After upgrading from 2.7.13 to 2.7.14RC1, my isy-99 has stopped writing to the log. It has gone a couple of days now without any log entries. I tried clearing the log but only a portion of the log was cleared.
Any ideas?
--Bruce
Hi Bruce,
I am so very sorry to hear this. Has the log actually been cleared? Would you be kind enough to clear the log and then right mouse click on Network and then choose Query.
Please note that if you have less than 32 entries in the memory, log is not flushed till such time that you have more. So, you may want to do the query twice.
Hi Michel,
When I cleared the log right after I noticed that nothing was being logged, the log went from 41833 lines to 9102 lines.
As per your instructions, I cleared the log again and did the right click on Network/Query twice. Then after a few minutes, I checked the log and found that no new entries were added to the log and the log is still at 9102 lines.
I am using tools/log to write the log out to a .txt file to check it.
Regards,
Bruce
Hi Bruce,
Hi Michel,
I have sent the zip file containing the SD card contents.
I am not sure of the size limits that my ISP puts on email attachments.
So please confirm when you have received it.
Regards,
Bruce
Hi Bruce,
Thanks so very much. At this point, I have to think that this is a bug and I would sincerely appreciate your help. Would it be possible for you to take the SD Card out, zip all contents therein and send it to tech@universal-devices.com?
Thanks and with kind regards,
Hello MAC users in general and Jeff in particular,
Based on your input, we started some root cause analysis and you were right: something did get broken in 2.7.12. In fact, the problem is that we changed the networking/TCP code to support Verizon FIOS/ActionTec routers which do not like tcp window size of 0 during the handshake. So, when we put a workaround for that issue, MAC upload got broken because MAC does NOT understand any other tcp window sizes unless EXPLICITLY provided by the application. So, what we did is to specify the tcp window size in the Admin Console. This should work for all platforms even though window size should be negotiated (as such I believe there is a bug in MAC). In any case, please try:
Michel,
I verified that I can upload using the latest JWS admin console app on my Mac (MacOS 10.6.3, Java 1.6.0_17 64-bit) against my ISY99i running 2.7.14RC1. I re-loaded 2.7.14RC1 on the first try.
Thanks for the quick fix!
-Jeff
http://www.universal-devices.com/99i/2.7.14/admin.jnlp and let me know if you can upload (make sure to use CWT of 10,000 for http). If so, then I will consider this case closed. Otherwise, we will have to do more digging.
Success using this method to upgrade 2.7.13 to 2.7.14 on a Mac running 10.5.8 (Leopard) on the first try.
I retain the unusual issue of the Java applet calling on 1.5 instead of 1.6 and so I cannot run the ISY admin console from inside a browser, only with the jnlp application.
Also, version 1 t-stat adapters do not appear to updating their 'Fan State' with either a programmatic nor manual 'Query'
Hi all,
Thanks so very much for the verification. Appreciate it.
Illusion, I have the same problem with my MAC. The problem is that I have yet to find a JVM 1.6 that supports 32 bit systems. Unfortunately, mine is 32 bits and that's why everything reverts to 1.5.
Does anyone else have a problem with the fan state not reporting?
With my v2 thermostat adapter + Venstar T1800:
- If fan is manually turned on (button on T1800), ISY99i reflects the state change to "On"
- If fan is turned on automatically because the system is heating or cooling, fan state does not change; it remains in "auto"
Aside: Perhaps the control is inappropriately labeled? It seems this is more of a "fan mode" control rather than "fan state" (i.e., is the fan running or not?).
-Jeff
Hi Illusion,
Thanks for the tip ... indeed that works properly. I wonder what's the cause.
Jeff,
Fan should also update when you go from Auto to On. The only time it may not work is if you change the mode quickly which does not give enough time for the dongle to sense the change.
Greetings
My T1800 + V2 thermostat dongle seems to be working fine, but looking at the logs I am now getting weird heat setpoints sent or somehow generated transiently.
Here's an excerpt from this morning's log: (this looks fine in a wider window, sorry if it wraps on posting):
Hallway_Thermostat - Main Thermostat Mode Auto Tue 2010/04/06 08:07:06 AM Program Log
Hallway_Thermostat - Main Heat Setpoint 70° Tue 2010/04/06 08:07:08 AM Program Log
Garage_HW_Pump On 255 Tue 2010/04/06 08:07:09 AM Program Log
Garage_HW_Pump Tue 2010/04/06 08:07:13 AM System -2
Hallway_Thermostat - Main Thermostat Mode Auto Tue 2010/04/06 08:08:16 PM Program Log
Hallway_Thermostat - Main Heat Setpoint 16° Tue 2010/04/06 08:08:18 PM System Log
Hallway_Thermostat - Main Heat Setpoint 70° Tue 2010/04/06 08:08:18 PM Program Log
Hallway_Thermostat - Main Setpoint 32 Tue 2010/04/06 08:08:18 PM System Log
Garage_HW_Pump On 255 Tue 2010/04/06 08:08:19 PM Program Log
Hallway_Thermostat - Main Heat Setpoint 70° Tue 2010/04/06 08:08:19 PM System Log
Hallway_Thermostat - Main Setpoint 140 Tue 2010/04/06 08:08:19 PM System Log
What the heck is that 16 degrees in the middle of that record? Am I being tripped up by the "-2" reported after the Garage_HW_Pump was set on (yep, it's a v35 SwitchLinc I guess I ought to call Smarthome about replacing :wink:
And what is the relationship between "Setpoint" and "Heat Setpoint"? Are they always issued together and setpoint is double the temperature in F?
Thanks in advance and kind regards,
Simon
PS - I agree, "fan state" should be called "fan mode" to make more sense.
Hi Simon,
Those numbers are quite strange especially the 16. The 140 I can understand since communicating with the thermostat requires using the actual setpoint x 2. Sometimes, the thermostat might act erratically since the group commands it sends use the actual temp.
I do not think this has to do with your SWL35. If you don't mind, please send me the program that was running at that time.
Michel,
As discussed offline I have been using a new program scheme that leaves plenty of time between "mode set" thermostat command and any subsequent setpoint commands. It seemed to help.
Unfortunately I have to report that I am still getting these erroneous "16" setpoints thrown in. On the plus side I can say now that it is clearly happening immediately following the "mode set auto" command.
Kind regards,
Simon
Hi Simon,
Thanks so very much for the update. Perhaps we should do a constraint check in the code as a workaround. I hate this solution because it does not address the main issue of the thermostat sending the wrong data but it seems that we do not have a choice.
Hi Michel,
I have been having problems for a few releases now using device reported Insteon communication under advanced options.
I2, devices will not add in this mode giving an error; New links in this mode don't seem like there added, though I get no errors.
I understand this mode is not recommended and most users had problems, but for me it was opposite; It worked good and the speed increase was noticeable also a few times (RemoteLincs) it seemed to work better than I1.
A large amount of my devices are I2, as I had lots of LampLincs that died on me and where replaced, also I have many access-points.
It still could be communication or other issues but If you could do some quick testing on your end I would appreciate it.
Nick
Hi Nick,
Please note that even if a device reports i2 it does NOT mean that the device supports i2 programming for link database. This is why we had to introduce automatic mode since except for motion sensor, triggerlinc, and some function of thermostat, i2 commands were NOT reliable and caused more harm than good.
If you can add motion sensors/triggerlincs, and thermostats then I would strongly advise against using the device reported mode since it's basically quite unpredictable.
Swithlinc Relay v.3A
Programmaticly set LED backlight brightness to:
100% led is bright
50% can't see much change to the eye
1% led is very very dim but still on
0% led is screaming bright. Like twice as bright as 100%
Keypadlinc v.33
I am not quite sure how the LED brightness levels work. I upgraded from version 2.7.6 where the LED brightness allowed me to set it up to a maximum of 63. That is where I had it set. I just tried to set it using 2.7.14. I set the On level to the maximum of 15 and the brightness on the KPL seemed to be cut in half of what it was previously. I then experimented and set the Off level to the maximum of 7 and the brightness went even brighter than it was in 2.7.6. How are the LED levels supposed to work?
Also, the contextual menu (right click) in the admin console does not persist unless I hold down the right mouse button.
Troy
Hi Illusion,
Thanks so very much for the feedback. This is probably another case of firmware idiosyncrasies between devices.
Hi Troy,
There was indeed a problem with releases starting at 2.7.8 where LED brightness would not work on certain KPLs. This has been fixed in 2.7.15 (which should be our official release).
In short, this is how it works:
1. You have Off Level ... i.e the brightness level for when the button is in the Off mode
2. You have On Level ... i.e the brightness level for when the button is in the On mode
3. And, the most important thing to note is that the On Level is a function of the Off Level. So, the lower the Off Level, then the lower the On Level
Keypadlinc v.33
Troy
I have been using the "set scene" feature in programs to change the way my motion sensors control the lighting. It has been working beautifully until recently when I began noticing my scene changes weren't being written to the device. After scratching my head a while, I finally realized that I had disabled the "automatically write changes to devices" button. In essence, my program was being blocked because the ISY was holding the changes until sent manually to the devices.
It would be nice if there were an alert that pops up when you disable the "auto write to devices" that tells you this will screw up your programs if you do this.
Hi All,
Just updated my ISY from 2.7.12 to 2.7.14.
Update installed successfully however had a very interesting item come up. Installed , closed all browser windows, cleared java cache and then reopened Admin. On my first launch of Admin I noticed one of my keypad linc relays had “ioio†next to each button. I know for sure this was not appearing immediately prior to update from login of two separate computers few mins before update.
Interestingly enough I had been having problems being able to link the keypad linc relay successfully in a scene where the ISY would show units linked fine and all controllable via ISY fine however keypad linc relay would not respond to remote units
Right clicked and selected ‘write updates to device’
Here is the log:
Mon 04/26/2010 02:38:55 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:38:55 PM : [F D2 55 1 ] Link 4 : 0FD8 [A2200FD929FF1F07] Writing [A2200FD929FF1F07]
Mon 04/26/2010 02:38:55 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:38:56 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:38:56 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:38:56 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D8 06 PEEK (D8)
Mon 04/26/2010 02:38:56 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:38:56 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:38:57 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:38:57 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:38:57 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D9 06 PEEK (D9)
Mon 04/26/2010 02:38:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 20 PEEK (20)
Mon 04/26/2010 02:38:58 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:38:58 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:38:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:38:58 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:38:58 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DA 06 PEEK (DA)
Mon 04/26/2010 02:38:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 0F PEEK (0F)
Mon 04/26/2010 02:38:59 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:38:59 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:38:59 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:38:59 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DB 06 PEEK (DB)
Mon 04/26/2010 02:38:59 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:00 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:00 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:00 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:00 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DC 06 PEEK (DC)
Mon 04/26/2010 02:39:00 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:39:00 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:01 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:01 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:01 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:01 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DD 06 PEEK (DD)
Mon 04/26/2010 02:39:01 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B FF PEEK (FF)
Mon 04/26/2010 02:39:01 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:02 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:02 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:02 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:02 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DE 06 PEEK (DE)
Mon 04/26/2010 02:39:02 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 1F PEEK (1F)
Mon 04/26/2010 02:39:02 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:03 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:03 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:03 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:03 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B DF 06 PEEK (DF)
Mon 04/26/2010 02:39:04 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 07 PEEK (07)
Mon 04/26/2010 02:39:04 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:04 PM : [MNG-LNK-RSP ] 02 6F 40 E2 20 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:39:04 PM : [PLM ] Group 32 : Writing Controller Link matching [F D2 55 1 ] Link 4 : 0FD8 [A2200FD929FF1F07]
Mon 04/26/2010 02:39:04 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:39:04 PM : [F D2 55 1 ] Link 5 : 0FD0 [A21D0FD929FF1F07] Writing [A21D0FD929FF1F07]
Mon 04/26/2010 02:39:04 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:05 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:05 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:05 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D0 06 PEEK (D0)
Mon 04/26/2010 02:39:05 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:39:05 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:05 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:05 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:06 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D1 06 PEEK (D1)
Mon 04/26/2010 02:39:06 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 1D PEEK (1D)
Mon 04/26/2010 02:39:06 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:06 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:06 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:07 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D2 06 PEEK (D2)
Mon 04/26/2010 02:39:07 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:39:07 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:07 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:07 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:08 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D3 06 PEEK (D3)
Mon 04/26/2010 02:39:08 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:08 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:08 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:09 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:09 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:09 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D4 06 PEEK (D4)
Mon 04/26/2010 02:39:09 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B 29 PEEK (29)
Mon 04/26/2010 02:39:09 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:09 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:10 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:10 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:10 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D5 06 PEEK (D5)
Mon 04/26/2010 02:39:11 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B FF PEEK (FF)
Mon 04/26/2010 02:39:11 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:11 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:12 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:12 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:12 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D6 06 PEEK (D6)
Mon 04/26/2010 02:39:12 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 1F PEEK (1F)
Mon 04/26/2010 02:39:12 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:12 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:13 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:13 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:13 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B D7 06 PEEK (D7)
Mon 04/26/2010 02:39:13 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 07 PEEK (07)
Mon 04/26/2010 02:39:13 PM : [MNG-LNK-RSP ] 02 6F 40 E2 1D 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:39:13 PM : [PLM ] Group 29 : Writing Controller Link matching [F D2 55 1 ] Link 5 : 0FD0 [A21D0FD929FF1F07]
Mon 04/26/2010 02:39:13 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:39:13 PM : [F D2 55 1 ] Link 6 : 0FC8 [A21D0FD929FF1F05] Writing [A21D0FD929FF1F05]
Mon 04/26/2010 02:39:14 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:14 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:14 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:14 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C8 06 PEEK (C8)
Mon 04/26/2010 02:39:14 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:39:15 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:15 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:15 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:15 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C9 06 PEEK (C9)
Mon 04/26/2010 02:39:16 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B 1D PEEK (1D)
Mon 04/26/2010 02:39:16 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:16 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:16 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:16 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:16 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CA 06 PEEK (CA)
Mon 04/26/2010 02:39:16 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:39:17 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:17 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:17 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:17 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CB 06 PEEK (CB)
Mon 04/26/2010 02:39:18 PM : [iNST-ERX ] 02 51 0F D2 55 0F D9 29 75 5F ED A0 11 00 00 20 20 1F FF 3F 00 09 00 00 00
Mon 04/26/2010 02:39:18 PM : [standard-Cleanup Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=1, Hops Left=1
Mon 04/26/2010 02:39:18 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:18 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:18 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:18 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:18 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:19 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CC 06 PEEK (CC)
Mon 04/26/2010 02:39:19 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 29 PEEK (29)
Mon 04/26/2010 02:39:19 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:19 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:19 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:19 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:20 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CD 06 PEEK (CD)
Mon 04/26/2010 02:39:20 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B FF PEEK (FF)
Mon 04/26/2010 02:39:20 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:20 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:20 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:21 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CE 06 PEEK (CE)
Mon 04/26/2010 02:39:21 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 1F PEEK (1F)
Mon 04/26/2010 02:39:21 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:21 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:22 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:22 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:22 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B CF 06 PEEK (CF)
Mon 04/26/2010 02:39:22 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 05 PEEK (05)
Mon 04/26/2010 02:39:22 PM : [MNG-LNK-RSP ] 02 6F 40 E2 1D 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:39:22 PM : [PLM ] Group 29 : Writing Controller Link matching [F D2 55 1 ] Link 6 : 0FC8 [A21D0FD929FF1F05]
Mon 04/26/2010 02:39:22 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:39:22 PM : [F D2 55 1 ] Link 7 : 0FC0 [A21C0FD929FF1F02] Writing [A21C0FD929FF1F02]
Mon 04/26/2010 02:39:23 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:23 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:23 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:23 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C0 06 PEEK (C0)
Mon 04/26/2010 02:39:23 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:39:24 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:24 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:24 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:24 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C1 06 PEEK (C1)
Mon 04/26/2010 02:39:25 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 1C PEEK (1C)
Mon 04/26/2010 02:39:25 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:25 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:25 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:25 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:25 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C2 06 PEEK (C2)
Mon 04/26/2010 02:39:25 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:39:26 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:26 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:26 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:26 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C3 06 PEEK (C3)
Mon 04/26/2010 02:39:27 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:27 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:27 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:27 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:27 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C4 06 PEEK (C4)
Mon 04/26/2010 02:39:28 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 29 PEEK (29)
Mon 04/26/2010 02:39:28 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:28 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:29 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:29 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:29 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C5 06 PEEK (C5)
Mon 04/26/2010 02:39:29 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B FF PEEK (FF)
Mon 04/26/2010 02:39:29 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:29 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:29 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:30 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C6 06 PEEK (C6)
Mon 04/26/2010 02:39:30 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B 1F PEEK (1F)
Mon 04/26/2010 02:39:30 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:30 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:30 PM : [iNST-ERX ] 02 51 0F D2 55 0F D9 29 75 41 BF D0 61 00 00 20 20 1F FF 3F 00 09 00 00 00
Mon 04/26/2010 02:39:30 PM : [standard-Cleanup Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=1, Hops Left=1
Mon 04/26/2010 02:39:31 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:31 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:31 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B C7 06 PEEK (C7)
Mon 04/26/2010 02:39:31 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 02 PEEK (02)
Mon 04/26/2010 02:39:31 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:31 PM : [MNG-LNK-RSP ] 02 6F 40 E2 1C 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:39:31 PM : [PLM ] Group 28 : Writing Controller Link matching [F D2 55 1 ] Link 7 : 0FC0 [A21C0FD929FF1F02]
Mon 04/26/2010 02:39:31 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:39:31 PM : [F D2 55 1 ] Link 8 : 0FB8 [A2000FD929FF1F00] Writing [A2000FD929FF1F00]
Mon 04/26/2010 02:39:32 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:32 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:32 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:32 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B8 06 PEEK (B8)
Mon 04/26/2010 02:39:33 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:39:33 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:33 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:33 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:33 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B9 06 PEEK (B9)
Mon 04/26/2010 02:39:34 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 00 PEEK (00)
Mon 04/26/2010 02:39:34 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:34 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:34 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:34 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:34 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BA 06 PEEK (BA)
Mon 04/26/2010 02:39:35 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:39:35 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:35 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:36 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:36 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:36 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BB 06 PEEK (BB)
Mon 04/26/2010 02:39:36 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:36 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:37 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:37 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:37 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BC 06 PEEK (BC)
Mon 04/26/2010 02:39:37 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 29 PEEK (29)
Mon 04/26/2010 02:39:37 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:38 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:38 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:39:38 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BD 06 PEEK (BD)
Mon 04/26/2010 02:39:38 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B FF PEEK (FF)
Mon 04/26/2010 02:39:38 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:38 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:39 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:39 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:39 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BE 06 PEEK (BE)
Mon 04/26/2010 02:39:40 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 1F PEEK (1F)
Mon 04/26/2010 02:39:40 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:40 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:40 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:40 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B BF 06 PEEK (BF)
Mon 04/26/2010 02:39:41 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:39:41 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:41 PM : [MNG-LNK-RSP ] 02 6F 40 E2 00 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:39:41 PM : [PLM ] Group 0 : Writing Controller Link matching [F D2 55 1 ] Link 8 : 0FB8 [A2000FD929FF1F00]
Mon 04/26/2010 02:39:41 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:39:41 PM : [F D2 55 1 ] Link 9 : 0FB0 [A21E0FD929FF1F01] Writing [A21E0FD929FF1F01]
Mon 04/26/2010 02:39:41 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:42 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:42 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:42 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B0 06 PEEK (B0)
Mon 04/26/2010 02:39:42 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:39:42 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:43 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:43 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:43 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B1 06 PEEK (B1)
Mon 04/26/2010 02:39:43 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 1E PEEK (1E)
Mon 04/26/2010 02:39:43 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:44 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:44 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:44 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B2 06 PEEK (B2)
Mon 04/26/2010 02:39:44 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:39:44 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:45 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:45 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:45 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B3 06 PEEK (B3)
Mon 04/26/2010 02:39:45 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:39:45 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:46 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:46 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:46 PM : [iNST-ACK ] 02 62 0F.D2.55 0F B4 00 06 (00)
Mon 04/26/2010 02:39:46 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B B4 00 (00)
Mon 04/26/2010 02:39:46 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:55 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:55 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:55 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:56 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B4 06 PEEK (B4)
Mon 04/26/2010 02:39:57 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:39:57 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:57 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:39:57 PM : [iNST-ERX ] 02 51 0F D2 55 0F D9 29 10 D7 CF FA 01 00 00 20 20 1F FF 3F 00 09 00 00 00
Mon 04/26/2010 02:39:57 PM : [Extended-Direct][0F.D2.55-->ISY/PLM Group=0] Max Hops=0, Hops Left=0
Mon 04/26/2010 02:39:57 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 28 0F SET-MSB(0F)
Mon 04/26/2010 02:39:57 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:39:57 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B5 06 PEEK (B5)
Mon 04/26/2010 02:39:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B FF PEEK (FF)
Mon 04/26/2010 02:39:58 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:39:58 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:07 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:07 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:07 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:07 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B6 06 PEEK (B6)
Mon 04/26/2010 02:40:08 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 1F PEEK (1F)
Mon 04/26/2010 02:40:08 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:08 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:08 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:08 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B B7 06 PEEK (B7)
Mon 04/26/2010 02:40:09 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 01 PEEK (01)
Mon 04/26/2010 02:40:09 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:09 PM : [MNG-LNK-RSP ] 02 6F 40 E2 1E 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:40:09 PM : [PLM ] Group 30 : Writing Controller Link matching [F D2 55 1 ] Link 9 : 0FB0 [A21E0FD929FF1F01]
Mon 04/26/2010 02:40:09 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:09 PM : [F D2 55 1 ] Link 10 : 0FA8 [A23B0FD929FF1F01] Writing [A23B0FD929FF1F01]
Mon 04/26/2010 02:40:09 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:10 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:10 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:10 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A8 06 PEEK (A8)
Mon 04/26/2010 02:40:10 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B A2 PEEK (A2)
Mon 04/26/2010 02:40:10 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:11 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:11 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:11 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A9 06 PEEK (A9)
Mon 04/26/2010 02:40:11 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 3B PEEK (3B)
Mon 04/26/2010 02:40:11 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:12 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:12 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:12 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AA 06 PEEK (AA)
Mon 04/26/2010 02:40:13 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 0F PEEK (0F)
Mon 04/26/2010 02:40:13 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:13 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:14 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:14 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:14 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AB 06 PEEK (AB)
Mon 04/26/2010 02:40:14 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:40:14 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:14 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:14 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:15 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AC 06 PEEK (AC)
Mon 04/26/2010 02:40:15 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:40:15 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:15 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:15 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:16 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AD 06 PEEK (AD)
Mon 04/26/2010 02:40:16 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B FF PEEK (FF)
Mon 04/26/2010 02:40:16 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:16 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:16 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:16 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:17 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AE 06 PEEK (AE)
Mon 04/26/2010 02:40:17 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 1F PEEK (1F)
Mon 04/26/2010 02:40:17 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:17 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:18 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:18 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:18 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B AF 06 PEEK (AF)
Mon 04/26/2010 02:40:18 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 01 PEEK (01)
Mon 04/26/2010 02:40:18 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:18 PM : [MNG-LNK-RSP ] 02 6F 40 E2 3B 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:40:18 PM : [PLM ] Group 59 : Writing Controller Link matching [F D2 55 1 ] Link 10 : 0FA8 [A23B0FD929FF1F01]
Mon 04/26/2010 02:40:18 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:18 PM : [F D2 55 1 ] Link 11 : 0FA0 [E20109FAE4000001] Writing [E20109FAE4000001]
Mon 04/26/2010 02:40:19 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:19 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:19 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:19 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A0 06 PEEK (A0)
Mon 04/26/2010 02:40:20 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B E2 PEEK (E2)
Mon 04/26/2010 02:40:20 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:20 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:20 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:20 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A1 06 PEEK (A1)
Mon 04/26/2010 02:40:21 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 01 PEEK (01)
Mon 04/26/2010 02:40:21 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:21 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:21 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:21 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A2 06 PEEK (A2)
Mon 04/26/2010 02:40:22 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 09 PEEK (09)
Mon 04/26/2010 02:40:22 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:22 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:22 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:22 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A3 06 PEEK (A3)
Mon 04/26/2010 02:40:23 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B FA PEEK (FA)
Mon 04/26/2010 02:40:23 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:23 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:23 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:23 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:23 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A4 06 PEEK (A4)
Mon 04/26/2010 02:40:24 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B E4 PEEK (E4)
Mon 04/26/2010 02:40:24 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:24 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:24 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:24 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A5 06 PEEK (A5)
Mon 04/26/2010 02:40:25 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 00 PEEK (00)
Mon 04/26/2010 02:40:25 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:25 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:25 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:25 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:25 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A6 06 PEEK (A6)
Mon 04/26/2010 02:40:26 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:40:26 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:26 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:26 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:26 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B A7 06 PEEK (A7)
Mon 04/26/2010 02:40:27 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 01 PEEK (01)
Mon 04/26/2010 02:40:27 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:27 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:27 PM : [F D2 55 1 ] Link 12 : 0F98 [E2010FD929000001] Writing [E2010FD929000001]
Mon 04/26/2010 02:40:27 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:27 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:27 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 98 06 PEEK (98)
Mon 04/26/2010 02:40:28 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B E2 PEEK (E2)
Mon 04/26/2010 02:40:28 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:40:28 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:28 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:28 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:28 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 99 06 PEEK (99)
Mon 04/26/2010 02:40:29 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 01 PEEK (01)
Mon 04/26/2010 02:40:29 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:29 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:30 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:30 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:30 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9A 06 PEEK (9A)
Mon 04/26/2010 02:40:30 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:40:30 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:31 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:31 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:31 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9B 06 PEEK (9B)
Mon 04/26/2010 02:40:31 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:40:31 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:32 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:32 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:32 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9C 06 PEEK (9C)
Mon 04/26/2010 02:40:32 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:40:32 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:33 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:33 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:33 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9D 06 PEEK (9D)
Mon 04/26/2010 02:40:33 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:40:33 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:34 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:34 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:34 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9E 06 PEEK (9E)
Mon 04/26/2010 02:40:34 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 00 PEEK (00)
Mon 04/26/2010 02:40:34 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:34 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:35 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:35 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:35 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 9F 06 PEEK (9F)
Mon 04/26/2010 02:40:35 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 01 PEEK (01)
Mon 04/26/2010 02:40:36 PM : [MNG-LNK-RSP ] 02 6F 41 A2 01 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:40:36 PM : [PLM ] Group 1 : Writing Responder Link matching [F D2 55 1 ] Link 12 : 0F98 [E2010FD929000001]
Mon 04/26/2010 02:40:36 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:36 PM : [F D2 55 1 ] Link 13 : 0F90 [E2020FD929000002] Writing [E2020FD929000002]
Mon 04/26/2010 02:40:36 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:36 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:36 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:36 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 90 06 PEEK (90)
Mon 04/26/2010 02:40:37 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B E2 PEEK (E2)
Mon 04/26/2010 02:40:37 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:37 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:37 PM : [iNST-ERX ] 02 51 0F D2 55 0F D9 29 75 41 BF D0 61 00 00 20 20 1F FF 3F 00 09 00 00 00
Mon 04/26/2010 02:40:37 PM : [standard-Cleanup Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=1, Hops Left=1
Mon 04/26/2010 02:40:38 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:38 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:40:38 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 91 06 PEEK (91)
Mon 04/26/2010 02:40:38 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 02 PEEK (02)
Mon 04/26/2010 02:40:38 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:38 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:39 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:39 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:39 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 92 06 PEEK (92)
Mon 04/26/2010 02:40:39 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:40:39 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:39 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:40 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:40 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:40 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 93 06 PEEK (93)
Mon 04/26/2010 02:40:40 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:40:40 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:40 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:41 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:41 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:41 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 94 06 PEEK (94)
Mon 04/26/2010 02:40:41 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:40:41 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:41 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:42 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:42 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:42 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 95 06 PEEK (95)
Mon 04/26/2010 02:40:42 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:40:42 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:42 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:43 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:43 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:43 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 96 06 PEEK (96)
Mon 04/26/2010 02:40:43 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:40:43 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:44 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:44 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:44 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 97 06 PEEK (97)
Mon 04/26/2010 02:40:45 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 23 2B 02 PEEK (02)
Mon 04/26/2010 02:40:45 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=0
Mon 04/26/2010 02:40:45 PM : [MNG-LNK-RSP ] 02 6F 41 A2 02 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:40:45 PM : [PLM ] Group 2 : Writing Responder Link matching [F D2 55 1 ] Link 13 : 0F90 [E2020FD929000002]
Mon 04/26/2010 02:40:45 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:45 PM : [F D2 55 1 ] Link 14 : 0F88 [E2030FD929000003] Writing [E2030FD929000003]
Mon 04/26/2010 02:40:45 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:45 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:45 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:46 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 88 06 PEEK (88)
Mon 04/26/2010 02:40:46 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B E2 PEEK (E2)
Mon 04/26/2010 02:40:46 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:46 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:46 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:47 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 89 06 PEEK (89)
Mon 04/26/2010 02:40:47 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 03 PEEK (03)
Mon 04/26/2010 02:40:47 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:47 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:48 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:48 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:48 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8A 06 PEEK (8A)
Mon 04/26/2010 02:40:48 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:40:48 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:49 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:49 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:49 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8B 06 PEEK (8B)
Mon 04/26/2010 02:40:49 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:40:49 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:50 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:50 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:50 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8C 06 PEEK (8C)
Mon 04/26/2010 02:40:51 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 29 PEEK (29)
Mon 04/26/2010 02:40:51 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:51 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:51 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:51 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:51 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8D 06 PEEK (8D)
Mon 04/26/2010 02:40:52 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 00 PEEK (00)
Mon 04/26/2010 02:40:52 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:52 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:53 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:53 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:53 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8E 06 PEEK (8E)
Mon 04/26/2010 02:40:53 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:40:53 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:53 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:54 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:54 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:54 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 8F 06 PEEK (8F)
Mon 04/26/2010 02:40:54 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 03 PEEK (03)
Mon 04/26/2010 02:40:54 PM : [MNG-LNK-RSP ] 02 6F 41 A2 03 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:40:54 PM : [PLM ] Group 3 : Writing Responder Link matching [F D2 55 1 ] Link 14 : 0F88 [E2030FD929000003]
Mon 04/26/2010 02:40:54 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:40:54 PM : [F D2 55 1 ] Link 15 : 0F80 [E2040FD929000004] Writing [E2040FD929000004]
Mon 04/26/2010 02:40:55 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:55 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:55 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:55 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 80 06 PEEK (80)
Mon 04/26/2010 02:40:56 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B E2 PEEK (E2)
Mon 04/26/2010 02:40:56 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:40:56 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:56 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:56 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:56 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 81 06 PEEK (81)
Mon 04/26/2010 02:40:57 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 04 PEEK (04)
Mon 04/26/2010 02:40:57 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:57 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:57 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:57 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 82 06 PEEK (82)
Mon 04/26/2010 02:40:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 0F PEEK (0F)
Mon 04/26/2010 02:40:58 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:58 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:58 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:58 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 83 06 PEEK (83)
Mon 04/26/2010 02:40:59 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B D9 PEEK (D9)
Mon 04/26/2010 02:40:59 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:40:59 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:40:59 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:40:59 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 84 06 PEEK (84)
Mon 04/26/2010 02:41:00 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 29 PEEK (29)
Mon 04/26/2010 02:41:00 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:41:00 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:41:00 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:41:00 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 85 06 PEEK (85)
Mon 04/26/2010 02:41:01 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:41:01 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:41:01 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:41:10 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:41:10 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 28 0F SET-MSB(0F)
Mon 04/26/2010 02:41:10 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:41:10 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 86 06 PEEK (86)
Mon 04/26/2010 02:41:11 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 2B 00 PEEK (00)
Mon 04/26/2010 02:41:11 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 02:41:11 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:41:11 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:41:11 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 2B 87 06 PEEK (87)
Mon 04/26/2010 02:41:12 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 27 2B 04 PEEK (04)
Mon 04/26/2010 02:41:12 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 02:41:12 PM : [MNG-LNK-RSP ] 02 6F 41 A2 04 0F D2 55 02 0F 33 15
Mon 04/26/2010 02:41:12 PM : [PLM ] Group 4 : Writing Responder Link matching [F D2 55 1 ] Link 15 : 0F80 [E2040FD929000004]
Mon 04/26/2010 02:41:12 PM : [F D2 55 1 ] Using engine version i1 for 'GarageLights'
Mon 04/26/2010 02:41:12 PM : [F D2 55 1 ] Link 16 : 0F78 [E2050FD929000005] Writing [E2050FD929000005]
Mon 04/26/2010 02:41:13 PM : [iNST-ACK ] 02 62 0F.D2.55 0F 28 0F 06 SET-MSB(0F)
Mon 04/26/2010 02:41:13 PM : [iNST-SRX ] 02 50 0F.D2.55 0F.D9.29 2B 28 0F SET-MSB(0F)
Mon 04/26/2010 02:41:13 PM : [standard-Direct Ack][0F.D2.55-->ISY/PLM Group=0] Max
sorry that last post was so long ..
following up on my original issue here.
Using an EZ Raing Irrigation Controller. I can successfully update the timeouts for all of the zones except for zone 1. When I click set options for zone 1 it reads the timeout of 15 mins by doing a query, I then change the time to 30 mins and click "ok". Notably the ISY does not display the progress bar when I click "ok" setting zone 1 but it does for setting of the other zones. Re checking the "Set Options" reveals zone 1 timeout is still set for 15 mins.
log for setting time out on zone 1 (where setting does not set)
Mon 04/26/2010 06:25:03 PM : [1 73 3B 1 ] Using engine version i1 for 'EZRain 1 Front Yard'
Mon 04/26/2010 06:25:03 PM : [iNST-ACK ] 02 62 01.73.3B 0F 28 00 06 SET-MSB(00)
Mon 04/26/2010 06:25:03 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 2B 28 00 SET-MSB(00)
Mon 04/26/2010 06:25:03 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 06:25:04 PM : [iNST-ACK ] 02 62 01.73.3B 0F 2B 00 06 PEEK (00)
Mon 04/26/2010 06:25:04 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 2B 0F PEEK (0F)
Mon 04/26/2010 06:25:04 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 06:25:20 PM : [1 73 3B 1 ] Using engine version i1 for 'EZRain 1 Front Yard'
Mon 04/26/2010 06:25:21 PM : [iNST-ACK ] 02 62 01.73.3B 0F 44 01 06 (01)
Mon 04/26/2010 06:25:21 PM : [iNST-ACK ] 02 62 01.73.3B 0F 44 01 06 (01): Received an ACK for a different device
Mon 04/26/2010 06:25:21 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 23 44 01 (01)
Mon 04/26/2010 06:25:21 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=0Mon 04/26/2010 06:25:21 PM : Duplicate: ignored
Mon 04/26/2010 06:25:21 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 23 44 01 (01): Process Message: failed
Log for setting zone 7 where setting does set
Mon 04/26/2010 06:25:44 PM : [1 73 3B 7 ] Using engine version i1 for 'EZRain.7'
Mon 04/26/2010 06:25:44 PM : [iNST-ACK ] 02 62 01.73.3B 0F 28 00 06 SET-MSB(00)
Mon 04/26/2010 06:25:44 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 2B 28 00 SET-MSB(00)
Mon 04/26/2010 06:25:44 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=2
Mon 04/26/2010 06:25:44 PM : [iNST-ACK ] 02 62 01.73.3B 0F 2B 06 06 PEEK (06)
Mon 04/26/2010 06:25:45 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 2B 1E PEEK (1E)
Mon 04/26/2010 06:25:45 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 06:25:51 PM : [1 73 3B 7 ] Using engine version i1 for 'EZRain.7'
Mon 04/26/2010 06:25:51 PM : [iNST-ACK ] 02 62 01.73.3B 0F 44 01 06 (01)
Mon 04/26/2010 06:25:51 PM : [iNST-ACK ] 02 62 01.73.3B 0F 44 01 06 (01): Received an ACK for a different device
Mon 04/26/2010 06:25:51 PM : [1 73 3B 1 ] Memory : Write dbAddr=0x0006 [1D]
Mon 04/26/2010 06:25:51 PM : [1 73 3B 1 ] Using engine version i1 for 'EZRain 1 Front Yard'
Mon 04/26/2010 06:25:51 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 44 01 (01)
Mon 04/26/2010 06:25:51 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 06:25:51 PM : Duplicate: ignored
Mon 04/26/2010 06:25:51 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 44 01 (01): Process Message: failed
Mon 04/26/2010 06:25:51 PM : [iNST-ACK ] 02 62 01.73.3B 0F 28 00 06 SET-MSB(00)
Mon 04/26/2010 06:25:52 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 28 00 SET-MSB(00)
Mon 04/26/2010 06:25:52 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=1
Mon 04/26/2010 06:25:52 PM : [iNST-ACK ] 02 62 01.73.3B 0F 2B 06 06 PEEK (06)
Mon 04/26/2010 06:25:52 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 2B 1E PEEK (1E)
Mon 04/26/2010 06:25:52 PM : [iNST-ACK ] 02 62 01.73.3B 0F 29 1D 06 POKE (1D)
Mon 04/26/2010 06:25:52 PM : [iNST-SRX ] 02 50 01.43.3B 0F.D9.29 20 D4 DE (DE)
Mon 04/26/2010 06:25:52 PM : [standard-Direct Ack][01.43.3B-->ISY/PLM Group=0] Max Hops=0, Hops Left=0
Mon 04/26/2010 06:25:52 PM : [iNST-SRX ] 02 50 01.43.3B 0F.D9.29 20 D4 DE (DE): Process Message: failed
Mon 04/26/2010 06:25:53 PM : [iNST-SRX ] 02 50 01.73.3B 0F.D9.29 27 29 1D POKE (1D)
Mon 04/26/2010 06:25:53 PM : [standard-Direct Ack][01.73.3B-->ISY/PLM Group=0] Max Hops=3, Hops Left=1