miataguy Posted June 26, 2016 Posted June 26, 2016 I have an Insteon 2441TH installed. Been working fine for the past year. The past week, it has shut down twice. This is what I see in the log. What caused it to shut itself down? Nothing programming is doing it. What do the error codes mean? Why did it set the set points at 60 and 80 at 3:37am? I have no program that does it. Main thermostat - Main Humidity 40% Sat 2016/06/25 08:44:59 PM System Log Main thermostat - Cool Ctl Status On Sat 2016/06/25 09:12:36 PM System Log Main thermostat - Main Heat/Cool State Cool On Sat 2016/06/25 09:12:36 PM System Log Main thermostat - Main Humidity 39% Sat 2016/06/25 09:34:03 PM System Log Main thermostat - Main Humidity 37% Sat 2016/06/25 09:54:02 PM System Log Main thermostat - Cool Ctl Status Off Sat 2016/06/25 09:56:21 PM System Log Main thermostat - Main Heat/Cool State Off Sat 2016/06/25 09:56:21 PM System Log Main thermostat - Main Cool Setpoint 78° Sat 2016/06/25 10:12:38 PM Program Log Main thermostat - Main Error 1 Sat 2016/06/25 10:13:01 PM System Log Main thermostat - Main Sat 2016/06/25 10:13:01 PM System -2 Main thermostat - Main Cool Setpoint 78° Sat 2016/06/25 10:13:01 PM Program -1 Main thermostat - Main Heat Setpoint 67° Sat 2016/06/25 10:13:01 PM Program Log Main thermostat - Main Heat Setpoint 67° Sat 2016/06/25 10:13:23 PM Program -1 Main thermostat - Main Cool Setpoint 78° Sat 2016/06/25 10:24:02 PM Program Log Main thermostat - Main Cool Setpoint 78° Sat 2016/06/25 10:24:24 PM Program -1 Main thermostat - Main Heat Setpoint 67° Sat 2016/06/25 10:24:24 PM Program Log Main thermostat - Main Heat Setpoint 67° Sat 2016/06/25 10:24:46 PM Program -1 Main thermostat - Main Error 0 Sun 2016/06/26 03:36:59 AM System Log Main thermostat - Main Heat Setpoint 60° Sun 2016/06/26 03:36:59 AM System Log Main thermostat - Main Cool Setpoint 80° Sun 2016/06/26 03:37:00 AM System Log Main thermostat - Main Thermostat Mode Off Sun 2016/06/26 03:37:01 AM System Log Main thermostat - Main Status 77° Sun 2016/06/26 03:37:03 AM System Log
Michel Kohanim Posted June 27, 2016 Posted June 27, 2016 Hi miataguy, What do you mean by shut down? Does it mean that the thermostat turns off completely? How do you get it to work again? The errors mean that ISY cannot communicate with the thermostat. With kind regards, Michel
miataguy Posted August 20, 2016 Author Posted August 20, 2016 Wanted to circle back on this since I finally found the problem. There was a moisture sensor in the air handler that was triggering and shutting off power to the thermostat. I replaced the moisture sensor with a float switch. Problem solved.
Michel Kohanim Posted August 21, 2016 Posted August 21, 2016 Hi miataguy, Thanks so very much for the update! With kind regards, Michel
Recommended Posts