Skip to content
View in the app

A better way to browse. Learn more.

Universal Devices Forum

A full-screen app on your home screen with push notifications, badges and more.

To install this app on iOS and iPadOS
  1. Tap the Share icon in Safari
  2. Scroll the menu and tap Add to Home Screen.
  3. Tap Add in the top-right corner.
To install this app on Android
  1. Tap the 3-dot menu (⋮) in the top-right corner of the browser.
  2. Tap Add to Home screen or Install app.
  3. Confirm by tapping Install.

Brian H

Members
  • Joined

  • Last visited

Everything posted by Brian H

  1. The 2457D2 LampLinc is a 120 VAC module. You where using the 12 VAC on the low voltage side of the transformer to run the LampLinc and it actually worked? It has one of the small switching ICs in it so I guess it maybe possible. I suspect it was using Insteon RF signals from a nearby Dual Band device. As I doubt the Insteon power line commands making it through the transformer. It maybe damaged. 12 volt lights may draw more current at a lower voltage. Take and plug a standard 120 volt light in it and see how it acts. In a 120 volt outlet. With no Load on the output outlet. If you push the On button does it stay On or cycle back Off? You could try a factory reset and see if anything changes. Do you know if the lighting transformer is made to work with a dimmer?
  2. Also when powering back up. Power up the PLM first so it can fully initialize before powering up the ISY994i.
  3. I just tested my ISY99i. Firmware 3.3.10. No PLM. It went into Safe Mode as we thought. I think in the Safe Mode. The Network add on may not do much.
  4. Brian H replied to jgcharlotte's topic in ISY994
    If you do a Show PLM Link Table test in the Tools Diagnostics a few times. If it is almost empty. That would be another sign the PLM has power supply issues. PLM Info/Status if it shows safe mode also can be an indicator. Long thread here on how the PLM may fail and how some have fixed theirs with new capacitors. http://forum.universal-devices.com/topic/13866-repair-of-2413s-plm-when-the-power-supply-fails/
  5. The 2474DWH is a two wire dimmer. Steals its power through the Load. Load has to be an Incandescent or 120 Volt equivalent halogen bulb. It will not work with anything else. Like CFL, LED bulbs, inductive things like motors. 2477D can be used as a controller for other Insteon Modules. Supplying the AC Line {Black} and Neutral {White} power connections. Can control a Load if the Red wire is connected and not capped off.
  6. Both the Alert Module and now the Siren Module. Go way back before the takeover. They still are not supported properly due to Smartlabs not giving the needed information in a timely manner. I too lately have seen Smartlabs reluctance to give UDI the needed information. I have reservation on their relationship myself.
  7. Brian H replied to slpelts's topic in ISY994
    The 2992-222 Range Extender. Is actually a 2457D2 Lamplinc with out the dimming parts and probably difference firmware. A full feature Dual Band module is not much more costly and it allows you more options.
  8. Thank you for the heads up on how crafty the Spammers are now getting. I will have to look more closely in forums I attend or moderate.
  9. Does not have to be something new. Can be something moved to a different location. Dual Band device like a 2443 Access Point going south and no longer getting the Insteon commands to the other power line. If you have any Access Points see if they are hardware 2.0 or higher. They have the same power supply issues as the 2413S PLMs. Though the Scene showing off and the lights are On maybe a clue.
  10. Brian H replied to slpelts's topic in ISY994
    There are also a few White Papers on the Insteon.com web site. http://www.insteon.com/technology/#documentation
  11. Some surge suppressors have a noise filter in them also. So some may absorb the Insteon Power Line Commands as noise. I had some with an across an AC power line rated .1uf 250VAC capacitor in them absorb both X10 and Insteon power line commands. Lucky for me they where on a small PCB and could easily be removed.
  12. Brian H replied to slpelts's topic in ISY994
    Even closer. RF signals can be strange, If the new location has any metal in the wall or the RF paths no longer are in line with each other. Things may not work as well. Dual Band Switches in a metal electrical box. Can have their RF distance and communications direction limited by the metal. Does not help that the Insteon RF antennas are in the BACK of the module. Closest to back back of a metal electrical box.
  13. Brian H replied to slpelts's topic in ISY994
    When you moved it to a different location. You changed things both power line and RF. You may have the PLM on a different circuit. One with noise makers or signal absobers. If the PLM is now on the other half of the house wiring. The power line signals may now have an issue getting to where they use to. Dual Band modules along with the Range Extenders can act as coupling between the incoming power lines. How new are your switches? Most presently sold Insteon Modules are Dual Band. The 2441V is strictly an Insteon RF device. So it has to be in RF range of the PLM or another Dual Band Module to do the Insteon RF communications.
  14. Brian H replied to Techman's topic in ISY994
    Found by a search. Not too sure if this will help. It has some information on what they call "Smart Hops" http://cache.insteon.com/developer/i2CSdev-022012-en.pdf
  15. Look at the starting post for 4.6.2 firmware. http://forum.universal-devices.com/topic/22000-release-462-is-now-official/ The firmware update does not update the UI or Dashboard. The post gives you the link to the new UI and how to properly update it. It also gives the link to the 4.6.2 Dashboard if you use it.
  16. Brian H replied to rg65's topic in ISY994
    I think I gave you some information that maybe not be 100% correct. I now remember that I was swapping 2412S/U PLM Daughter Boards and 2414S/U PLC Daughter Boards. In the 2412S/U the swap was fine. I imagine the 2413S/U {same basic daughter boards with a faster speed EEPROM memory chip} would be OK also. Even the 2414S serial board would work in the 2412S PLM. I have some early 2412S PLM unit with 2414S Serial Daughter Boards in them. The added RTC clock chip and battery where ignored along with the much larger memory size. The USB board between a 2414U and 2412U would not work. As they have a different baud rate.
  17. Brian H replied to rg65's topic in ISY994
    The 2413UH is the purchased HouseLinc version of the PLM. It has a different Subcategory ID number in the main boards firmware. To the ISY994i it may not matter. It did if you tried to use a 2413U with the purchased version of HouseLinc. I have swapped Serial and USB PLM Daughter Boards and for me they worked. It may not work but should not emit the magic electronic smoke.
  18. I have seen the earlier hardware power line only Insteon Modules. Reported to be more prone to power line issues. Get into a unknown state.. That an AC power cycle reset clearing the unknown state. The troubleshooting chart in the full users manuals would say to do a AC power cycle reset for locked up and strange acting devices. Noise on the AC power from storms could be a factor in your modules issues.
  19. Your decoding the capacitor markings look correct. 8.25 uF and 4.75 uF. I double recommend getting capacitors rated for use on AC Power Line connections. My thoughts on the Triac in the FanLinc is they use them to switch the different capacitor into the Fan Load Output. Check you fans wiring thoroughly. They could be connecting the caps to different winding taps for some speeds or changing direction by swapping wires.
  20. Thank you for reinforcing the data posted, in this very long thread. I too have had 2443 Hardware V2 Access Points {V1 hardware are the older design with power transformer supply} have the same bad caps and very low unregulated 12 volt supplies. Usually around 18-20 VDC. Mine where <7VDC and the logic supply IC was out of regulation. Fixed a few myself. Even in my newest {V2.3} PLM they are still using the same questionable brand caps. C7 and C13 are still 100uF but upped the working voltage to 50VDC. Older hardware 2413 PLM and hardware V2 Access Points have the 10uF 35VDC C7 and C13. They are mounted horizontally on the PCB and held with a glob of component glue. Physically to large to mount normally vertically to the PCB. My V2.3 also has a new RS232 interface chip on the Daughter Board. Has a IEC61000-4-2 ESD Protection rating.
  21. Many of the older power line only Insteon modules. Used a power line derived type power supply. With a capacitor to limit the current into a Zenner Diode regulated supply. They could get confused by some line noise and needed a power cycle reset. I can also verify the 2456D and 2456S modules have the +5 volt Logic supply connected directly to the AC Line input pin and logic regulation all in the common side.
  22. If all three Blue LEDs are on. That is not correct. Here is some UDI Wiki information on the front panel LEDs. http://wiki.universal-devices.com/index.php?title=Main_Page#Front_Panel_LEDs.2FLights Before calling the ISY994i defective. I would also suggest the power up sequences mentioned to see if anything changed. I would suspect the 2413S PLM before the ISY994i. Unless you where counting on Insteon RF only and the PLM was also on a surge suppressor or UPS. It is directly connected to the incoming AC power. I have also seen some indications the RS232 IC in the 2413S PLM was sometimes an issue and I know they changed it to an ESD rated IC in the hardware 2.3 and above.
  23. Brian H replied to Techman's topic in ISY994
    Not necessarily the PLM. Do a search here. There are a few All On, All Off and maybe random changes. In threads here. Not related to a PLM.
  24. Just make a note. The HUB's Insteon ID will be in the Alert Module and the ISY994i will not know it. If for any reason you may restore the Alert Module with the ISY994i it may over write the HUB's ID.
  25. If the valve has limit switches or can be held open or closed with the 24VAC. The 2450 I/OLinc NO and NC relay outputs and a 24VAC supply should work. Reason I ask about limit switches or holding open and closed. Is 24VAC will be active on either the Open or Closed wiring all the time. So it has to stop with a internal limit switch or designed to be held open and closed. I would imagine if you had to. You could use an On/Off module to control power to the 24VAC supply and then the 2450 to open and close the valve itself. As Stu asked. If you can provide a link to the valve or its model number. It would be a big help. I did a web search. I found a manual for a PE24VA Pool Valve. If your is a PV24VA or similar. It has Limit Switches to stop it when the valve is open or closed. So a 24VAC supply and a 2450 I/OLinc should control it.

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.