Lights dimming off and on repeatedly


deirwin

Recommended Posts

I have a 2476d Switchlinc Dimmer that after I turn it on (whether regular on or fast on), dims slowly off and on and off and on repeatedly. I also have an ISY-99i Pro and an ELK M1 Gold. I've removed the switch from all programs on both ISY and ELK. I've also manually Factpry reset switch. Nothing seems to help. Has anybody had this problem?

Link to comment
I'm still having problems. It has at times gone through the dim cycle, but the odd issue is that the lights do not turn on or off, unless i double tap. has anyone had this problem?

 

It can appear as though the device isn't responding if you have programmed the device with a long ramp rate. When you select the device, what does it report as the current local rate?

Link to comment

deirwin

 

I just ran tests with a SwitchLinc Dimmer hardware sticker v5.15 firmware v.38. Changing the Local On Level and Local Ramp Rate DO NOT take effect until the SwitchLinc is power cycled (AC power removed). This can be done by turning the circuit breaker Off/On or pulling the Air Gap switch to remove power from the device. The SwitchLinc should be left off for 20/30 seconds before restoring power. If the Air Gap switch is used be careful to push it FLUSH only with the SwitchLinc frame. If pressed too far in a factory reset can be done.

 

Lee

Link to comment

Thanks Lee. On and off now work. However, lights still turn off after a while. once they stayed off and once they went back on. i used to have a test program with the nearby motion sensor theough elk 1. maybe it's connected? they just turned off and ramped back on again, then turned off.

Link to comment

deirwin

 

Very possible. If the device is being commanded from the ISY it is easy to determine. Run Tools | Diagnostics | Event Viewer with Device communications events selected. Walk past the motion sensor to trigger motion. The Event Viewer will trace any Insteon commands sent by the ISY to the SwitchLinc. If the event viewer trace is not familiar save the file and copy/paste the trace. I can interpret (need SwitchLinc Insteon address).

 

 

If the ELK is doing it all on its own (I don't own an ELK so not familiar with its capability) that would not show up.

 

Lee

Link to comment

Thanks again Lee. My kids were running through room, so taht provided some activity. Here's what I have:

 

0D.2D.38 - (2476D) Switchlinc Dimmer v.27

 

 

Sun 04/03/2011 07:41:12 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 8C (8C)

 

Sun 04/03/2011 07:41:12 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=1

 

Sun 04/03/2011 07:41:15 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 FF (FF)

 

Sun 04/03/2011 07:41:15 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=0

 

Sun 04/03/2011 07:41:50 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 FF (FF)

 

Sun 04/03/2011 07:41:50 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=0

 

Sun 04/03/2011 07:41:52 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 8C (8C)

 

Sun 04/03/2011 07:41:52 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=1

 

Sun 04/03/2011 07:41:54 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 FF (FF)

 

Sun 04/03/2011 07:41:54 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=0

 

Sun 04/03/2011 07:43:33 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 FF (FF)

 

Sun 04/03/2011 07:43:33 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=0

 

Sun 04/03/2011 07:43:35 PM : [iNST-SRX ] 02 50 0D.2D.38 01.FF.FF C7 27 84 (84)

 

Sun 04/03/2011 07:43:35 PM : [standard-Group][0D.2D.38-->01.FF.FF] Max Hops=3, Hops Left=1

 

Sun 04/03/2011 07:43:38 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 FF (FF)

 

Sun 04/03/2011 07:43:38 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=1

 

Sun 04/03/2011 07:44:10 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 00 (00)

 

Sun 04/03/2011 07:44:10 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=1

Link to comment

deirwin

 

Well that is an Insteon command I have never seen used before. It is a Light Set Status (0x27) that “Updates SwitchLinc Companion’s LEDsâ€.

 

Is that SwitchLinc part of a special package order that included multiple SwitchLincs that are prelinked together?

 

The 0x27 command is not normal Insteon device to device control of individual devices.

 

Lee

Link to comment

It is possible it was part of a 3-way packaged purchase, but not sure. I know I purchased one once. It was working fine prior to installing Elk and changing this to control different lighting.

 

I think all of this activity is related to the Elk motion detector. That was the only thing changing.

 

FYI, when we put in the Elk M1G, i programmed a Test Rule in the Elk to turn these lights on and off when motion was detected (just to see if it would work). I later deleted that Rule.

Link to comment

deirwin

 

I’ve been using Insteon almost from the beginning of Insteon. The basic structure of the commands being traced indicates a “from†device address of the SwitchLinc in question. That normally indicates the SwitchLinc paddle is being pressed but the command being sent (0x27) is not the normal command for a simple paddle press (unless related to some package of “companion†switchlincs).

 

Can you cover the ELK motion sensor (I assume it is not the Insteon motion sensor) so that it cannot signal motion to eliminate the ELK as the source of the SwitchLinc changing On levels?

 

 

Lee

Link to comment

I really appreciate your help Lee. I checked and it does not appear to be the unit that was part of a prepackaged 3-way system.

 

I covered motion detector, cleared log, then turned on light. following are results:

 

 

Sun 04/03/2011 08:48:57 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 FF (FF)

 

Sun 04/03/2011 08:48:57 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=1

 

Sun 04/03/2011 08:55:17 PM : [ Time] 20:55:18 5(0)

 

Sun 04/03/2011 08:55:32 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 00 (00)

 

Sun 04/03/2011 08:55:32 PM : [standard-Group][0D.2D.38-->Group=1] Max Hops=3, Hops Left=0

Link to comment

deirwin

 

From the cmd2 values I think the SwitchLinc was turned On at 08:48:57

 

Sun 04/03/2011 08:48:57 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C7 27 FF (FF)

 

And turned Off at 08:55:32

 

Sun 04/03/2011 08:55:32 PM : [iNST-SRX ] 02 50 0D.2D.38 00.00.01 C3 27 00 (00)

 

I doubt the Admin Console will reflect the fact that the SwitchLinc was turned On/Off manually because of the unusual Insteon command being used to control the “companion†device. Since the SwitchLinc thinks it has a “companion†device, that companion device may also be controlling this SwitchLinc.

 

 

Tom

 

Can you shed any light on a SwitchLinc companion package from years ago (firmware is v.27 so the SwitchLinc would seem to be vintage).

 

 

Lee

Link to comment

deirwin

 

I have no explanation for the SwitchLinc turning itself Off. I would look for the “companion†to this SwitchLinc. This SwitchLinc is issuing a command sequence I have never seen before. Best guess at this point is there is another SwitchLinc that is a “companion†to this one and they are interacting with each other.

 

Lee

Link to comment

Thanks LeeG. It worked perfectly prior to Elk M1G. I initially set a test rule in the Elk to have these lights turn on for a couple of minutes when motion was detected, then turn off. I think it has to be related to that. It appears all of the activity went away when i covered motion sensor and they never turned back on. Perhaps you never saw the command from Elk?

 

Has anyone else seen this or familiar with Elk?

Link to comment