@schda12, I read through a couple of your earlier posts regarding your ISY994 install and migration to the Eisy. Summarizing: Your ISY994/PLM install was in a bad location. So much so, that you had to relocate the PLM to write configuration changes to Insteon devices. You migrated to the Eisy, but are having intermittent issues communicating with devices. You are using the same PLM? In the same location? Normally intermittent communication failures do NOT indicate a PLM failure. The intermittent nature is due to problem devices turning on/off. I am also trying to determine if you are having new problems due to a partial migration. Your 2477D that did not respond with the PLM plugged in next to it sounds like a device that was not migrated properly. Is this device intermittent or 100% non-responsive. If 100% non-responsive to the PLM, it's likely a configuration problem. You could try restoring the device. You mentioned your Aprilaire steam generator - I wouldn't normally think of this as a problem item, but it does pull significant power. Try turning it off to see if you notice a difference in communication. Your heat pump is likely a 220V device that is run off a dedicated circuit breaker in your panel - i.e. not on the same circuit. Not sure if you can correlate the heat pump on/off cycles with communication problems. Not sure I would recommend powering off the heat pump (some of the HVAC systems get mad if they can't communicate with the components). You could try changing the setpoint so the system doesn't run for an extended period - then try running communication tests. When you are running tests, performing queries are the most reliable communication method. Said differently, if a query fails you are having severe communication problems (or you have a device configuration issue). The PLM will retry communication 5x and the Eisy will retry 3x. Your description below was the Eisy re-trying the query 3x with no response. You can query individual devices, scenes, or your entire installation by right clicking the Admin Console device tree and selecting "query". By performing the query on "My Lighting" you will get every device known to the Eisy. This can be helpful if you are trying to localize a problem. The following is a event viewer query (level 3) of my 1st floor scene devices. The "[Std-Direct Ack]" is a summary of the device communication back to the PLM. "Hops Left" of 2 or 3 is good. Lower Hops remaining is worse. Just to make things confusing, I managed to capture some system Echo's (Device 0C.C2.32 and 58.B0.74). These devices show 2 responses: one with 3 hops remaining and one with 0 hops. I refer to these as echo's - probably from the opposite electrical phase. The second query is showing failures to 3 ISY retries (device is not installed). Mon 04/01/2024 07:54:16 AM : [INST-TX-I1 ] 02 62 1A 5D C7 0F 19 00 Mon 04/01/2024 07:54:16 AM : [INST-ACK ] 02 62 1A.5D.C7 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:16 AM : [INST-SRX ] 02 50 1A.5D.C7 53.BC.3A 2B 00 F7 (F7) Mon 04/01/2024 07:54:16 AM : [Std-Direct Ack] 1A.5D.C7-->ISY/PLM Group=0, Max Hops=3, Hops Left=2 Mon 04/01/2024 07:54:16 AM : [INST-TX-I1 ] 02 62 0C C2 32 0F 19 00 Mon 04/01/2024 07:54:16 AM : [INST-ACK ] 02 62 0C.C2.32 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:17 AM : [INST-SRX ] 02 50 0C.C2.32 53.BC.3A 2F 31 FF (FF) Mon 04/01/2024 07:54:17 AM : [Std-Direct Ack] 0C.C2.32-->ISY/PLM Group=0, Max Hops=3, Hops Left=3 Mon 04/01/2024 07:54:17 AM : [INST-TX-I1 ] 02 62 58 B0 74 0F 19 00 Mon 04/01/2024 07:54:17 AM : [INST-SRX ] 02 50 0C.C2.32 53.BC.3A 23 31 FF (FF) Mon 04/01/2024 07:54:17 AM : [Std-Direct Ack] 0C.C2.32-->ISY/PLM Group=0, Max Hops=3, Hops Left=0 Mon 04/01/2024 07:54:17 AM : [INST-ACK ] 02 62 58.B0.74 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:17 AM : [INST-SRX ] 02 50 58.B0.74 53.BC.3A 2F 00 00 (00) Mon 04/01/2024 07:54:17 AM : [Std-Direct Ack] 58.B0.74-->ISY/PLM Group=0, Max Hops=3, Hops Left=3 Mon 04/01/2024 07:54:17 AM : [INST-TX-I1 ] 02 62 16 CD 80 0F 19 00 Mon 04/01/2024 07:54:17 AM : [INST-ACK ] 02 62 16.CD.80 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:17 AM : [INST-SRX ] 02 50 58.B0.74 53.BC.3A 23 00 00 (00) Mon 04/01/2024 07:54:17 AM : [Std-Direct Ack] 58.B0.74-->ISY/PLM Group=0, Max Hops=3, Hops Left=0 Mon 04/01/2024 07:54:18 AM : [INST-SRX ] 02 50 16.CD.80 53.BC.3A 2B 00 00 (00) Mon 04/01/2024 07:54:18 AM : [Std-Direct Ack] 16.CD.80-->ISY/PLM Group=0, Max Hops=3, Hops Left=2 Mon 04/01/2024 07:54:18 AM : [INST-TX-I1 ] 02 62 41 29 3D 0F 19 00 Mon 04/01/2024 07:54:18 AM : [INST-ACK ] 02 62 41.29.3D 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:18 AM : [INST-SRX ] 02 50 41.29.3D 53.BC.3A 2F 00 00 (00) Mon 04/01/2024 07:54:18 AM : [Std-Direct Ack] 41.29.3D-->ISY/PLM Group=0, Max Hops=3, Hops Left=3 Mon 04/01/2024 07:54:18 AM : [INST-TX-I1 ] 02 62 05 4B 4B 0F 19 00 Mon 04/01/2024 07:54:18 AM : [INST-ACK ] 02 62 05.4B.4B 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:19 AM : [INST-SRX ] 02 50 05.4B.4B 53.BC.3A 2F 24 00 (00) Mon 04/01/2024 07:54:19 AM : [Std-Direct Ack] 05.4B.4B-->ISY/PLM Group=0, Max Hops=3, Hops Left=3 Mon 04/01/2024 07:54:19 AM : [INST-TX-I1 ] 02 62 58 CB 74 0F 19 00 Mon 04/01/2024 07:54:19 AM : [INST-ACK ] 02 62 58.CB.74 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 07:54:19 AM : [INST-SRX ] 02 50 58.CB.74 53.BC.3A 2F 00 00 (00) Mon 04/01/2024 07:54:19 AM : [Std-Direct Ack] 58.CB.74-->ISY/PLM Group=0, Max Hops=3, Hops Left=3 Device no-response to 3 ISY retries Mon 04/01/2024 08:14:16 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 04/01/2024 08:14:16 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 08:14:25 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 04/01/2024 08:14:25 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Mon 04/01/2024 08:14:34 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 04/01/2024 08:14:34 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Give us a bit more information on your system and play around a bit to try localizing things. Intermittent problems are difficult, but this should be solvable.
-
I have not seen anything indicating that newer PLM's are more sensitive to noise or lower power. Could you point me to these reference? Thank you
-
@piconut, I was actually referring to the Log File (not the error log). When your program runs, and you use a Device Direct command to turn on a device (not s scene), an error should be logged if the device does not respond (Error 0 as shown above). @woodchip, I'm not much help with the error logs. I just regurgitate what others have posted without any real understanding of the errors: https://forum.universal-devices.com/topic/13665-understanding-error-logs/ https://wiki.universal-devices.com/index.php?title=ISY-99i/ISY-26_INSTEON:Errors_And_Error_Messages
-
So, the good news is that with 95 dual band devices you should have no worries about phase coupling... The ISY994 PRO is capable of handling 1000 nodes and 1000 programs. Since you are not using Scenes, you should be comfortably below the node limit. The PLM is capable of handling 1000 links. You should be below that limit as well. Even if you were above the limit (yes it's possible to be over the limit) the symptoms would be different. That's all the good news. You'll need your Sherlock Holmes cap to watch for patterns and experiment with possible problem devices. Since your programs turn devices on/off directly (not in scenes), an error should be generated when a device doesn't respond. Errors should also be generated if devices don't respond during the 3 am query. These will be in the Log file "Error 0". You may be able to use these errors to localize your communication problem (particular circuit or area in your home). Other than the log file, the best that I can offer at the moment is unplugging possible offenders near the PLM or problem devices to see if things improve. Difficult when things are intermittent. Generated the following error log by issuing an ON command to a device that I had unplugged
-
It sounds like you are having intermittent communication issues with a number of devices. The fact that they happen individually and "heal" would seem to indicate that the problem is not the PLM. Not sure what type devices we are dealing with here and what the makeup of your installation looks like - If you have an older installation with primarily powerline devices (NOT dual band) it's possible that you lost a phase coupling device. This would cause a reduced signal level on the phase opposite of your PLM. If your devices are newer dual band then your phases are likely well coupled. Multiple unit issues are normally due to a degraded PLM or SIGNAL ABSORBER near the PLM. Always possible that you have a noise source/signal absorber that is only active at certain times of the day. Try to look for patterns in the communication problems. If you think you are having issues communicating with a device, run a query on it. The ISY will try 3 times to communicate and then tag the device as "failed to communicate with.." Intermittent problems are the worst. Very difficult to track down and be sure that you've found the culprit. Give us a bit more detail and what your system looks like and what devices you are having problems with (i.e. 2477 dimmer vs 2476 dimmer) Edit: Realized that I did not answer your question about replacing the PLM. @Techman provided the PLM replacement procedure above... The only "Risk" in replacing your PLM is the possibility that there is something else in your system causing the problems. If that is the case you may have difficulty in writing the new PLM information to your devices (1011 tags). Aside from that, you will need to wake your battery devices to update them with the new PLM links. If you have motion sensors in difficult to reach areas, UD provided a method to program these when motion is sensed. I typically disable these programs when not in use, otherwise they will trigger every time motion is sense. Motion Sensor Update Program: BSMT Sensor Program - [ID 004A][Parent 0066][Not Enabled] If 'Motion/RF / BSMT-Sensor' is switched On Or 'Motion/RF / BSMT-Sensor' is switched Off Then Set 'Motion/RF / BSMT-Sensor' Write Changes Else - No Actions - (To add one, press 'Action')
-
Device state as condition, but not trigger for program
IndyMike replied to beninsteon's topic in IoX Program Support
Similar to @Goose66's approach - you can create a "conditional folder" use the "status" of your Ecobee thermostat to enable it. Place your trigger program in the conditional folder. This will give you a visual of when the folder is enabled (Green - Enabled, Red - Disabled). Running a disabled program will absolutely work, but I'm old and often forget that some programs SHOULD be disabled (it hurts my brain). -
@gregkinney, Glad to hear you tracked the offender down. For the other forum readers, would you mind providing a few more details on how you located/isolate the PC as the problem? Intermittent problems are normally the worst. It can be extremely difficult to isolate the problem to a circuit or device.
-
Hi @piconut, Paul and Techman both have good points. I am however curious about two things: You stated that your devices are controlled by programs - not in scenes. The fact that the ISY "thinks" that your devices are at one lighting level when they are actually at another make it sound like you are using scenes. Could you post your programs? Normally the ISY polls all devices @3:00am. If your PLM is failing, this query will fail miserably. You will be greeted by a host of "cannot communicate with...device" when you log in. If you are not seeing these communication failures and the (!) on your devices, I would say that your PLM has not given up (yet). Have you seen signs that the ISY has tagged devices as being offline?
-
Since you are having very isolated problems (3 devices out of 100's) it is likely that the noise/signal absorber is on the same circuit. If you can determine which circuit(s) are having issues, begin removing loads (chargers, UPS, TV's) until the problem cleans. If you are looking at circuits in your breaker panel - remember that the phases are the same horizontal and alternate as you go down the panel vertically. Typical Panel Layout
-
1500VA is a large UPS. Unless you are willing to build your own, the only thing that I know of that is currently available is the XTB-F15+ from Jeff Volp. The filter is advertised for X10, but will work for Insteon as well. https://jvde.us/xtb-f10/ Insteon is very good at bridging the phases - assuming you have dual band modules. X10, on the other hand, will have great difficulties in crossing phases without a dedicated coupler or 220V resistive path (oven, dryer). Again, not sure if the UPS is absorbing Insteon signals to the point where they are at the noise floor, or generating noise in the Insteon band (or both). It's certainly worth testing by moving one of the two to another circuit.
-
The UPS is a relevant piece of information. Most of them have a EMI filter that will absorb Insteon signals. Other units have been found to be noise generators. Either way it should probably be installed on a filterlinc. Check the current draw of the UPS before installing a filter. If you don't want to move your PLM to the garage circuit, you could move your UPS and equipment to that circuit as a test.
-
As Paul indicated, this doesn't necessarily have to be an Insteon device producing the traffic. I had an old (10+ years) Homelink receiver in my garage that was capable of Transmitting X10 - It went nuts one day and began spamming the powerline on housecode P. It happens. You could try air gapping (not resetting) your Insteon devices to see if the communication stops. Unfortunately there are two that are difficult to access. I still think your best approach is to turn off breakers one at a time until the noise goes away. If you cycle through all the breakers except the circuit the PLM is on and still have the noise - move the PLM to another circuit and check the breaker on the former.
-
I might agree that there is a Low risk in doing a device restore. Unfortunately it WILL NOT eliminate X10 address programming and it is likely to fail with the X10 traffic present on your system. AFAIK, the ISY cannot "un-program" an X10 address. There are devices that can (Houselinc) but you don't have them. The "easy" way to eliminate a X10 address in an Insteon device would be to perform a factory reset (eliminate the x10 address) and then restore it. I would not factory reset anything while the X10 traffic is present. As I said above, the restore is likely to fail (just as your queries are failing). You need to locate the source of the traffic and eliminate it. Since this just started happening recently, chances are that you have a device that is dying or just in an unhappy state. Cycling power may correct things. I think the best approach is to shut off breakers until the offender goes silent. As far as why Insteon devices would have X10 addresses - there was a period of time where new devices were received with X10 address from the factory. Not sure why, test escapes or whatever. It became so prevalent that "best practice" was to factory reset every device prior to installation. This was probably many years ago (seems like yesterday), not sure if it applies to any of your devices. Used devices could have had X10 addresses programmed by their previous owners. The addresses would NOT be eliminated by linking to the Eisy. They are in a section of memory that is separate from the device link table.
-
Wow, that's a lot of X10 traffic. That alone can bring your system to it's knees. It may also explain why wireless devices function while powerline is intermittent. The Status request isn't a normal X10 device - that's a controller function. If you don't have any X10 controllers installed (garage door, alarm panel, etc) you may have an Insteon device that's failing (although I've never seen one put out Status requests). Unless you can come up with a list of likely suspects, the normal way of isolating is to start turning off breakers until the X10 transmission stops. One you find the suspect circuit inspect/remove devices until you find the culprit. It's time consuming, but now all that hard. Best to do when family members are not around to avoid plummeting approval factors.
-
Paul's suggestion of checking the PLM links is a good one. It will give you a general idea of the health of your PLM. In order to get an accurate count of the PLM links, you need to keep the system quiet (disable programs, no powerline or RF activity). That's not necessary here as you are simply trying to asses if the PLM has totally dumped it's link table (10 link records = bad, over 100 link records probably ok). The 3 Inst-TX messages that you see in the event viewer sound like the Eisy is sending messages and getting no-response (timeout) and retrying the transmission. For each TX you should see an INST-ACK (plm Acknowledging) as follows. This is a query of a device that I removed from my system: Mon 03/04/2024 08:52:10 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 03/04/2024 08:52:10 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Mon 03/04/2024 08:52:19 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 03/04/2024 08:52:19 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Mon 03/04/2024 08:52:28 AM : [INST-TX-I1 ] 02 62 54 A1 F5 0F 19 00 Mon 03/04/2024 08:52:28 AM : [INST-ACK ] 02 62 54.A1.F5 0F 19 00 06 LTSREQ (LIGHT) Mon 03/04/2024 08:52:32 AM : [D2D EVENT ] Event [54 A1 F5 1] [ERR] [1] uom=0 prec=-1 Mon 03/04/2024 08:52:32 AM : [ 54 A1 F5 1] ERR 1 Please post an example of your event viewer query (level 3). If you are not seeing the ACK's, try power cycling the PLM. Also post examples of the periodic X10 communication. I never like seeing this in a system with no X10 devices. At best, it slows down insteon communication. At worst, it corrupts the powerline. Since you are seeing widespread communication issues, the most likely culprit is the PLM - or at least something near it. You could try moving the PLM, or using an extension cord to plug it in somewhere else.
-
If your switch is the controller of a Scene - the flashing red is indicating that it can't communicate with one (or more) of the scene members. If your switch is NOT a scene controller - the flashing red indicates that it can't communicate with the PLM. If you were to say "isn't the dual band Insteon feature supposed to eliminate this?", you would be absolutely correct. Unfortunately, nothing is perfect. There are situations where noise/signal absorption will prevent a device from hearing both powerline/rf. Looking into the HdHomeRun and Garage LED's are both solid ideas as you know that these have changed. Don't discount the possibility that you have a device that's on it's last legs (failing EMI capacitor, failing triac, etc) that is causing this (#2 on the list to check). If all else fails you'll need to identify which circuits (breaker panel) are being affected and what devices are installed - the old process of elimination. Best of luck - let us know how your experiments go.
-
I'm sorry, but the above statement is simply incorrect. In a "perfect home installation" with a PLM and 100 devices - activating the "Beacon Test" on the PLM would cause 50 devices to flash green (opposite phase) and 50 devices to flash red (same phase). Red flashing does not imply improper bridging.
-
@Techman - the document you linked is for the range extenders and it is dealing with "bridging" the phases. In that context it's rather misleading. A Red flashing LED indicates the receiving device is on the SAME PHASE as the transmitter. A Green flashing LED indicates the receiving device is on the OPPOSITE PHASE. It's a bit more clear in the On/Off Module Manual: Phase Bridge Detect Beacon/RF Range Test On/Off Outdoor Module automatically bridges the electrical phases in your home (via communications with other dual-band devices on the “other phase”). This is only important in 2-phase homes with powerline-only INSTEON products or buildings with both 2- and 3- phase circuits. The phase bridge detect beacon can also be used as an RF range test to see if your devices are within communication range. You will need at least one other INSTEON dual-band device installed. 1) Quickly tap Set button four times On/Off Outdoor Module will start beeping once per second LED will turn solid green 2) Check the LED behavior of other dual-band devices Phase Bridge Detect Beacon • If the other dual-band device is blinking green, it is on the other phase: Device provides a phase bridge to Micro module • If the other dual-band device is blinking red, it is on the same phase: Device does not provide a phase bridge to Micro module Relocate if necessary (and practical) • If the other dual-band device is not blinking: Device is not within RF range of Micro module so it does not provide a phase bridge Relocate if necessary (and practical) or add an additional dual-band device RF Range Test • RF range test: if LED is blinking: Device is within RF communication range • RF range test: if LED is not blinking: Device is not within RF communication range Relocate if necessary (and practical) or add an additional dual-band device 3) Tap Set button On/Off Outdoor Module will stop beeping Other device LEDs will stop blinking https://cache.insteon.com/documentation/2634-222-en.pdf
-
The AirTV and HDHomeRun are different devices with different power supplies. I have used the HDHomeRun and it wasn't problematic for me. The may have changed the power supply. 110V Led shop lights also use power supplies. They would be my main suspect. Since your problem appears intermittent, look for chargers and things that move around or are activated at particular times of day. This doesn't necessarily have to be a new device. I've had multiple solar sensors die on my post lamp. When they nosing over they tend to flood the powerline with noise. I've stopped using them and switched to a bulb with a solar sensor. The 4 tap test in the PLM is still a good troublshooting tool. Tap the button 4 times rapidly and all dual band devices in range will flash red or green. If a device does not flash, it's either old or it can't hear the PLM. Try this with your problem devices when they are working properly to see how it functions. When things stop operating correctly, try it again. The start looking for items on the circuit that could be absorbing the signal or generating noise.
-
If you have "hundreds" of devices that function and 3 the do not, it's probably not the PLM. Try moving one of your on/off modules to the same outlet as the PLM. Assuming that works, start looking for signal absorbers or coupling problems on your problematic circuit. You can also try running a 4-tap test on your PLM. If your devices support the test, and can hear the plm, they will flash green or red.
-
Glad to hear that you are not using the IOLinc to operate your furnace. Hopefully, your wall heater has over temperature protection. Please do consider the consequences of the heater being left on due to a communication error, or activating without the EISY knowing about it (All-on phenomena). This can be mitigated to a degree by polling the IOlinc regularly to test for an uncommanded on condition.
-
Hello @Tom Carmody, I looked up the installation instructions for your GC-TBZ48. The thermostat is completely capable of controlling the Furnace heat/cool cycles through it's hardwired interface. Since you are trying to control the appliance (Heat/Cool) using Insteon, I am assuming that you are using the GC-TBZ48 in battery mode with no hardwired interface to the appliance. PLEASE DO NOT DO THIS - There are many failure modes that can erroneously turn your appliance off or (Worse) turn it on and leave it on. It sounds like you are using a Insteon 2450 I/O Linc to activate the appliance. The 2450 is a powerline only device (not dual band) that is susceptible to erroneous turn on/off (search spontaneous All-On). There is no automation device that I would trust for this application. Please run the wiring, and install the thermostat as it was designed to be used. I'll apologize in advance if I'm incorrect in my assumptions above. Please post back and clarify if that is the case. IM
-
FWIW, I moved a couple of Aqara zigbee sensors to my basement refrigerator/freezer. The are working well. Top two plots are the Zigbee temp/humidity/pressure sensors. Inexpensive and have good battery life. The bottom plot is a Zooz energy monitoring plug. The spike around 6:00 pm is due to the defrost cycle. Note that the defrost may make it difficult to set alarms based on temperature.
-
That should eliminate your home wiring and coupling. What we do not know is whether a V2.7 PLM can receive X10, OR whether the current EISY can display X10 in the event viewer. I can't help with either. We need other forum members to help here... I anyone has a V2.7 PLM that receives X10, OR a EISY - please reply to this thread.
-
@glacier991, Brian's point about the capacitor is a good one - caps do go bad. Unfortunately, you should not need the Signalinc with the XTB-II. The XTB is a much better coupler than any passive device will ever be. Let's focus on the X10 signals in the event viewer - you mentioned that you have a Maxi-Contoller. Please verify that it works (activate a lamp with it), then plug it into the same outlet as the PLM and activate it. 1) If you still don't see X10 events in the event viewer we'll call this a PLM/Eisy issue. 2) If you do see events we'll need to troubleshoot your wiring/coupling configuration.