Hi,
Sorry to have so many posts recently. I really appreciate this piece of software and the work you've put into it.
I am using Kiddie hardwired smoke & CO detectors in my home and have them connected to my Honeywell Alarm panel (zone 1 fire, zone 8 CO) with the Kiddie CO120X and SM120X. I actually got the idea from you in an old post
When either the smoke or CO detector goes off, it looks like the XX120Xs only open for a moment and then go back to their normal state. The trigger is detected by the alarm panel, but I think the switch is so fast that the actual zone status nodelink sees does not change (and thus is not reflected in the ISY). The "Partition 1" node does see the alarm and "Fire Alarm" goes from 0 to 1. The only difficulty I have here is I can't detect the difference between a "Fire" and a "CO" alarm. Is there any way to use the data the EVL is sending to NodeLink to get more precise feedback here? They Honeywell panels do provide different feedback based on Fire or CO alarms (if zone types are correctly set). Is there any way you could add a "CO Alarm" variable to the "Partition X" node? Here are some relevant logs:
2019-01-10 11:42:07 - Hon: Virtual Keypad Update (01,0008,10,00,FAULT 10 FAMILY ROOM MOTION     $) [hwalrm1]
2019-01-10 11:42:07 - Hon/ISY: Zone 10 (Family Room PIR (Zone 10)) Open [hwalrm1]
2019-01-10 11:42:08 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-10 11:42:08 - Hon TCP: %00,01,0008,10,00,FAULT 10 FAMILY ROOM MOTION     $[C][L] [hwalrm1]
2019-01-10 11:42:11 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-10 11:42:11 - Hon TCP: %02,0100000000000000$[C][L]%00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-10 11:42:11 - Hon: Partition State Change [hwalrm1]
2019-01-10 11:42:11 - Hon: Virtual Keypad Update (01,3208,01,04,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-10 11:42:11 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0008,02,04,FAULT 02 MAIN   FLOOR MOTION    $[C][L] [hwalrm1]
2019-01-10 11:42:11 - Hon: Virtual Keypad Update (01,0008,02,04,FAULT 02 MAIN   FLOOR MOTION    $) [hwalrm1]
2019-01-10 11:42:14 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-10 11:42:14 - Hon TCP: %02,0100000000000000$[C][L]%00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-10 11:42:14 - Hon: Partition State Change [hwalrm1]
2019-01-10 11:42:14 - Hon: Virtual Keypad Update (01,3208,01,04,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-10 11:42:15 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-10 11:42:15 - Hon TCP: %03,1373010010$[C][L] [hwalrm1]
2019-01-10 11:42:17 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-10 11:42:17 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-10 11:42:18 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-10 11:42:18 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-10 11:42:22 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-10 11:42:22 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-10 11:42:23 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-10 11:42:23 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-10 11:42:23 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
Yep, no problem adding a separate variable based on your log.  Will add when I'm back from vacation.
So not as straight forward as I hoped.
The fire alarm gets reset because it can read a %00 update which includes two bits for fire.  The CO does not have bits in the %00 so I'd have to reset it based on the panel not being in "trouble" anymore.
Can you give me another log with a few more lines?  I want to see the CO alarm (not fire), and see the %00 after it is cleared.
Thanks for looking into it. I tripped the CO Zone then cleared panel. Here are logs:
2019-01-22 17:22:05 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:22:05 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:05 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-22 17:22:06 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:22:06 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0008,04,00,FAULT 04        BASEMENT MOTION $[C][L] [hwalrm1]
2019-01-22 17:22:06 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:06 - Hon: Virtual Keypad Update (01,0008,04,00,FAULT 04        BASEMENT MOTION $) [hwalrm1]
2019-01-22 17:22:06 - Hon/ISY: Zone 4 (Basement motion (Zone 04)) Open [hwalrm1]
2019-01-22 17:22:08 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:22:08 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:22:08 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:08 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-22 17:22:11 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:11 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:22:21 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:21 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:22:27 - Hon TCP: Polling Alarm [hwalrm1]
2019-01-22 17:22:27 - Hon TCP: Data Received - 9 Bytes [hwalrm1]
2019-01-22 17:22:27 - Hon TCP: ^00,00$[C][L] [hwalrm1]
2019-01-22 17:22:31 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:31 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:22:35 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:35 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:35 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:22:40 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:40 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:40 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-22 17:22:40 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-22 17:22:42 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:42 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:45 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:45 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:46 - Hon TCP: Data Received - 115 Bytes [hwalrm1]
2019-01-22 17:22:46 - Hon TCP: %02,0300000000000000$[C][L]%01,0A000000000000000000000000000000$[C][L]%00,01,0008,02,04,FAULT 02 MAIN   FLOOR MOTION    $[C][L] [hwalrm1]
2019-01-22 17:22:46 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:46 - Hon: 01 - Zone State Change [hwalrm1]
2019-01-22 17:22:46 - Hon: Virtual Keypad Update (01,0008,02,04,FAULT 02 MAIN   FLOOR MOTION    $) [hwalrm1]
2019-01-22 17:22:46 - Hon/ISY: Zone 2 (Main floor PIR (Zone 02)) Open [hwalrm1]
2019-01-22 17:22:50 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:50 - Hon TCP: %00,01,0208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:50 - Hon: Virtual Keypad Update (01,0208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:22:52 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:22:52 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:52 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:52 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:22:56 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:22:56 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:22:57 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:22:57 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0008,04,04,FAULT 04        BASEMENT MOTION $[C][L] [hwalrm1]
2019-01-22 17:22:57 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:22:57 - Hon: Virtual Keypad Update (01,0008,04,04,FAULT 04        BASEMENT MOTION $) [hwalrm1]
2019-01-22 17:22:57 - Hon/ISY: Zone 4 (Basement motion (Zone 04)) Open [hwalrm1]
2019-01-22 17:23:00 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:00 - Hon TCP: %00,01,0208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:00 - Hon: Virtual Keypad Update (01,0208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:23:01 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:23:01 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:01 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:23:01 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:23:03 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:03 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:03 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:23:05 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:05 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:06 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:06 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:06 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:23:07 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:23:07 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-22 17:23:07 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:23:07 - Hon: Virtual Keypad Update (01,0208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-22 17:23:09 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:09 - Hon TCP: %00,01,0C08,08,01,****DISARMED****Hit * for faults$[C][L] [hwalrm1]
2019-01-22 17:23:09 - Hon: Virtual Keypad Update (01,0C08,08,01,****DISARMED****Hit * for faults$) [hwalrm1]
2019-01-22 17:23:10 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:10 - Hon TCP: %00,01,0008,04,00,FAULT 04        BASEMENT MOTION $[C][L] [hwalrm1]
2019-01-22 17:23:10 - Hon: Virtual Keypad Update (01,0008,04,00,FAULT 04        BASEMENT MOTION $) [hwalrm1]
2019-01-22 17:23:10 - Hon/ISY: Zone 4 (Basement motion (Zone 04)) Open [hwalrm1]
2019-01-22 17:23:12 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:23:12 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-22 17:23:12 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:23:12 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-22 17:23:14 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-22 17:23:14 - Hon TCP: %03,3380010080$[C][L] [hwalrm1]
2019-01-22 17:23:15 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-22 17:23:15 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0008,02,00,FAULT 02 MAIN   FLOOR MOTION    $[C][L] [hwalrm1]
2019-01-22 17:23:15 - Hon: Partition State Change [hwalrm1]
2019-01-22 17:23:15 - Hon: Virtual Keypad Update (01,0008,02,00,FAULT 02 MAIN   FLOOR MOTION    $) [hwalrm1]
2019-01-22 17:23:15 - Hon/ISY: Zone 2 (Main floor PIR (Zone 02)) Open [hwalrm1]
2019-01-22 17:23:18 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-22 17:23:18 - Hon TCP: %00,01,0008,04,00,FAULT 04        BASEMENT MOTION $[C][L] [hwalrm1]
2019-01-22 17:23:18 - Hon: Virtual Keypad Update (01,0008,04,00,FAULT 04        BASEMENT MOTION $) [hwalrm1]
2019-01-22 17:23:18 - Hon/ISY: Zone 4 (Basement motion (Zone 04)) Open [hwalrm1]
Yea so I'll have to use the panel all clear to clear the CO.  Should be fine.
Thanks so much. Updated to latest version. CO Trouble variable now appears in partition node. Unfortunately when there is CO trouble the variable doesn't change (panel trouble changes to 1 but CO trouble stays at 0). Fire trouble works as it should. Here are the logs.
2019-01-25 22:05:49 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-25 22:05:49 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:05:49 - Hon: Partition State Change [hwalrm1]
2019-01-25 22:05:49 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-25 22:05:52 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:05:52 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:05:52 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:05:56 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:05:56 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:05:56 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:05:56 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-25 22:05:59 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:05:59 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:03 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:03 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:04 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:04 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:04 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:06 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:06 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:06 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:10 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:10 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:12 - Hon TCP: Polling Alarm [hwalrm1]
2019-01-25 22:06:12 - Hon TCP: Data Received - 9 Bytes [hwalrm1]
2019-01-25 22:06:12 - Hon TCP: ^00,00$[C][L] [hwalrm1]
2019-01-25 22:06:14 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:14 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:14 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:15 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:15 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:19 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:19 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:19 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:19 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:23 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:23 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:24 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:06:24 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-25 22:06:25 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:25 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:25 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:27 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:27 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:28 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:28 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:28 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:29 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:06:29 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-25 22:06:30 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:30 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:30 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:33 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:33 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:37 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:37 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:41 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:41 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:45 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:45 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:49 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:49 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:53 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:53 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:55 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:55 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-25 22:06:55 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-25 22:06:58 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:06:58 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:06:58 - Hon: Virtual Keypad Update (01,1C08,08,01,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-25 22:07:00 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:00 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:07:02 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:07:02 - Hon TCP: %03,3380010080$[C][L] [hwalrm1]
2019-01-25 22:07:04 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:04 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:07:04 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-25 22:07:05 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:07:05 - Hon TCP: %03,1373010010$[C][L] [hwalrm1]
2019-01-25 22:07:05 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:05 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:05 - Hon: Virtual Keypad Update (01,3208,01,04,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-25 22:07:09 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:09 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:10 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:10 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:12 - Hon TCP: Polling Alarm [hwalrm1]
2019-01-25 22:07:12 - Hon TCP: Data Received - 9 Bytes [hwalrm1]
2019-01-25 22:07:12 - Hon TCP: ^00,00$[C][L] [hwalrm1]
2019-01-25 22:07:14 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:14 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:18 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:18 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:21 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:21 - Hon TCP: %00,01,3208,01,01,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:21 - Hon: Virtual Keypad Update (01,3208,01,01,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-25 22:07:25 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:25 - Hon TCP: %00,01,3208,01,00,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-25 22:07:25 - Hon: Virtual Keypad Update (01,3208,01,00,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-25 22:07:26 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:26 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:07:26 - Hon: Virtual Keypad Update (01,1C08,08,01,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-25 22:07:30 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:30 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-25 22:07:30 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-25 22:07:30 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-25 22:07:30 - Hon TCP: %03,3373010010$[C][L] [hwalrm1]
2019-01-25 22:07:40 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-25 22:07:40 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
Yep, my bad.  These panels are a pain.  You can manually download this one to try:
Thanks for having a look. Same behaviour with this version. Log:
2019-01-26 11:40:56 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:40:57 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:40:57 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:40:57 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:00 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:00 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:01 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:41:01 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-26 11:41:04 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:04 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:06 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:06 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:06 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:08 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:08 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:08 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:11 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:11 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:13 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:13 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:16 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:16 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:16 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:20 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:20 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:21 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:21 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:24 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-26 11:41:24 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:24 - Hon: Partition State Change [hwalrm1]
2019-01-26 11:41:24 - Hon: Virtual Keypad Update (01,0208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:26 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-26 11:41:26 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:41:26 - Hon: Partition State Change [hwalrm1]
2019-01-26 11:41:26 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:41:30 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:30 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:41:30 - Hon: Virtual Keypad Update (01,1C08,08,01,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:41:33 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:33 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:41:33 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:41:34 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:41:34 - Hon TCP: %03,3380010080$[C][L] [hwalrm1]
2019-01-26 11:41:43 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:43 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:41:44 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:44 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:41:44 - Hon: Virtual Keypad Update (01,3208,01,04,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-26 11:41:48 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:48 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:41:49 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:41:49 - Hon TCP: %03,1373010010$[C][L] [hwalrm1]
2019-01-26 11:41:51 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:51 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:41:54 - Hon TCP: Polling Alarm [hwalrm1]
2019-01-26 11:41:54 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:54 - Hon TCP: %00,01,3208,01,04,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:41:55 - Hon TCP: Data Received - 9 Bytes [hwalrm1]
2019-01-26 11:41:55 - Hon TCP: ^00,00$[C][L] [hwalrm1]
2019-01-26 11:41:56 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:41:56 - Hon TCP: %00,01,3208,01,01,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:41:56 - Hon: Virtual Keypad Update (01,3208,01,01,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-26 11:42:00 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:00 - Hon TCP: %00,01,3208,01,00,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:42:00 - Hon: Virtual Keypad Update (01,3208,01,00,****DISARMED****FIRE TROUBLE  01$) [hwalrm1]
2019-01-26 11:42:04 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:04 - Hon TCP: %00,01,3208,01,00,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:42:08 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:08 - Hon TCP: %00,01,3208,01,00,****DISARMED****FIRE TROUBLE  01$[C][L] [hwalrm1]
2019-01-26 11:42:09 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:09 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:09 - Hon: Virtual Keypad Update (01,1C08,08,01,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:42:12 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:12 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:13 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:42:13 - Hon TCP: %03,3373010010$[C][L] [hwalrm1]
2019-01-26 11:42:15 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:15 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:15 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:42:19 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-26 11:42:19 - Hon TCP: %02,0300000000000000$[C][L]%00,01,0C08,08,00,****DISARMED****Hit * for faults$[C][L] [hwalrm1]
2019-01-26 11:42:19 - Hon: Partition State Change [hwalrm1]
2019-01-26 11:42:19 - Hon: Virtual Keypad Update (01,0C08,08,00,****DISARMED****Hit * for faults$) [hwalrm1]
2019-01-26 11:42:19 - Hon TCP: Data Received - 92 Bytes [hwalrm1]
2019-01-26 11:42:19 - Hon TCP: %01,00020000000000000000000000000000$[C][L]%00,01,0008,10,00,FAULT 10 FAMILY ROOM MOTION     $[C][L] [hwalrm1]
2019-01-26 11:42:19 - Hon: 01 - Zone State Change [hwalrm1]
2019-01-26 11:42:19 - Hon: Virtual Keypad Update (01,0008,10,00,FAULT 10 FAMILY ROOM MOTION     $) [hwalrm1]
2019-01-26 11:42:19 - Hon/ISY: Zone 10 (Family Room PIR (Zone 10)) Open [hwalrm1]
2019-01-26 11:42:22 - Hon TCP: Data Received - 76 Bytes [hwalrm1]
2019-01-26 11:42:22 - Hon TCP: %02,0100000000000000$[C][L]%00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:42:22 - Hon: Partition State Change [hwalrm1]
2019-01-26 11:42:22 - Hon: Virtual Keypad Update (01,1208,08,04,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:42:26 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:26 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:42:26 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:42:26 - Hon TCP: %03,1380010080$[C][L] [hwalrm1]
2019-01-26 11:42:30 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:30 - Hon TCP: %00,01,1208,08,04,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:42:33 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:33 - Hon TCP: %00,01,1208,08,00,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:42:33 - Hon: Virtual Keypad Update (01,1208,08,00,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:42:35 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:35 - Hon TCP: %00,01,1208,08,01,****DISARMED****CO TROUBLE    08$[C][L] [hwalrm1]
2019-01-26 11:42:35 - Hon: Virtual Keypad Update (01,1208,08,01,****DISARMED****CO TROUBLE    08$) [hwalrm1]
2019-01-26 11:42:39 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:39 - Hon TCP: %00,01,1C08,08,01,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:39 - Hon: Virtual Keypad Update (01,1C08,08,01,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:42:43 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:43 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:43 - Hon: Virtual Keypad Update (01,1C08,08,00,****DISARMED****  Ready to Arm  $) [hwalrm1]
2019-01-26 11:42:43 - Hon TCP: Data Received - 17 Bytes [hwalrm1]
2019-01-26 11:42:43 - Hon TCP: %03,3380010080$[C][L] [hwalrm1]
2019-01-26 11:42:53 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:42:53 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:42:54 - Hon TCP: Polling Alarm [hwalrm1]
2019-01-26 11:42:54 - Hon TCP: Data Received - 9 Bytes [hwalrm1]
2019-01-26 11:42:54 - Hon TCP: ^00,00$[C][L] [hwalrm1]
2019-01-26 11:43:03 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:43:03 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:43:13 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:43:13 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:43:23 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:43:23 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
2019-01-26 11:43:32 - Hon TCP: Data Received - 53 Bytes [hwalrm1]
2019-01-26 11:43:32 - Hon TCP: %00,01,1C08,08,00,****DISARMED****  Ready to Arm  $[C][L] [hwalrm1]
Edited by beninsteon