Isy/PLM freeze when adding 2-wire dimmer (RF) - 2474DWH


Braq

Recommended Posts

I need help as I'm having major trouble adding 2 new switchlinc 2-wire dimmers (RF only) - model 2474DWH (v1.0) to my ISY 99i.

 

I tried everything I can think of, but cannot get ISY to finish adding them. The switchlincs are controlling the loads (ceiling lights) fine so the install is good. I tried adding them both with "new insteon device" and "start linking", but every time the progress bar quits abruptly after "writing 0 bytes to devices" and my ISY no longer sees any traffic come through so I have to cut the power to both the ISY and PLM (2413S) to get them working again. I have many other switchlincs/in-linelinc/appliancelinc/lamplinc dual band/fanlinc that I've been using for several months without any trouble and I just installed a few new keypadlincs that I was able to add to the ISY on the first try.

 

Should I be doing something special for this to work? ISY and UI are v3.2.6.

 

Here is the output from the event viewer (level 3). You can see the ISY is able to communicate with the device, but stops after "LNK-BGN".

 

Sun 09/02/2012 09:17:58 AM : ---- Initializing the linked devices ----

Sun 09/02/2012 09:17:58 AM : ---- All Linked Devices are now initialized ----

Sun 09/02/2012 09:17:58 AM : ---- Add remaining devices ----

Sun 09/02/2012 09:17:58 AM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 0D 00

Sun 09/02/2012 09:17:58 AM : [iNST-ACK ] 02 62 1E.62.A3 0F 0D 00 06 (00)

Sun 09/02/2012 09:17:58 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD A7 0D FF (FF)

Sun 09/02/2012 09:17:58 AM : [standard-Direct Nack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Sun 09/02/2012 09:17:58 AM : [iNST-TX-I2CS] 02 62 1E 62 A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6

Sun 09/02/2012 09:17:58 AM : [iNST-ACK ] 02 62 1E.62.A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6 06 LNK-ON (01)

Sun 09/02/2012 09:17:58 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 09 01 LNK-ON (01)

Sun 09/02/2012 09:17:58 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Sun 09/02/2012 09:17:58 AM : [LNK-BGN ] 02 64 01 00 01

Sun 09/02/2012 09:17:58 AM : ---- All Remaining Device Added ----

Sun 09/02/2012 09:17:58 AM : [All ] Writing 0 bytes to devices

 

Any ideas?

Link to comment

The RF SwitchLinc did not complete the exchange with the PLM. See the message in red from a device add of an I2CS device. This message is missing in the posted trace. Suggest moving an Access Point closer to the RF SwitchLinc. Be sure not to lose phase coupling in the process.

 

The PLM can also be power cycled before doing the next device add.

 

Tue 06/05/2012 08:12:17 PM : ---- Initializing the linked devices ----

 

Tue 06/05/2012 08:12:17 PM : ---- All Linked Devices are now initialized ----

 

Tue 06/05/2012 08:12:17 PM : ---- Add remaining devices ----

 

Tue 06/05/2012 08:12:17 PM : [iNST-TX-I1 ] 02 62 1C FD D5 0F 0D 00

 

Tue 06/05/2012 08:12:17 PM : [iNST-ACK ] 02 62 1C.FD.D5 0F 0D 00 06 (00)

 

Tue 06/05/2012 08:12:17 PM : [iNST-SRX ] 02 50 1C.FD.D5 19.70.06 AB 0D FF (FF)

 

Tue 06/05/2012 08:12:17 PM : [standard-Direct Nack][1C.FD.D5-->ISY/PLM Group=0] Max Hops=3, Hops Left=2

 

Tue 06/05/2012 08:12:17 PM : [iNST-TX-I2CS] 02 62 1C FD D5 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6

 

Tue 06/05/2012 08:12:17 PM : [iNST-ACK ] 02 62 1C.FD.D5 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6 06 LNK-ON (01)

 

Tue 06/05/2012 08:12:17 PM : [iNST-SRX ] 02 50 1C.FD.D5 19.70.06 2B 09 01 LNK-ON (01)

 

Tue 06/05/2012 08:12:17 PM : [standard-Direct Ack][1C.FD.D5-->ISY/PLM Group=0] Max Hops=3, Hops Left=2

 

Tue 06/05/2012 08:12:17 PM : [LNK-BGN ] 02 64 01 00 06

 

Tue 06/05/2012 08:12:17 PM : [LNK-STAT ] 02 53 M(01) gid=00 1C.FD.D5 0700 41

Link to comment

Thanks. Power cycled the PLM and put 4 dual band lamplincs around the switchlinc and tried again. Same story. Here is the output from event viewer. Each time I do this I have to power cycle the ISY and PLM as the ISY is no longer able to communicate with the PLM. If I try to turn off/on a light it doesn't go through anymore, but after power cycling it works again. Feels like the PLM is not sending/receiving the final command and freezes somewhere in the process.

 

Sun 09/02/2012 06:27:25 PM : ---- Initializing the linked devices ----

Sun 09/02/2012 06:27:25 PM : ---- All Linked Devices are now initialized ----

Sun 09/02/2012 06:27:25 PM : ---- Add remaining devices ----

Sun 09/02/2012 06:27:25 PM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 0D 00

Sun 09/02/2012 06:27:25 PM : [iNST-ACK ] 02 62 1E.62.A3 0F 0D 00 06 (00)

Sun 09/02/2012 06:27:25 PM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD A7 0D FF (FF)

Sun 09/02/2012 06:27:25 PM : [standard-Direct Nack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Sun 09/02/2012 06:27:25 PM : [iNST-TX-I2CS] 02 62 1E 62 A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6

Sun 09/02/2012 06:27:25 PM : [iNST-ACK ] 02 62 1E.62.A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6 06 LNK-ON (01)

Sun 09/02/2012 06:27:26 PM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 09 01 LNK-ON (01)

Sun 09/02/2012 06:27:26 PM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Sun 09/02/2012 06:27:26 PM : [LNK-BGN ] 02 64 01 00 03

Sun 09/02/2012 06:27:26 PM : ---- All Remaining Device Added ----

Sun 09/02/2012 06:27:26 PM : [All ] Writing 0 bytes to devices

Sun 09/02/2012 06:27:43 PM : [iNST-TX-I1 ] 02 62 00 00 29 CF 13 00

 

LeeG, nothing in the error log except a lot of the following:

Sun 2012/09/02 06:30:07 PM System -170001 [HTTP] ***.***.***.***:57378->80

Link to comment

I am seeing an unusual response to the 02 64 command. In one case there is a 03 response, in another a 01 response. Note the 06 response in my trace entry which is the standard response from a PLM when the serial command is accepted. Is there any possibility the PLM is full, not being able to create a new link. The command sequence being executed is trying to establish a link between the new device and the ISY PLM. This is a requirement of I2CS devices before the PLM can create additional links or control/configure the new device.

 

Sun 09/02/2012 06:27:26 PM : [LNK-BGN ] 02 64 01 00 03

Sun 09/02/2012 09:17:58 AM : [LNK-BGN ] 02 64 01 00 01

 

Tue 06/05/2012 08:12:17 PM : [LNK-BGN ] 02 64 01 00 06

 

A Show PLM Links Table and Count will produce a count of the links in the PLM. The issue with this is any inbound Insteon message from a device will create false high/low record counts. It is necessary to run multiple Show PLM Links Table and Count to see if a consistent count be get obtained.

Link to comment

Hi LeeG, thanks so very much for all your help and precise instructions.

 

Hi Braq, as LeeG mentioned, the main issue is that the device is not responding to Link Begin. All I2CS devices require this method to link. The reason you can no longer talk to other devices is because the PLM is in Linking mode and will not get out of this mode for about 4 minutes or till ISY hears a Link Response.

 

Quick questions:

1. Do you have any Baby Monitors around?

2. Do you have any thermostats around?

 

With kind regards,

Michel

Link to comment

Michel, LeeG, I got it to work!

 

I do indeed have a baby monitor (angelcare 927MHz) and a thermostat (Z-Wave 900 MHz, but far away), and I also recently installed a few Aeon lab multisensors (Z-Wave 900 MHz) which I assume are all causing interference. I also have an AT&T microcell (850 and 1900 MHz) in the same closet as my PLM. I turned all of them off, but it didn't help. I then took a closer look and at my lamplincs and by chance it seems they were all on the same phase. So I moved one around (using the method described in http://www.insteon.net/pdf/2443.pdf) and that did it. I was able to successfully add the 2 new switchlincs, and now it all works even with the other RF equipment on.

 

Thank you both so much for your help! These 2 wire switchlincs are a life saver in our old house.

 

Braq

 

Mon 09/03/2012 10:00:57 AM : ---- Initializing the linked devices ----

Mon 09/03/2012 10:00:57 AM : ---- All Linked Devices are now initialized ----

Mon 09/03/2012 10:00:57 AM : ---- Add remaining devices ----

Mon 09/03/2012 10:00:57 AM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 0D 00

Mon 09/03/2012 10:00:57 AM : [iNST-ACK ] 02 62 1E.62.A3 0F 0D 00 06 (00)

Mon 09/03/2012 10:00:57 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD A7 0D FF (FF)

Mon 09/03/2012 10:00:57 AM : [standard-Direct Nack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:00:57 AM : [iNST-TX-I2CS] 02 62 1E 62 A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6

Mon 09/03/2012 10:00:57 AM : [iNST-ACK ] 02 62 1E.62.A3 1F 09 01 00 00 00 00 00 00 00 00 00 00 00 00 00 F6 06 LNK-ON (01)

Mon 09/03/2012 10:00:58 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 09 01 LNK-ON (01)

Mon 09/03/2012 10:00:58 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:00:58 AM : [LNK-BGN ] 02 64 01 00 06

Mon 09/03/2012 10:00:59 AM : [LNK-STAT ] 02 53 M(01) gid=00 1E.62.A3 0124 41

Mon 09/03/2012 10:00:59 AM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 0D 00

Mon 09/03/2012 10:00:59 AM : [LNK-END ] 02 65 06

Mon 09/03/2012 10:00:59 AM : [standard Msg. Handler] Unexpected Ack imCmd=65 cmd1= 0xA3

Mon 09/03/2012 10:00:59 AM : [iNST-ACK ] 02 62 1E.62.A3 0F 0D 00 06 (00)

Mon 09/03/2012 10:01:00 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 0D 02 (02)

Mon 09/03/2012 10:01:00 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:01:04 AM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 0D 00

Mon 09/03/2012 10:01:04 AM : [iNST-ACK ] 02 62 1E.62.A3 0F 0D 00 06 (00)

Mon 09/03/2012 10:01:04 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 0D 02 (02)

Mon 09/03/2012 10:01:04 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:01:04 AM : [1E 62 A3 0 ] Calibrating engine version

Mon 09/03/2012 10:01:04 AM : [ 1E 62 A3 1] Adding device to ISY t=01.24.0000

Mon 09/03/2012 10:01:04 AM : [1E 62 A3 1 ] Start : Adding device to ISY

Mon 09/03/2012 10:01:04 AM : [1E 62 A3 1 ] Finish : Adding device to ISY was Successful

Mon 09/03/2012 10:01:04 AM : [1E 62 A3 1 ] Link 0 : 0FF8 [A2001482DDFF1F01] Saving [A2001482DDFF1F01]

Mon 09/03/2012 10:01:04 AM : [1E 62 A3 1 ] Link 1 : 0FF0 [E2011482DDFF1F01] Saving [E2011482DDFF1F01]

Mon 09/03/2012 10:01:04 AM : [iNST-TX-I2CS] 02 62 1E 62 A3 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1

Mon 09/03/2012 10:01:04 AM : [iNST-ACK ] 02 62 1E.62.A3 1F 2E 00 01 00 00 00 00 00 00 00 00 00 00 00 00 D1 06 (00)

Mon 09/03/2012 10:01:04 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 2E 00 (00)

Mon 09/03/2012 10:01:04 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:01:05 AM : [iNST-ERX ] 02 51 1E 62 A3 14 82 DD 11 2E 00 01 01 00 00 20 20 1C FE 3F 00 01 00 00 00

Mon 09/03/2012 10:01:05 AM : [Extended-Direct][1E.62.A3-->ISY/PLM Group=0] Max Hops=1, Hops Left=0

Mon 09/03/2012 10:01:05 AM : [ 1E 62 A3 1] OL 255

Mon 09/03/2012 10:01:05 AM : [ 1E 62 A3 1] RR 28

Mon 09/03/2012 10:01:05 AM : [iNST-TX-I1 ] 02 62 1E 62 A3 0F 19 00

Mon 09/03/2012 10:01:05 AM : [iNST-ACK ] 02 62 1E.62.A3 0F 19 00 06 LTSREQ (LIGHT)

Mon 09/03/2012 10:01:05 AM : [iNST-SRX ] 02 50 1E.62.A3 14.82.DD 27 01 FE (FE)

Mon 09/03/2012 10:01:05 AM : [standard-Direct Ack][1E.62.A3-->ISY/PLM Group=0] Max Hops=3, Hops Left=1

Mon 09/03/2012 10:01:05 AM : [ 1E 62 A3 1] ST 255

Mon 09/03/2012 10:01:05 AM : [ 1E 62 A3 1] OL 255

Mon 09/03/2012 10:01:05 AM : [ 1E 62 A3 1] RR 28

Mon 09/03/2012 10:01:06 AM : [1E 62 A3 1 ] Device added to ISY

Mon 09/03/2012 10:01:07 AM : ---- All Remaining Device Added ----

Link to comment

Is the microcells power supply on the same circuit as the PLM?

Some wall wart switching supplies can be a power line signal problem.

 

I don't know if the ZWave and Insteon frequencies are too close to step on each other.

Is the Aeon Labs unit always sending sensor data?

If there is no ZWave transmissions when the Insteon Signals where being sent. Then I would think it could not be a problem.

Link to comment

I tried adding a third switchlinc (less than 6 feet away from the other one and on the same circuit), but have the same problem again. It's replying back in the beginning, but not continuing after "link begin". I turned everything off again, but no luck. I will try again tomorrow morning, maybe there is a noisemaker on the line somewhere that was off by chance this morning when I was able to add the other ones.

 

Brian, yes, the microcell's power supply is on the same circuit as the PLM. Don't have another filterlinc lying around unfortunately. With the 2 switchlincs I added this morning I've had no problem so doesn't look like the zwave sensors are interfering. I take out their batteries / remove power when I try to add the switchlincs.

Link to comment