MemoryLeak Posted July 28, 2016 Posted July 28, 2016 Good day to everybody! Recently moved to new house. Previous owner had an ISY configured. Many devices configured to work with. But he took the ISY, as it was custom configured to his desires. Now, I'm trying to figure out all the things myself. The first device I tried to configure is EzFlora sprinkler controller. Steps I did: factory reset EzFlora linked EzFlora to ISY using "add insteon device by address" Now, I see 8 zones. But, when I try to open a zone nothing happens. Not sure where to start to troubleshoot the issue. Can you advise, please? Thanks!
MemoryLeak Posted July 28, 2016 Author Posted July 28, 2016 (edited) Ran a test, results below Wed 07/27/2016 05:14:02 PM : [GRP-RX ] 02 61 11 13 00 06 Wed 07/27/2016 05:14:03 PM : [CLEAN-UP-RPT] 02 58 06 Wed 07/27/2016 05:14:03 PM : [iNST-SRX ] 02 50 1E.79.65 41.E8.F8 65 13 11 LTOFFRR(11) Wed 07/27/2016 05:14:03 PM : [std-Cleanup Ack] 1E.79.65-->ISY/PLM Group=0, Max Hops=1, Hops Left=1 <html><font color="red">----- Outdoor lawn Test Results -----</font></html> <html><font color="red">[succeeded]</font> EzFlora - 8 (1E 79 65 8 )</html> <html><font color="red">[succeeded]</font> EzFlora - 7 (1E 79 65 7)</html> <html><font color="red">[succeeded]</font> EzFlora - 2 (1E 79 65 2)</html> <html><font color="red">[succeeded]</font> EzFlora (1E 79 65 1)</html> <html><font color="red">[succeeded]</font> EzFlora - 4 (1E 79 65 4)</html> <html><font color="red">[succeeded]</font> EzFlora - 3 (1E 79 65 3)</html> <html><font color="red">[succeeded]</font> EzFlora - 6 (1E 79 65 6)</html> <html><font color="red">[succeeded]</font> EzFlora - 5 (1E 79 65 5)</html> <html><font color="red">----- Outdoor lawn Test Results -----</font></html> Wed 07/27/2016 05:14:11 PM : [iNST-TX-I1 ] 02 62 00 00 11 CF 13 00 Wed 07/27/2016 05:14:11 PM : [iNST-ACK ] 02 62 00.00.11 CF 13 00 06 LTOFFRR(00) Edited July 28, 2016 by MemoryLeak
LeeG Posted July 28, 2016 Posted July 28, 2016 Should be no problem turning On Zones, only one zone at time. What were you expecting to happen beside the zone showing On in Admin Console?
paulbates Posted July 28, 2016 Posted July 28, 2016 (edited) Hi and welcome to the forums! Let's start by understanding the irrigation system itself with these questions: Was the ezflora already installed, or did you install it new? Does the system use a master valve or pump? The previous owner should know. If its a pump or master valve based system, you need to set the option in the admin console to enable it, or you'll get the results you're seeing SInce the previous owner took the ISY, can they give you their last ISY backup? Restoring that should give a good working base to start with Paul Edited July 28, 2016 by paulbates
MemoryLeak Posted July 28, 2016 Author Posted July 28, 2016 Should be no problem turning On Zones, only one zone at time. What were you expecting to happen beside the zone showing On in Admin Console? my understanding the valve is that when a zone is on, the actual valve would open, and it will rain
MemoryLeak Posted July 28, 2016 Author Posted July 28, 2016 Hi and welcome to the forums! Let's start by understanding the irrigation system itself with these questions: Was the ezflora already installed, or did you install it new? Does the system use a master valve or pump? The previous owner should know. If its a pump or master valve based system, you need to set the option in the admin console to enable it, or you'll get the results you're seeing SInce the previous owner took the ISY, can they give you their last ISY backup? Restoring that should give a good working base to start with Paul ezflora was already installed master valve or pump - how do I check that? there are 7 zones where exactly in the Admin Console should I look? can't get the backup. can't contact the owner.
paulbates Posted July 28, 2016 Posted July 28, 2016 (edited) ezflora was already installed master valve or pump - how do I check that? there are 7 zones where exactly in the Admin Console should I look? can't get the backup. can't contact the owner master valve or pump - how do I check that? there are 7 zones. Inspect the Ezflora unit, is there a wire connected to zone 8? If yes, then very likely that's it. Mastervalves were more of a trend in the late 80s and 90s, not so much for a newer systems. When it was factory reset, the existing mastervalve setting the prior owner had would be the factory default of "off". where exactly in the Admin Console should I look? Click on a valve in the admin console. In the center panel at the bottom, it will say options. One of the options is "Zone 8: Pump". That needs to be set if you have a master valve or pump as indicated by the wiring. Edited July 28, 2016 by paulbates
MemoryLeak Posted August 2, 2016 Author Posted August 2, 2016 There is NO wire connected to zone 8. There is "Zone 8: Pump" option.
paulbates Posted August 2, 2016 Posted August 2, 2016 Hmm, ok. So if there is no 8th wire, there is no pump or master-valve. So it looks like the ISY thinks its turning zones on and off without errors, so that suggests the Insteon to Ezflora messaging is working and something may be wrong with the sprinkler system. 2 other things to check The sprinkler system needs 25vac to make the valves open. That's usually a ~2" x 2" plugin transformer near the ezflora and wiring termination. The owner may have taken it? The ezflora has an optional plug in termination at the bottom near the wiring for a rain sensor. The rain sensor will stop the unit from watering if it thinks its on. Is there a plug and extra wires near where the sprinkler wires plug in? Paul
MemoryLeak Posted August 3, 2016 Author Posted August 3, 2016 There is a transformer and light is green on it. There is no rain sensor plugged in. Please see the photo.
larryllix Posted August 3, 2016 Posted August 3, 2016 AC power is disconnected (white is removed from terminal) Your 7th zone looks like it may be disconnected also. Or wire is just stripped too long. Is the terminal screw and the wire tight?
paulbates Posted August 3, 2016 Posted August 3, 2016 (edited) Larry's right, the zones aren't opening because they have no power due to the disconnected transformer lead. It needs to be attached to the second "AC xmr" terminal. Pull the transformer out of the wall before attempting to disconnect/reconnect any leads to the ezflora. There's probably not enough voltage to hurt you, but unintended shorts could damage the ezflora's outputs. I would suggest installing a small terminal block in the housing.. attach the transformer to two of its terminals, and a similar gauge wire to the sprinkler wire from each of the 2 terminals of the block to the ezflora. The transformer wire looks to big for the the small terminals of the ezflora. That's what I did. Make sure there is no bare wire showing from the bottom when any lead is screwed in place. To Larry's other point, Zone 7 and the White Comm lead are a little long. With the transformer unplugged, unscrew them and attempt to push them in further. If that does not work, take them out, one at at time, trim the end until it fits with no bare showing. Paul Edited August 3, 2016 by paulbates
mwester Posted August 3, 2016 Posted August 3, 2016 I agree with the posters above -- and I'll add that proper installation of the wires is NOT just due to "anal-retentive" or OCD people on this forum! Sloppy installations result in failures - which are bad - or outright short circuits - which are worse. And even though this is only 24VAC, that's enough power to result in an overheating situation. Starting from the right side, going left -- the installation looks very good, gradually decaying to horrifyingly awful at the left end. It needs to be cleaned up and fixed. As noted earlier, make sure NO bare copper is showing. Also, use the proper wire size -- the stranded wire on the far left is NOT the right size, and you can't just put that into those terminal strips -- you'll need to use wire nuts and a short length of solid copper wire to make the connection to that stranded cable. Sloppy == failure, if not immediately then at some point in time where Murphy's law dictates that said failure will result in maximum inconvenience or outright monetary damages.
paulbates Posted August 3, 2016 Posted August 3, 2016 (edited) To keep riding the OCD express , one issue might be the transformers and sprinkler system wires hanging down from the bottom pulled the leads out of the ezflora. I mount each bundled wire package with a strap and put a little bit of a bend in each individual wire so there is a slight pressure into the ezflora, so jostling of the box doesn't cause what appears to have happened here Paul Edited August 3, 2016 by paulbates
Brian H Posted August 3, 2016 Posted August 3, 2016 The transformer wires also look like they are close to the largest wire gauge the terminal strip can handle. So extra patience is needed to get it into the terminal and get a good solid grip that will not pull out again and no stray strands touching the next terminal over.. I second the tie wraps or wire straps to take the strain off of the wires and terminal clamps.
MemoryLeak Posted August 3, 2016 Author Posted August 3, 2016 ok. So the transformer is dead. Currently it's a VITEK VT24VAC20 Do I have to go with VITEK only? What are the alternatives? (couldn't find a store here, in Ontario, that sells VITEK products) Thanks!
Brian H Posted August 3, 2016 Posted August 3, 2016 (edited) You have determined it was the transformer is bad and not just disconnected on the EzFlora? No it does not have to be that brand. Smartenit sells a 24VAC 20VA transformer for the EZFlora. http://smartenit.com/product/24vac-20va-transformer/ You don't have to get it from them either. You need a transformer that is 24 VAC 20VA output. Edited August 3, 2016 by Brian H
paulbates Posted August 3, 2016 Posted August 3, 2016 The 24vac 20va is a North American irrigation system standard as Brian pointed out. If those 2 wires contacted when the one pulled out, it could have blown the transformer. It seems odd that its light was still on if that was the case.
MemoryLeak Posted August 24, 2016 Author Posted August 24, 2016 Thanks everybody. The root issue was the dead transformer. After I've replaced it everything works fine.
paulbates Posted August 24, 2016 Posted August 24, 2016 Great, glad you are working, hopefully your yard is good. Paul
Brian H Posted August 24, 2016 Posted August 24, 2016 That is good news. I am glad you are now back in business.