Everything posted by ELA
Neighbor got solar, I got problems
Hello Dekall, Since you share the same transformer secondary... It certainly is a possibility that noise from your neighbors is making its way into your homes electrical network. As others have pointed out this is similar to the Powerwall links provided. The solution for that was a large EMI filter. If you were to do that you would need a very large and expensive filter for a 200+ amp? service. Have you tried asking your power company if separating your service from your neighbors is a possibility? (adding a separate transformer). Probably not likely ... but worth trying.? These types of solar installs, that create so much noise, really should be addressed at the source. If you read the link provided it is clear that noise mitigation should be installed at the noise producer. They tell installers to use ferrites which are somewhat of a joke for lower frequency offenders. EMI filters should be a standard part of those installs. Best of luck to you.
Issues after installing Tesla powerwall 3
Hello cksedg, Have your electricians or Tesla reps used a Power Quality meter or logging oscilloscope to monitor your power over some time period? This should be done both with the PW3 connected and also when the PW3 is isolated from your power. I would be concerned if you have lost that many electronics since the install. It appears the PW3 needs to have a proper EMI filter installed to remove the interference frequencies that are affecting Insteon. The proper filter is not ferrites. It is a large EMI filter that incorporates larger inductors.
Help w flickering floods on a 3-way Insteon circuit
Hello windrockwater, The fixture in the link is not dimmable by 120AC phase fired dimmer. It has a separate 0-10Vdc dimming input. You need an Insteon relay for that one if not intending to dim.
New eisy Model, home r2, 994 upgrade Path offer
This is where I am at as well. However I would like to be able to purchase newer Insteon I3 devices as replacements when device failures occur. I currently have one older switchlinc 2476S with the failing pushbutton issue I want to replace. I would prefer the I3 device but will need to stick with the 2477S due to my ISY994. Seems a shame not to invest in newer Insteon components when replacements are required.
Lights switch on at random times
Thank you for sharing your work kclenden, This is very interesting. I have yet to upgrade to an eISY and have never seen such a thing with my ISY994. The "link Info" messages are new to me, should they be of concern ? Does not appear like any of the older All/ON , ALL/OFF issues from my experience. It might be interesting to send the invalid message "02 62 00.11.00 CF 13 00" (A group broadcast to group zero to turn off) directly to the PLM to see how it responds. If you were to open a ticket with UDI ... I would be curious what they think?
Hello Kclended, Could you please post an example of your capture where you see the corrupted echo? Out of curiosity, how log is your cable from eISY to the PLM?
Insteon Trade Up Promotion 3/2025
I have had a few older icon devices go bad of late. Just bought a replacement last week. It was not worth it to send back the old device as you pointed out return shipping nearly wipes out any gain. If they had records of previous purchases could they not offer decent credits for new purchases when you have spent over $2k on product over the years?
The filter discussion was primarily for the OP -Richtimpa. He stated the communications issue was important to him. Flickering or strobing could possibly be improved with the appropriate filter at the Power Wall. For Flickering - As a first attempt I would try the Jasco LED bypass that I referred to in my first page post. Have you tried those? They are mounted directly at each Dimmer or its load. They can be a big help in some cases but not all. Unfortunately they are showing out of stock presently. They are most helpful when the dimmer is lightly loaded with an LED load. A dimmer is susceptible to having its triac triggering upset when there is "noise" or " a "zero-cross waveform distortion" occurring with a minimal LED load. The Jasco device turns on only near the zero-cross point in the waveform to provide a more stable load for the dimmer triggering circuit, - at a time when the LED load is not yet conducting much current.
EMI filter vs Insteon: While in general, adding an EMI filter at the service entrance may be good for protecting electronics, it may be a negative for Insteon communications. Often times Insteon users with communications issues complain about "Noise" when the real issue is often that a device is a "signal sucker". Often times it is not all that important to understand which of those two that the offending device is. Adding an Insteon Filterlinc can be the solution for either. The Filterlinc both filters Noise from the line side and can also "isolate" a signal sucker from the line. With a large current device like the Power Wall it is much more important to attempt to understand whether it is a noise issue, a signal sucker issue or both. From the descriptions written here thus far it does sound like it may be a little of both. It is important to be clear on the terms Surge Suppressor vs. EMI filter. There are lots of Surge Suppressor -only devices that can be added without affecting Insteon communications. However there are a lot of EMI filters, especially those with a simple capacitor only filter, that will degrade Insteon comms. If Insteon offered a Filterlinc with large enough current capability that could be a solution. Since they do not, finding a custom EMI filter that that both suppresses noise from the line, but also isolates the load side may be difficult to identify and expensive. The M2120 mentioned does not provide enough data as to what the EMI portion of it consists of. Many inexpensive EMI filters are simply a capacitor. The capacitor alone suppresses a wide range of frequencies, usually including the Insteon freq. That makes it a "signal sucker" to insteon. So adding an EMI filter at the service may actually degrade the Insteon performance unless it is one that also incorporates large inductors to isolate the load side from the capacitance. The Power Wall vs Insteon issue is much more difficult due to the high currents involved. An Insteon user can buy a filterlinc and install it as a fix without incurring a large expense. If it does not work they are not out all that much. A Power Wall size filter would be very expensive to purchase in "hopes" that it might help.
Ask the installer/Tesla rep. if the Powerwall 3 is "CE" marked? I took a quick look and it looked as if that is planned ? Or maybe what I saw was old data so I am curious. CE marking allows them to be sold in Europe and CE marking requires a much more stringent series of Electromagnetic Emissions testing. It may be that they will need to install the filter the installer mentioned in order to meet the CE standards. Ferrite cores are generally only effective at higher frequencies, those much greater than the Insteon 131Khz. To attenuate or isolate the emissions from a device in the Insteon range requires a larger inductance. Like the Line reactor(inductor) I mentioned in my earlier post. IndyMike posted an interesting link. It would be nice to have a plot of the emissions from the Powerwall 3 showing what the offending frequencies are. If the installer/Tesla rep could provide some emissions test data that might be helpful. Best of luck to you all.
Hello Richtimpa, I do not have a power wall but will try to offer some insights and/or questions you can ask the Tesla rep. 1) What type of lights are blinking more often? LED or Incandescent or both? Are the lights on Dimmers? From your description it sounds like it may be a combination of things. It is likely the Power Wall (PW.) has internal filtering (across the line capacitors) to reduce the noise level it puts onto the power line. We refer to those as signal suckers. A signal sucker can make the communications less reliable and result in the sluggish query you see. It would be somewhat difficult to find an Insteon filter large enough to "isolate" the PW signal sucker from your power line. A large "Line Reactor" or inductor-only filter could possibly help but identifying that would be difficult without Tesla's help. You may have had some other signal sucker issues in your home prior to the PW install so the PW may not even be at fault for that one. It also sounds like the Solar Install may be communicating with the PW over the power lines and sending signals near zero cross that cause the lights to Flicker. LED would tend to be the most sensitive to this. If the biggest issue were with LED then a different brand might be less sensitive. If on Dimmers then adding a device such as a "Jasco lighting bypass" might help. If at all possible to get input from a Tesla expert that would be best as these types of issues can be difficult to resolve without knowing more about the Solar-PW interconnections. Having an Oscilloscope to observe the power line requires a device to filter out the large 60hz waveform in order to observe low level power line noise interference. Best of luck to you.
Migrating from Insteon Hub to EISY
Hello and Welcome to this forum, Are you willing to become an Automation Hobbyist? If not then I would recommend you stay with the Hub. I may be incorrect but I would think that most here would consider their automation interest a hobby. It definitely demands a bit of your time if you want to explore all the powerful features that an ISY/EISY can add to your existing automation installation. If you are willing to spend the time required the people on this site are great at offering their time to help you along the way. As already mentioned it would be helpful if you described a bit about your existing installation. I would suspect that you had to spend some time getting your existing installation up and running reliably. You say you are having some issues now with the Hub. Are you sure it is the hub? Many experience issues with getting their communications between devices reliable. If existing issues are communications related, then changing to an EISY alone may not be all that is required. Having to resolve communications issues can make you a hobbyist :)
2476D paddle (hw) failures
Thanks for the Zooz information IndyMike, My wife had bought me a T-shirt years ago that says "I Void Warranties" I find my enthusiasm for changing/adding new automation types is waning. Will stay with the ISY994 as long as it allows me to.
Thanks Brian, With prices as they are now it might be tempting to replace the pushbutton switches but enforcing Dual Band coverage I felt was worth the cost. Unfortunately I have also just had an older In-Linelinc go bad. I have ordered a Micro Module for it as a replacement. $60 each fail is not been very kind to my retirement fund
I have a few older devices that have begun to fail recently. For the most part I had escaped the original devices "infamous Paddle Failures" but now some older devices are starting to fail in similar ways. I had just replaced two 2476D's that started requiring multiple taps to turn on. I did not mind that so much as the older units (R5.15) were not dual band and I liked the idea of improving my RF coverage with more dual band devices. Right after replacing the second unit, in a two gang box, another 2476D next to it failed in the ON position. I could not turn it off manually, but could turn it off via the ISY. The paddle felt very stiff when trying to push the bottom section ( off). I was hopeful that I could simply replace the Paddle section only with some color replacements I had. After changing out the paddle the 2476D worked once again. What was strange to me is that after removal of the original paddle, that paddle itself seemed to work just fine when no longer mounted. Being curious I cut open the paddle to see what was going on. As you can see in the picture one of the two "D-shaped rockers" had broken off and lodged itself in the bottom section of the switch. This prevented the paddle from being able to depress in the down position(off). Once the paddle was removed the D-shaped piece had migrated again and thus freed up the down position operation once again.
Motion Sensor II
Your last line may be where the confusion comes in. IndyMike and I are saying that the MSII can be retriggered once the ON time has timed out at 40 sec+ ... your last line is now attempting to retrigger the device BEFORE the On time times out and thus it will not send more ON commands. If you don't wait you are re-extending the ON time by restarting it. Anytime you wait long enough for the ON timer to expire then a retrigger can be created and once again an ON command is sent. When configured for ON-ONLY there is NO OFF time. You must wait for the ON time to expire before retriggering if you want additional On commands to be sent.
Motion Sensor II
One more data point for reference in hopes might help: MSII: R3.3 , date code 3418 , V.47 Initially set for both on and off with a 10sec timeout. Measured actual on time at 14sec ( when off command is sent) Re- Set for On only with same 10sec timeout Actuate and wait 15 seconds then actuate again = will send another on status message.
Is there a log to show the history of programs or scenes and the trigger?
- Is there a log to show the history of programs or scenes and the trigger?
Techman, What I was sharing has nothing to do with programs. The older style MS Sensor by default sends both ON and OFF commands. Link the MS sensor to the PLM via ISY994 - no programs created. Activate the sensor several times and read the excel log. You see both On and Off commands logged. Install jumper #4 for ON only mode. Activate the sensor several times and note that the log contains no commands from the MS sensor. This is what occurs in my ISY994 rev 5.0.15 firmware. I have always assumed this was a bug in the ISY firmware and that it was likely fixed in later versions. I was curious if this might be the case in the EISY and its versions of firmware or if it has been fixed.- Is there a log to show the history of programs or scenes and the trigger?
Techman No I am not asking for assistance in debugging programs. I was sharing that two of my IR sensors, that are configured to report both day and night, and to send only the ON command, do not show up in the log. That fact can make debugging more complicated. I am just a little curious if that particular IR configuration, coupled with certain firmware versions, and failing to report to the log, is unique or if others may also have experienced this.- Is there a log to show the history of programs or scenes and the trigger?
I am still running an older ISY994 running ver 5.0.15 firmware and noticed that some IR sensor on/off activations do not show in the log. I have 8 IR sensors total and 6 of those 8 report all on/off actions to the log. Those 6 are configured to only trigger at night. The 2 that do not report to the log are configured to be active both night and day and send On only. I have found that a little frustrating when trying to debug program issues. I am not sure why that the lack of reporting happens for that configuration. I always assumed it was a bug that was fixed in newer releases but perhaps not?- NYC Wiring
You suspect? NEC 250.118(A)(13) says it is ok.- 2342-222 8 button remote question
Perhaps they are referring to the 4 button configuration with arrows shown here:? https://shop.insteon.com/products/mini-remote-control-keypad-4-scene- Motion Senior 2 Battery Life
below is a page from some testing I did back in 2019 on the MSII current demand. Upon motion the sensor comes out of "sleep mode" and consumes a fairly large current while awake for 5 sec or so. Battery life will be directly related to the number of motions sensed. Likely more in a Hallway of course. Compare your settings of each sensor to see if one is different for some reason. I get fairly good battery life on mine but they are not used for Hallway type traffic. On my sensors I turn the LED brightness as low as it will go. Mine only report at night and only report the "On" to keep the number of wake cycles lower.- Insteon On/Off Outlet 2663-222 Max Load
That unit says 0.5hp. How many horsepower is your pump motor? At 12-14 amps likely more than 0.5hp. Rough approximation = 12A*120V = 1440watts / 750W/hp = near 2 hp. - Is there a log to show the history of programs or scenes and the trigger?