not. Hopefully Michel can chime in on that. Lets hope you have/can get a good backup and that a reformat is all thats needed. -Xathros EDIT: Also, if you are using the Network Resources Module and have stuff in the webserver, you need to copy that out first as it is not in the backups and will be lost on the reformat. EDIT #2: Lets start simple. Power down the ISY, then remove and re-seat the SD card first. Test.
  4. I don't really think the initial DHCP process is whats locking it up but possibly at IP lease renew. Really just trying to eliminate things to narrow down the problem. Also I see -50010 errors in your log related to smtp.gmail.com. I believe this is a DNS lookup failure. I was having some issues with my ISY not resolving both SMTP and NTP servers a month or so ago. I resolved it by statically setting 8.8.8.8 and 4.2.2.2 as my DNS for the ISY. I suspicion is that the ISY is not waiting long enough for a response from the DNS servers and my ISP's servers in conjunction with my router were not responding fast enough resulting in a timeout. (Thats all just my "feeling" as I haven't been able to prove any of it yet) In any case, setting the DNS as stated above solved the problem for me. I am concerned that the MEM led is on steady when it's locked up. This may be a clue since as far as I can tell that LED should only be lit during SD card access and not be in a steady on state ever. It's possible you have a corrupted or failing SD card. I'd like Michel's thoughts on this as well. In any event, here is the Wiki data on reformatting or replacing the SD card: http://www.universal-devices.com/mwiki/ ... an_SD_Card If you are up for it, I would try the reformat first. MAKE SURE you have a good backup of the ISY before you begin. -Xathros
  5. I really think you will be happy with MobiLinc. I love it. Lets eliminate DHCP issues. Can you assign a static address inside the ISY that is outside of your routers DHCP address range? This will simplify the startup a bit and will eliminate DHCP errors from the log. You will need to edit your port forwards (if you have any for the ISY) to match the new address. What was the state of the LEDs after it locked up this time ? How old is this ISY ? -Xathros
  6. I'm not entirely sure, however, if your login credentials haven't changes and conductor is failing to log in, there is a strong possibility that the certificate that conductor has is mismatched with that of the ISY. It wouldn't hurt to clear that on the android and let it re-accept what the ISY has. EDIT: I was just reading a bit over on the Conductor for Android forum and see that there is another person having the same problem after adding a FanLinc to their ISY. I wonder if there is some I2CS issue with conductor that shows up like an authentication error. Anyway, the recomendation there was to switch to Mobilinc for android. I love Mobilinc on my iPhone and Wes (the developer of Mobilinc) is as responsive and helpful as the UDI crew so support is not a concern. -Xathros
  7. hbsh01- I suspect your android phone has an old certificate for the ISY and needs to accept a new one after the upgrade. I don't know how to delete the existing cert on android but if you can find that and remove the old cert then allow it to accept a new one that may resolve your failure to authenticate from conductor. I too had issues with my web host's SMTP with the ISY and switched to gmail's SMTP. I've had no issues with notifications since. -Xathros
  8. It sounds like those have been eliminated then. Hopefully there will be something useful in the logs. EDIT: Another thing to consider, Is it possible you have another device on your network that is statically configured for the address that your router has issued the ISY ? Or, another device offering DHCP services on the same subnet ? To test, you could temproarily disconnect the ISY then try to ping that IP from a computer and see if you get a reply. If so, you have an IP conflict at that address. -Xathros
  9. I wonder if the combo of the new IOLinc and Conductor is whats causing the lockup. Can you either remove the IOLinc or disable Conductor for a little while to see if the lockups stop ? -Xathros EDIT: I see Michel is on the case here. I'll step back and watch unless something jumps out at me.
  10. Can you check your error log and see whats showing up there since the upgrade. -Xathros
  11. You can certainly configure things such that you could do all of the control from one place. You would still be able to control the second ISY or Smartlink independently if you wanted as well. -Xathros
  12. I'm sorry to hear that. I still wonder if there is a way to trick the transfer switch into thinking that utility power has been restored or to tap into the control circuitry at that point to tell the generator to do a normal shutdown. Please do let us know if you find a workable solution. -Xathros
  13. Excellent. Please let us know how it works out for you. I have some long term plans for doing something similar at my place. -Xathros
  14. Xathros replied to a post in a topic in ISY994
    There is another configuration that I had considered and rejected. Run the 24V over the existing 2 wire to the Venstar. Add EZIO or IOLinc at the furnace/zone valve/pump whatever for the contact closure and use the ISY to Monitor the tstat and control the zone. Only reason I rejected this is in the event of a comm failure a zone could be left on or fail to turn on. A periodic query could fix that issue as lons as comm failurs are rare in your setup. I preferred to have the tstat do the control directly. -Xathros
  15. Jeff- I don't believe there are any stack issues with this. I have something similar on my ISY and haven't had any problems. As for copy paste, right click the program name in the tree on the left, select Copy to Clipboard. HTH -Xathros
  16. Xathros replied to a post in a topic in ISY994
    PLCG- I ran into the exact same issue with my setup although mine is a single zone forced hot air system. I tried to find a way to just do a 3 wire run from the furnace to the Venstar but couldn't find a way to get the necessary connections at the furnace. I ended up buying a 24VAC transformer, pulling a run of 3 wire tstat wire to the tstat location and building a small relay circuit at the furnace to interface to the 2 wire line from the furnace. As I recall, I cost me all of about $20 for the wire and components from Radio Shack and another $20 for the transformer and jbox to mount that to. This has to be a fairly common problem and I'm surprised that nobody sells a conversion kit like this already built. If they do, I was unable to search it out. -Xathros
  17. pikach- Are both buildings on the same Ethernet network ? If so, An ISY (with the network resources module and either a dual band PLM or an access point) for the building with the thermostat. The dual band PLM or access point are required to communicate with the RF only thermostat. For the other building, you may be able to use a SmartLinc controller for the Insteon devices there and operate those over Ethernet from the network resources module via the SmartLinc. Not nearly as nice as having them all on the same Insteon network but I think this can meet your stated need. Michel, LeeG - Thought or comments on this approach ? -Xathros
  18. I'm not sure that inside the generator would be a friendly location for an IOLinc. There won't be line power there or a connection back to the rest of the insteon network unless the generator is running and the transfer switch has flipped to the generator side. This means no comms with that IOLinc under normal conditions. Also, the power at startup and shutdown of the generator is not going to be nice. I'm not sure how well the IOLinc will stand up to that. I think the house side of the transfer switch is the best place for the IOLinc to live. Thinking a bit more about the remote shutdown aspect, Cutting the power to the CDI is probably not a good idea as the generator will still likely continue trying to start thereby running down the starter battery. The low oil switch *should* prevent it from trying tho there may still be an active drain on the starter battery. Some testing beforehand should be done. I would think there is a method for taking the generator offline that you may be able to tap into and with any luck, that may be at the transfer switch. -Xathros
  19. It's safer to do locally however, I have done this remote a number of times without issue. If you feel that you have a solid connection from the remote location to the ISY then you should be alright. If you have problems making the backup due to the remote connection, that would be a good indication that you are likely to have similar issues during the upgrade. In that case I'd say wait until you can work locally. -Xathros
  20. hbsh01- Don't worry. Everything is retained through the upgrade. The first part of the update process prompts you to make a backup just in case anything goes wrong. Make sure you clear your Java cache AFTER the upgrade and BEFORE you attempt to log back into the admin console. -Xathros
  21. Nice looking installation there. Congrats! As for the remote shutdown my bet would be the low oil switch circuit for an easy relay operated remote generator shutdown. Of course, this means another pair run out to the generator. Otherwise maybe look for the V+ for the CDI and put some relay contacts in series with that line. -Xathros
  22. Thanks for the explanation Wes. This is a capability I didn't know existed in Mobilinc. I'll have to see if I can simplify any of my configuration using this. -Xathros
  23. The proper way to accomplish what you want in Mobilinc would be to make the scene for your 3way(s) a favorite(s). Make any other standalone devices favorites then everything you want will be on the favorites page in Mobilinc. You will control the 3way with a scene and the standalone devices as devices. I will have to play with the device icon thing that you mentioned. I don't believe that is the way it was intended to work. -Xathros UPDATE: I can confirm the device Icon in MobilincHD (Latest Version) acts as a scene controller for multiway configurations when accessed from a member device's device page.
  24. SetMonkey13- My RemoteLincs are in toggle mode so the LEDs alternate between red/green but since I'm under program control my lights toggle regardless of the red/green state of the buttons. In one case, I have a single RemoteLinc button cycle through (low-med-high-off) for my bedroom ceiling fan with faston/fastoff presses setting the fan off regardless of where it was in the cycle. -Xathros
  25. I have been running my ISY-99 with my MAC's for several years now with no complaints. I download ISY firmware images with Firefox rather than Safari and choose "Save" when prompted to "Open or Save" the download. -Xathros

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.