Corrupted Insteon network?
I'm looking for some guidance on how to fix my Insteon network.
Background. We had a power outage a couple of weeks ago which seemed to precipitated my issues. My EISY system is on a UPS but not the Insteon modem (for obvious reason). The UPS gave up after about 2hrs so both EISY and the modem were down. When the power came back on the EISY system couldn't talk to the Insteon network. I initially tried unplugging the modem, plugging it back in, and then rebooting EISY, all to no avail. I then tried completely powering off (removing power) EISY and that seemed to resolve the problem. Fast forward a week and now I have multiple Insteon devices showing up with an ! in front of the name and EISY is unable to talk to the devices. However, if I turn on a switch manually this change shows up in EISY for this device. Clearly EISY is getting messages from the ! devices but isn't able to communicate with them. Only about 15 devices out of 41 Insteon devices in the network have this problem. I have tried deleting some of the devices and readding them to the network which seems to allow EISY to control the devices but there is still an ! in front of these re-added devices. Another interesting clue is when I do anything with the network (for example checking the PLM status under Tools) it comes up with the PLM version and then starts updating the network (ie. shows the dialog box to not touch or change anything while the network is updated). This update goes on for 15 minutes or more before it finishes and I see Writes going on to Insteon devices that are not necessarily the ones that have the ! in front of their names.
My modem is an older serial modem (Ver v9E) that has worked reliably for years going back to my older ISY system. I suspect the modem flash is corrupted but am not sure how to proceed. I have a spare serial modem that I could try but I don't want to make things worse than they already are. I also have a spare USB modem but it is currently at a 2nd home so not something I can substitute in the near term.
BTW: The rest of the EISY system is working perfectly after the power outage. This includes multiple Z-Wave devices, multiple Plugins such as a Yolink network, an ELK system, Ambient weather system, etc. UD Mobile also works fine.
Can anyone tell me the conditions under which EISY show an ! in front of an Insteon node name? Is there a logical next step I should try in the debug process?
Mike
Edited by MMAltair
grammar corrections
@MMAltair , If your ISY is seeing manual device activations the PLM link table is intact (for that device at least). I believe that the V.9E firmware is the latest version (has not changed in some time).
This is sounding like a communication issue at the devices or the PLM:
  1. Are the devices on the same circuit - could mean a problem with that circuit.
  2. Any chance that a phase coupler died during the power outage - doesn't apply if you have newer dual band devices.
  3. Most likely is a problem near the PLM (or the PLM output stage). You might try unplugging devices on the same circuit as the PLM.
If you could open your event viewer on Level 3 and perform a query of "My Lighting", then upload the results, we can get an idea how well your devices are communicating.
Thanks for the feedback. The devices are all dual band devices so I have assumed they are not having communication issues. As I stated in my description, changes made at the device show up in the EISY Admin console so communication seems to work in one direction but not the other. In addition once I delete a device and re-add it to EISY I can then send commands to the device but it still shows up with an ! mark indicating something is wrong. I may try doing a restore on a device that I haven't tried deleting and see if this helps.
Mike
3 hours ago, Guy Lavoie said:
Well have you tried doing a "restore device" on these problematic devices? Give that a shot first.
Will give it a try and report back.
Mike
I tried "restoring" a device that wasn't working with no success. I also tried to restore the modem with no change in behavior.
Another thing I discovered is that many more of my devices aren't working although I don't know how many without testing them all. It turn's out the ! mark is only displayed if EISY tries to communicate with a device. I was aware of a number of devices not working (EISY not controlling them) since they are controlled programmatically and I notice when things aren't working. The only thing that has worked so far is to delete a device and re-add it to the network. It takes about 10 min to delete a device and 15-20 min to re-add it. It's going to take weeks to fix this. I may try to restore a new modem and go from there.
  • dual band devices are far better than powerline only, but that can still be affected by signal absorbers/noise. I have a filterlinc on my fancy linear compressor refrigerator because it takes 2 dual band devices offline without it (V.45)
  • Devices can absolutely work in one direction and not the other (send vs receive). The fact that you have several devices affected normally indicates that the issue is near the PLM.
  • The (!) indicates that a device did not respond to the ISY (On/off command, query, or programming command). A scene on/off will NOT cause a "failed to respond" (!) since it does not request status.
The fact that it takes 10 minutes to delete a device indicates that ISY/PLM are re-trying communications many times during the process.
I previously asked you to post an event viewer output from a query of "My Lighting" (event viewer on level 3). This will show which devices are having issues and the general status of your communications.
The following is a small snippet of a "My lighting" query from my system:
  • Hops left = 3: excellent
  • Hops left = 0: poor
  • Multiple communications without a response: timeout (!)
My Lighting Query:
Thu 07/30/2026 09:49:53 AM : [INST-TX-I1  ] 02 62 0C C2 32 0F 19 00
Thu 07/30/2026 09:49:53 AM : [INST-ACK    ] 02 62 0C.C2.32 0F 19 00 06          LTSREQ (LIGHT)
Thu 07/30/2026 09:49:53 AM : [INST-SRX    ] 02 50 0C.C2.32 53.BC.3A 2F 04 00           (00)
Thu 07/30/2026 09:49:53 AM : [Std-Direct Ack] 0C.C2.32-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Thu 07/30/2026 09:49:54 AM : [INST-TX-I1  ] 02 62 18 93 83 0F 19 00
Thu 07/30/2026 09:49:54 AM : [INST-ACK    ] 02 62 18.93.83 0F 19 00 06          LTSREQ (LIGHT)
Thu 07/30/2026 09:49:54 AM : [INST-SRX    ] 02 50 18.93.83 53.BC.3A 2F 11 00    LTONRR (00)
Thu 07/30/2026 09:49:54 AM : [Std-Direct Ack] 18.93.83-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Thu 07/30/2026 09:49:54 AM : [INST-TX-I1  ] 02 62 58 B0 74 0F 19 00
Thu 07/30/2026 09:49:55 AM : [INST-ACK    ] 02 62 58.B0.74 0F 19 00 06          LTSREQ (LIGHT)
Thu 07/30/2026 09:49:55 AM : [INST-SRX    ] 02 50 58.B0.74 53.BC.3A 2F 37 00           (00)
Thu 07/30/2026 09:49:55 AM : [Std-Direct Ack] 58.B0.74-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Thu 07/30/2026 09:49:55 AM : [INST-TX-I1  ] 02 62 16 CD 80 0F 19 00
Thu 07/30/2026 09:49:56 AM : [INST-ACK    ] 02 62 16.CD.80 0F 19 00 06          LTSREQ (LIGHT)
Thu 07/30/2026 09:49:56 AM : [INST-SRX    ] 02 50 16.CD.80 53.BC.3A 2B 37 00           (00)
Thu 07/30/2026 09:49:56 AM : [Std-Direct Ack] 16.CD.80-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
My Lighting Query:
Just getting back to this. Thanks for the ideas. I did check the Device Communications event log and do see some Nacks when I send commands to devices that have not been deleted and re-added to the system. I still suspect this is related to the power outage we had a few weeks ago. Since nothing else has changed in the house I think the PLM was likely damaged (It's old) by the power outage. My next step is to replace the PLM with a new one I bought a few moths ago, as a spare, and see if this resolves the issue.
Below is a snippet of the event log -
Mon 08/03/2026 12:06:53 PM : [INST-TX-I1 ] 02 62 1A 38 33 0F 11 FF
Mon 08/03/2026 12:06:53 PM : [INST-ACK ] 02 62 1A.38.33 0F 11 FF 06 LTONRR (FF)
Mon 08/03/2026 12:06:53 PM : [INST-SRX ] 02 50 1A.38.33 3D.94.80 2F 11 FF LTONRR (FF)
Mon 08/03/2026 12:06:53 PM : [Std-Direct Ack] 1A.38.33-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Mon 08/03/2026 12:06:53 PM : [D2D EVENT ] Event [1A 38 33 1] [ST] [255] uom=100 prec=0
Mon 08/03/2026 12:06:53 PM : [1A 38 33 1 ] ST 255 (uom=100 prec=0)
Mon 08/03/2026 12:06:57 PM : [INST-TX-I1 ] 02 62 1A 38 33 0F 13 00
Mon 08/03/2026 12:06:57 PM : [INST-ACK ] 02 62 1A.38.33 0F 13 00 06 LTOFFRR(00)
Mon 08/03/2026 12:06:57 PM : [INST-SRX ] 02 50 1A.38.33 3D.94.80 2F 13 00 LTOFFRR(00)
Mon 08/03/2026 12:06:57 PM : [Std-Direct Ack] 1A.38.33-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Mon 08/03/2026 12:06:58 PM : [D2D EVENT ] Event [1A 38 33 1] [ST] [0] uom=100 prec=0
Mon 08/03/2026 12:06:58 PM : [1A 38 33 1 ] ST 0 (uom=100 prec=0)
Mon 08/03/2026 12:07:11 PM : [VAR 2 42 ] 4
Mon 08/03/2026 12:07:12 PM : [D2D EVENT ] Event [n006_1921681219] [GV0] [38] uom=56 prec=0
Mon 08/03/2026 12:07:12 PM : [n006_1921681219 ][STS] GV0 38 (uom=56 prec=0)
Mon 08/03/2026 12:07:13 PM : [D2D EVENT ] Event [n006_192168165] [GV0] [8] uom=56 prec=0
Mon 08/03/2026 12:07:13 PM : [n006_192168165 ][STS] GV0 8 (uom=56 prec=0)
Mon 08/03/2026 12:07:15 PM : [INST-TX-I1 ] 02 62 71 9D 3F 0F 11 FF
Mon 08/03/2026 12:07:15 PM : [INST-ACK ] 02 62 71.9D.3F 0F 11 FF 06 LTONRR (FF)
Mon 08/03/2026 12:07:16 PM : [INST-SRX ] 02 50 71.9D.3F 3D.94.80 2F 11 FF LTONRR (FF)
Mon 08/03/2026 12:07:16 PM : [Std-Direct Ack] 71.9D.3F-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Mon 08/03/2026 12:07:16 PM : [D2D EVENT ] Event [71 9D 3F 1] [ST] [255] uom=100 prec=0
Mon 08/03/2026 12:07:16 PM : [71 9D 3F 1 ] ST 255 (uom=100 prec=0)
Mon 08/03/2026 12:07:26 PM : [INST-TX-I1 ] 02 62 71 9D 3F 0F 13 00
Mon 08/03/2026 12:07:26 PM : [INST-ACK ] 02 62 71.9D.3F 0F 13 00 06 LTOFFRR(00)
Mon 08/03/2026 12:07:26 PM : [INST-SRX ] 02 50 71.9D.3F 3D.94.80 2B 13 00 LTOFFRR(00)
Mon 08/03/2026 12:07:26 PM : [Std-Direct Ack] 71.9D.3F-->ISY/PLM Group=0, Max Hops=3, Hops Left=2
Mon 08/03/2026 12:07:26 PM : [D2D EVENT ] Event [71 9D 3F 1] [ST] [0] uom=100 prec=0
Mon 08/03/2026 12:07:26 PM : [71 9D 3F 1 ] ST 0 (uom=100 prec=0)
Mon 08/03/2026 12:07:28 PM : [VAR 2 43 ] 3
Mon 08/03/2026 12:07:34 PM : [VAR 2 41 ] 3
Mon 08/03/2026 12:07:39 PM : [INST-TX-I1 ] 02 62 71 0E A6 0F 11 FF
Mon 08/03/2026 12:07:39 PM : [INST-ACK ] 02 62 71.0E.A6 0F 11 FF 06 LTONRR (FF)
Mon 08/03/2026 12:07:42 PM : [VAR 2 42 ] 3
Mon 08/03/2026 12:07:43 PM : [INST-TX-I1 ] 02 62 71 0E A6 0F 13 00
Mon 08/03/2026 12:07:43 PM : [INST-ACK ] 02 62 71.0E.A6 0F 13 00 06 LTOFFRR(00)
Mon 08/03/2026 12:07:51 PM : [INST-TX-I1 ] 02 62 4D 9B F0 0F 11 00
Mon 08/03/2026 12:07:51 PM : [INST-ACK ] 02 62 4D.9B.F0 0F 11 00 06 LTONRR (00)
Mon 08/03/2026 12:07:51 PM : [INST-SRX ] 02 50 4D.9B.F0 3D.94.80 AF 11 FF LTONRR (FF)
Mon 08/03/2026 12:07:51 PM : [Std-Direct Nack] 4D.9B.F0-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Mon 08/03/2026 12:07:57 PM : [INST-TX-I1 ] 02 62 4D 9B F0 0F 13 00
Mon 08/03/2026 12:07:57 PM : [INST-ACK ] 02 62 4D.9B.F0 0F 13 00 06 LTOFFRR(00)
Mon 08/03/2026 12:07:57 PM : [INST-SRX ] 02 50 4D.9B.F0 3D.94.80 AF 13 FF LTOFFRR(FF)
Mon 08/03/2026 12:07:57 PM : [Std-Direct Nack] 4D.9B.F0-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Mon 08/03/2026 12:07:59 PM : [D2D EVENT ] Event [ZY004_199] [ST] [100] uom=51 prec=0
Mon 08/03/2026 12:07:59 PM : [ZY004_199 ] ST 100 (uom=51 prec=0)
Mon 08/03/2026 12:07:59 PM : [D2D EVENT ] Event [ZY004_199] [DON] [100] uom=78 prec=0
Mon 08/03/2026 12:07:59 PM : [ZY004_199 ] DON 100 (uom=78 prec=0)
Mon 08/03/2026 12:07:59 PM : [D2D EVENT ] Event [ZY004_199] [ST] [0] uom=51 prec=0
Mon 08/03/2026 12:07:59 PM : [ZY004_199 ] ST 0 (uom=51 prec=0)
Mon 08/03/2026 12:07:59 PM : [D2D EVENT ] Event [ZY004_199] [DOF] [0] uom=78 prec=0
Mon 08/03/2026 12:07:59 PM : [ZY004_199 ] DOF 0 (uom=78 prec=0)
Mike
@MMAltair thanks for the log.
In general, your communications to the devices are good. The NACK's are not. These are programming errors at the device.
You have 1 device that is returning a NACK (4D.9B.F0). This is an indication that a I2CS device is not programmed with your current PLM address. This should have nothing to due with a power outage.
Try a "restore device" on this device. If it does not correct the problem, then the ISY image is corrupt for this unit. If this is the only device affected, a "delete/re-add" should correct the problem. If you have many devices affected we need to dig a bit deeper.
I can't comment on devices that were not responding (!) because there weren't any in the log.
You mentioned 15 devices that were having issues. If see the 1 NACK in the log, can't help with the others.
Edited by IndyMike
Thanks. This log was a test log where I only tried on/off commands to one device that has an ! mark which doesn't work along with on/off commands to a couple of devices that have ! marks and were deleted/re-added and they do work. I have to disable a bunch of my polyglot plugins during the test since they fill the device communication log with unrelated entries.
Additional background: After the power failure none of my insteon devices worked so I tried unplugging the PLM, plugging it back in, and then restarting EISY to no avail. I then repeated this procedure but this time I unplugged power from EISY after restarting the PLM and then things seemed to work. However, a few days later it was apparent that only some devices were working. As a debug step I did try and do a restore on the PLM with no change in behavior.
One thing I should mention is around the time I noticed things weren't working I tried launching the Admin console using the wrong version of start.jnlp which worked (and shouldn't have). Shortly after this i realized my mistake and re-launched with the correct version of start.jnlp which also worked. I don't know if this error contributed to the problem or not.
As I stated before, I believe I need to rebuild my Insteon network with my new PLM and delete/re-add each Insteon device so the devices are aware of the new PLM. I plan to try and do a Restore on the new PLM to see if this improves things. It will take me a few days to do this work.
Mike
Mike
@MMAltair, I am struggling to understand how your devices came to be programmed with the incorrect PLM address. The would normally require a PLM change and a corrupted restore, or a restore from a backup from a previous PLM (without the ISY knowing a New PLM was attached).
Your description of events is not matching up with the symptoms. As a result, I'm very hesitant to suggest going to a new PLM. I do not see and indication that the old PLM has an issue. You have good communications, and your PLM can see device activations (sign that the PLM records are intact.
Could you try restoring an older Eisy backup?
Edit - before doing any thing drastic, could you perform/provide the following:
  1. Open the event viewer to level 3.
  2. Right click on a working device on the tree and select "Diagnostics\Show Device Link table"
  3. A window will pop up showing the device Links and the links will begin populating (reading in process). Once complete, click "Compare" on the lower right.
  4. Upload both the link table windows and the event viewer contents.
  5. Repeat the above for a device that is not working properly (!).
Also - please confirm that your current PLM address is 3D.94.80
Example link records and event viewer for one of my devices shown below
Example Link Table Read/Compare
Example Link Table Communication in Event Viewer
Wed 08/05/2026 07:51:58 AM : [INST-TX-I2  ] 02 62 18 93 83 1F 2F 00 00 00 0F FF 01 00 00 00 00 00 00 00 00 C2
Wed 08/05/2026 07:51:58 AM : [INST-ACK    ] 02 62 18.93.83 1F 2F 00 00 00 0F FF 01 00 00 00 00 00 00 00 00 C2 06        (00)
Wed 08/05/2026 07:51:58 AM : [INST-SRX    ] 02 50 18.93.83 53.BC.3A 2F 2F 00           (00)
Wed 08/05/2026 07:51:58 AM : [Std-Direct Ack] 18.93.83-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Wed 08/05/2026 07:51:59 AM : [INST-ERX    ] 02 51 18 93 83 53 BC 3A 15 2F 00 01 01 0F FF 01 A2 00 53 BC 3A FF 1F 01 C2
Wed 08/05/2026 07:51:59 AM : [Ext-Direct  ] 18.93.83-->ISY/PLM Group=0, Max Hops=1, Hops Left=1
Wed 08/05/2026 07:51:59 AM : [INST-TX-I2  ] 02 62 18 93 83 1F 2F 00 00 00 0F F7 01 00 00 00 00 00 00 00 00 CA
Wed 08/05/2026 07:51:59 AM : [INST-ACK    ] 02 62 18.93.83 1F 2F 00 00 00 0F F7 01 00 00 00 00 00 00 00 00 CA 06        (00)
Wed 08/05/2026 07:51:59 AM : [INST-SRX    ] 02 50 18.93.83 53.BC.3A 2F 2F 00           (00)
Wed 08/05/2026 07:51:59 AM : [Std-Direct Ack] 18.93.83-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Wed 08/05/2026 07:52:00 AM : [INST-ERX    ] 02 51 18 93 83 53 BC 3A 15 2F 00 01 01 0F F7 01 E2 01 53 BC 3A 01 00 01 CA
Wed 08/05/2026 07:52:00 AM : [Ext-Direct  ] 18.93.83-->ISY/PLM Group=0, Max Hops=1, Hops Left=1
Wed 08/05/2026 07:52:00 AM : [INST-TX-I2  ] 02 62 18 93 83 1F 2F 00 00 00 0F EF 01 00 00 00 00 00 00 00 00 D2
Wed 08/05/2026 07:52:00 AM : [INST-ACK    ] 02 62 18.93.83 1F 2F 00 00 00 0F EF 01 00 00 00 00 00 00 00 00 D2 06        (00)
Wed 08/05/2026 07:52:00 AM : [INST-SRX    ] 02 50 18.93.83 53.BC.3A 2F 2F 00           (00)
Wed 08/05/2026 07:52:00 AM : [Std-Direct Ack] 18.93.83-->ISY/PLM Group=0, Max Hops=3, Hops Left=3
Wed 08/05/2026 07:52:01 AM : [INST-ERX    ] 02 51 18 93 83 53 BC 3A 15 2F 00 01 01 0F EF 01 00 00 00 00 00 00 00 00 D2
Wed 08/05/2026 07:52:01 AM : [Ext-Direct  ] 18.93.83-->ISY/PLM Group=0, Max Hops=1, Hops Left=1
Edited by IndyMike
I'm back trying to make progress on this. I have not replaced the PLM and instead am trying to understand the source of the problem. As an experiment I deleted 2 devices that are in a scene and re-added the devices to the system. In this experiment the devices work fine after re-adding them but I still get an ! mark in front of each device in the My Lighting list. I then did a compare between the Device tables and the IoX tables and it shows a mismatch on one table entry. Do you have any idea why there would be a mismatch on the one entry after deleting and re-adding the device? I have included the screen shot below. Thanks
@MMAltair , you can disregard the mismatch @0FF0. the the "A" in the "EA" byte is a feature associated with newer device communications. For all intents and purposes, the tables are identical.
This devices has controller and responder links to your PLM and nothing else. It is not currently included in any scenes.
I'm a little confused by the fact that the device table shows deleted entries on lines 2, 3, and 4. Normally deleting the device/re-adding would eliminate these entries (like what I posted above).
How are you deleting/re-adding?
Does this device still have the (!) indicator?
Edited by IndyMike
I deleted the device using the "Delete" menu option by right clicking on the Device name in My Lighting. I then added the device back using the drop down menu "Link Management" and then selecting "New Insteon/A10/X10 Device".
The device has an ! mark in front of it.
I didn't do a factory reset on the device before I re-added it.
I have not added the device back to the scene that it was originally part of. Should I be removing devices from the scenes first before deleting and re-adding them to IoX?
One interesting observation I see is anytime I make a change to a device IoX is out writing to many devices that have nothing to do with the device I'm currently working on. I would expect this behavior if the device I'm working on were part of a scene that another device is in but this is not the case. Seems odd.
Another thing I just figured out is the PLM link table only has entries for the devices I have deleted and re-added to IoX (10). It has no entries for all of the other devices in my system (~ 30 devices). I suspect that when I tried to do a restore on the PLM somehow the PLM link table was erased.
I haven't been very diligent about creating back ups for IoX. The last backup I have is from when I updated the system to 6.0.4 back on 3/7/2026. I've made quite a few programming changes since then and would hate to lose all of that work by restoring an old backup to try and fix the Insteon issue.
Here's the PLM Links table -
Edited by MMAltair
added detail
Edited by MMAltair
There's a bit to unpack here...
Normally when you delete a device it removes all links/scenes from the ISY. Relinking (if you chose remove existing links) refreshes the device with a responder link to the PLM and a controller link to the PLM. Your device has "old links" from scenes that no longer exist. I've never seen that before (Curious), but it's not necessarily a problem. You might try a factory reset to see if things behave differently.
Also curious that you still have a (!) on this device. The ISY was able to program it and read the link table. Obviously it CAN communicate with the device. Not sure why it would flag it as non-responding.
Could you perform a link table read on the device with the event viewer on level 3, then post the viewer contents? This would help to assess communications with the device.
You should NOT need to remove the device from scenes prior to a delete. The ISY will do this automatically.
You likely have some "pending writes" on your devices. When the ISY is asked to update a specific device it will also try to update any other devices that are flagged as needing updates. The ISY994 has a method to turn off automatic write to devices. Not sure if that is available on the EISY.
That PLM table is a definite problem. It shows links to 10 of your 41 devices. It is either a partial listing (interrupted by communications) or a corrupt table. If you could try a few more reads to verify the contents, that would help. Otherwise you need to restore (or restore from a difference backup).
I've seen cases where one defective Insteon device can wreak havoc on the entire insteon network. A power failure/voltage spike can damage a device
Create a program with the then clause "Set EISY Query". When you run it this will show you the devices the eisy can't communicate with.
Disable those devices, by pulling out the set button or unplugging it, a few at a time. This will help you eliminate those devices as a problem
Edited by Techman
I had an Insteon On/Off plug-in module that would respond to commands with a scene On command instead of an ACK to the command. This drove me crazy for a few months until one day I recognized the lighting pattern of a scene that the On/Off module was not even involved in.
It seems the connected humidifier motor crashed the internal programming and the CPU inside was sending out weird responses. After a power cycle and a factory reset and restore that device has never acted crazy since for about 6-7 years now.
To error is human but to really foul things up takes a CPU and some memory.
@MMAltair , I am starting to believe that your EISY filesystem was corrupted during the power outage. You will not be able to do much with only 10 devices in your PLM.
You can try another PLM restore to see if that corrects the issue, but my guess is that the EISY image has been corrupted.
BEFORE you perform the restore, open the Event Viewer on Level 3. The EISY will then show you exactly which device records are being written to the PLM as in the example below.
If you wind up with a "short list" of devices, the EISY image is corrupt. To restore properly, you will need to find a good backup.
Programs can be exported to save them. I have had mixed results with this. The best results were obtained by exporting each subfolder to a separate file (do not try to save "My Programs" itself). You can also export individual programs. I would suggest trying this (export/import) to make sure you understand the functionality prior to restoring the backup. You can import folders/programs as a test and then hit "undo changes".
If you believe you have a good restore (all 41 of your devices) then you can start working through any remaining communication issues.
PLM Restore Snippet
Mon 07/27/2026 08:51:35 AM : [  53 BC 3A 1] Restoring PLM
Mon 07/27/2026 08:51:35 AM : [  58 B0 78 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  58 B0 78 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [  1A 5D C7 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  1A 5D C7 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [   C C2 32 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [   C C2 32 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [  18 93 83 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  18 93 83 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [  58 B0 74 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  58 B0 74 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [  16 CD 80 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  16 CD 80 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [   41 21 1 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [   41 21 1 1] Replacing PLM links Successful
Mon 07/27/2026 08:51:35 AM : [  29 53 3C 1] Replacing PLM links (locally and in PLM)
Mon 07/27/2026 08:51:35 AM : [  29 53 3C 1] Replacing PLM links Successful
It's certainly possible that an Insteon device was affected by the power outage. The devices I've deleted and re-added seem to work just fine with the exception of still having an ! mark in front of the names in IoX. In the logs I've looked at there aren't any retries going on indicating there aren't communication issues. I'm going to try an experiment where I delete a device, factory reset it, and re-add it to see if that clears up the problem of the system think something is wrong with the device. Thanks for the feedback.
PLM Restore Snippet
Thanks for the ideas. I'm pretty sure the Insteon network is the only issue in my system so perhaps the PLM Restore I tried messed up the PLM tables. I'm reluctant to try an old backup since I will lose programming and it will likely still leave my Insteon network in broken state due to the Insteon device links changes I've made trying to debug the current problem. My next step is to delete a deice, do a factory rest on it, and re-add it to IoX. Hopefully this will solve the problem of IoX thinking there is a problem with the re-added devices.
You can backup your current eisy config before you restore an old one. You can always reverse that and restore back to your current config that you just saved. But if everything works fine with a restore point prior to the power failure, then you know the eisy got messed up. Although since you deleted and re-added some devices those might not align with your old backup.
Also, as mentioned, you can export programs and then import them to the restore. You can also take screens shots of your programs pages for reference. If you are talking about a dozen programs or something it wouldn't be pretty easy. If you are talking about 100 programs it would be more tedious.
